To calculate the total heat transfer in a solar water heater system, measure the inlet and outlet water temperatures and the flow rate. The heat transfer can be calculated using the formula for heat flow, which incorporates density, heat capacity, temperature, and volume flow rate. It's important to account for the heat capacity of glycol, as it differs from that of water. A diagram of the system can help clarify measurement points and variables for calculations. Accurate periodic calculations will enable the home automation software to total the heat produced effectively.
modernhistorian
Messages
1
Reaction score
0
TL;DR Summary
Given a tank of known volume and knowing the temperatures of water as it enters, remains, and leaves the tank, is it possible to calculate heat gained or lost?
I have a solar water heater on my deck, with a circulator powered by PV, that pumps heated glycol through a wand heat exchanger placed in an 80 gallon tank. Water comes from the well's pressure tank, passes through this solar pre-heater tank, then into an LPG heater that adds any heat needed. I want to calculate, in my home automation software, the amount of heat in B.T.U's that are produced in the water flowing through this system. I can measure:

1. The temperature of the water as it enters and exits the system, and in the tank. As well, the temperature of the heat exchanger.
2. The flow of water through the system, which is of course intermittent.

if I can make this calculation periodically, then the software can total it. any guidance would be appreciated.
 
Engineering news on Phys.org
If you have the temperature and flow, a BTU is the energy required to heat a pound of water by 1 degree F.

...depending on the glycol fraction it may be significant enough to correct for its heat capacity difference (it is less than water).
 
Hello @modernhistorian ,
:welcome: ##\qquad## !​

I have to pass on the units you want to use -- so conversion is left up to you.

You may want to make a diagram of your setup (like here), indicating measurement points, so you can name the variables that occur in the calculations.

Heat flow ##\dot Q## ( in my SI units J/s or W ) is $$ \dot Q = \rho \, c_p \, T\,\Phi$$ with ##\rho## density in kg/m3 , ##c_p## heat capacity in J/(kg##\cdot##K), ##T## the temperature, and ## \Phi## volume flow in m3/s .

With this you can set up a heat balance. (detailed example here)

From your description I understand that you have ##\dot Q## for water at various points. What about the glycol ?
(i.e. I don't understand 'the' temperature of the heat exchanger -- there should be four temperatures: water in and out, glycol in and out)

##\ ##
 
Hi all, I have a question. So from the derivation of the Isentropic process relationship PV^gamma = constant, there is a step dW = PdV, which can only be said for quasi-equilibrium (or reversible) processes. As such I believe PV^gamma = constant (and the family of equations) should not be applicable to just adiabatic processes? Ie, it should be applicable only for adiabatic + reversible = isentropic processes? However, I've seen couple of online notes/books, and...
Thread 'How can I find the cleanout for my building drain?'
I am a long distance truck driver, but I recently completed a plumbing program with Stratford Career Institute. In the chapter of my textbook Repairing DWV Systems, the author says that if there is a clog in the building drain, one can clear out the clog by using a snake augur or maybe some other type of tool into the cleanout for the building drain. The author said that the cleanout for the building drain is usually near the stack. I live in a duplex townhouse. Just out of curiosity, I...
I have an engine that uses a dry sump oiling system. The oil collection pan has three AN fittings to use for scavenging. Two of the fittings are approximately on the same level, the third is about 1/2 to 3/4 inch higher than the other two. The system ran for years with no problem using a three stage pump (one pressure and two scavenge stages). The two scavenge stages were connected at times to any two of the three AN fittings on the tank. Recently I tried an upgrade to a four stage pump...
Back
Top