Calculating Ventilation Effect Watts in a Room

  • Thread starter Thread starter TSN79
  • Start date Start date
  • Tags Tags
    Ventilation
AI Thread Summary
To calculate the effect of a ventilation system in Watts, the proposed equation uses the specific heat capacity of air (0.335) and the temperature difference between incoming air (TA) and outside air (TO). However, if the incoming air is cooler than the room temperature, the energy required to heat this air must also be considered. The current formulation may lead to unit inconsistencies, as it compares Watts to a product of volume flow and temperature change, which does not yield the desired result. It is suggested to convert volume flow to mass flow to ensure proper unit alignment. Accurate calculations are essential for determining the effective heating impact of the ventilation system.
TSN79
Messages
422
Reaction score
0
I want to calculate how much effect in Watts a ventilation system brings into a room. Will it be correct to use the following equation for this:

<br /> \dot Q = \dot V \cdot 0,335 \cdot \left( {T_A - T_O } \right)<br />

where 0,335 is actually the Cp of air derived from {{1005} \over {3600}} \cdot 1,2
TA is the temperature the air enters the room with, and TO is the outside temp.

If the air enters the room with a lower temp than the room, how can the energy needed to heat up this air to room temp be taken into account?
 
Engineering news on Phys.org
I would think that should work, however, check your units. On the left you have watts, or J/s, on the right you have (m^3/s)(J/kgK)(K) giving you...well not what your looking for. I'm pretty sure you need to change your volume flow to mass flow.
 
Hi all, I have a question. So from the derivation of the Isentropic process relationship PV^gamma = constant, there is a step dW = PdV, which can only be said for quasi-equilibrium (or reversible) processes. As such I believe PV^gamma = constant (and the family of equations) should not be applicable to just adiabatic processes? Ie, it should be applicable only for adiabatic + reversible = isentropic processes? However, I've seen couple of online notes/books, and...
I have an engine that uses a dry sump oiling system. The oil collection pan has three AN fittings to use for scavenging. Two of the fittings are approximately on the same level, the third is about 1/2 to 3/4 inch higher than the other two. The system ran for years with no problem using a three stage pump (one pressure and two scavenge stages). The two scavenge stages were connected at times to any two of the three AN fittings on the tank. Recently I tried an upgrade to a four stage pump...