You've left me on a cliff-hanger :p
jim hardy said:Steinmetz's original paper is out here someplace on internet, i found it once and linked to it.
...................................
Think about it.
The transformer equivalent circuit is a math model describing the physics not the actiual physics itself. We can refine it ad infinitum.
Iron loss depends on how hard you push the core and it's not linear . It's B^1.4 or 1.6 or something.
You know if you double volts per turn you double flux. If you halve one you halve the other.
(1/2)^1.6 = 0.32
In the transformer model
P = E2/Rcore
Halving volts quarters the right side but only lowers P by 0.32 not 0.25 .
Rcore = E2 / P
So R has to change.
I'm sure you can work out a R vs E relation using logarithms but that makes equations not intuitive-at-a-glance for me. I have to work first in simple arithmetic then build toward elegance. I expect a roughly square root relation because in dividing you subtract exponents and 2 - 1.6 = 0.4 .
Appreciate any corrections - did i make a thought blooper ?
They place it between 1.5 and 2.5 for hysteresis looks like 2 for eddy current heatingtim9000 said:It doesn't have the 1.4 or 1.6, do you suppose they just rounded it up to 2?
https://www.mag-inc.com/Products/Ta.../Square-Permalloy-80-Material-Property-Curvestim9000 said:So I was thinking that a manufacturer would give you a 'watts / pound' for your steel sheet,
jim hardy said:They place it between 1.5 and 2.5 for hysteresis looks like 2 for eddy current heating
jim hardy said:Magnetics has a "how to" page for powder cores
https://www.mag-inc.com/design/design-guides/powder-core-loss-calculation
i suppose there's a similar one for tape cores but I've not found it yet. Would like to.
Here's an old thread i'd forgotten
https://www.physicsforums.com/threa...ses-hysteresis-eddy-current-constants.850475/
Yep. Doesn't open circuit test establish approximate operating B ? Hence approximate losses in that operating region ?tim9000 said:Presumably RC will depend on what B is?
Because, I'd have thought that rather than all this curve fitting stuff, you'd just do a Open Circuit test, find RC, then approximate what your losses would be based on how much magnetising current was going through RC for your secondary load current...?...No?
jim hardy said:Yep. Doesn't open circuit test establish approximate operating B ? Hence approximate losses in that operating region ?
View attachment 209823
It's just a math model. One can refine it forever, least squares fit Rc to B and write in the equation . Maybe for a thesis or something but it wouldn't make sense for everyday maintenance work i did all those years.. unless you had some unusual application that overworked the core. We once had some transformers melt from third harmonic current but that was overworking the copper not the iron. Took a while to figure that one out.
old jim
Characterizes core loss at or near the transformer's operating point. In early days they didnt know how much iron they needed in an AC machine. Steinmetz showed them how to calculate it. Flux level tells you how much heat it'll make and you have to provide mechanical design to get it out.tim9000 said:what is the value in determining Rc?
jim hardy said:Characterizes core loss at or near the transformer's operating point. In early days they didnt know how much iron they needed in an AC machine. Steinmetz showed them how to calculate it. Flux level tells you how much heat it'll make and you have to provide mechanical design to get it out.
tim9000 said:But the Rc is determined via the Open Circuit test (if I'm not mistaken). Is that really near the transformer's operating point? I'd have thought on-load the flux density would be less
try this guytim9000 said:RC ∝ Acore cross section, which I found counter-intuitive at first.
jim hardy said:on load or no load ?
Have you forgot that transformer flux is in proportion to voltage not load current ? Magnetizing current establishes flux to make counter-emf.
try this guy
http://web.eecs.utk.edu/~dcostine/ECE482/Spring2015/materials/magnetics/CoreLossTechniques.pdf
tim9000 said:I'm really surprised by this, because as we've discussed previously, triangular waves have higher harmonics in them than Sine waves. So I'd have thought those higher harmonics would increase core losses.
jim hardy said:Probably because sine wave spends more time near peak than a triangle ?
Compare Peak-to-RMS and Peak-to-Averege ratio for the two waves.
tim9000 said:But I may need some more explanation from you.
tim9000 said:So I'll re-ask you, as the primary current increases to compensate for the flux induced by the secondary load current, the net change in B is really insignificant (or perhaps even immeasurable) is it not?
tim9000 said:I wanted to ask you for a reminder on the impact of increasing your core cross sectional area, as the only independent variable. And this impact on flux and B. If memory serves, my conclusion from our previous discussion was that you can control for EITHER:
V.s/N
Or
N.I
which means that if you control V.s/N to keep it constant, and increase A then the flux stays the same, and B drops.
However, if you control N.I to keep it constant, and increase A the flux will increase and B will stay the same.
Going by the scarcity on the internet I'd say the odds of that are none.jim hardy said:If you ever run across a little paperback book on Magnetic Measurements by Jack M Janicke , BUY IT !
jim hardy said:go back to basics - as load goes up , voltage drop across primary resistance and primary leakage reactance subtract from applied voltage, so you need less counter-emf and flux can decrease accordingly.
But it's surely measurable - try it on a little transformer with two secondaries. Load one secondary and use the other unloaded as a flux detector. Remember - for sinewave, voltage and flux are in proportion. Won't careful measurement of voltage on open secondary tell you about flux ?
jim hardy said:C'mon now, back to basics
sinewave ?
volts per turn is flux and if you spread same flux over bigger area, well, what happens to flux density B ?
NI is MMF and if you apply same MMF to bigger area what happens to flux ?
Yes ! You answered your question yourself - I knew you already knew that - thanks !tim9000 said:However, if you hold N.I and increase the core cross-sectional Area, then doesn't B stay the same? Because, flux = MMF/Reluctance, and Reluctance = length/(Area.Permeability)
That is the distinction I was confirming.
because flux = B.Area
is the 'what'tim9000 said:However, if you control N.I to keep it constant, and increase A the flux will increase and B will stay the same.