Can I use two AC TRs with ONE neutral at sec. and prim.?

Click For Summary

Discussion Overview

The discussion revolves around the electrical connection of two transformers (TR1 and TR2) supplying different circuits in a Building Management System (BMS). Participants explore the implications of sharing a neutral connection between the transformers while ensuring proper operation of a valve actuator controlled by a 0-10V DC signal. The scope includes technical reasoning regarding transformer connections, control signal integrity, and circuit design considerations.

Discussion Character

  • Technical explanation
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • Some participants suggest short-circuiting the secondary winding neutrals of TR1 and TR2, while others express caution about this approach.
  • One participant proposes inserting a 1Ω resistor between the neutrals to mitigate potential issues, although this is met with skepticism regarding its effectiveness.
  • There is a discussion about the necessity of solidly connecting the transformer neutrals without a resistor, emphasizing the importance of common grounding in a TN scheme.
  • Concerns are raised about the derivation of the DC control signal from TR1 and its implications for circuit design.
  • Participants discuss the potential impact of incorrectly connected bridge diodes in the circuit diagrams, leading to confusion about the correct setup.
  • Some participants argue that placing a resistor in the control loop could disturb the voltage signal, questioning the appropriateness of using a 1Ω resistor in this context.
  • There is a mention of the isolation of the control circuitry from the 24Vac input, suggesting that the control signal may not share a common ground with the actuator circuit.

Areas of Agreement / Disagreement

Participants express differing opinions on whether to connect the neutrals directly or use a resistor, indicating a lack of consensus on the best approach. The discussion also highlights uncertainty regarding the implications of circuit design choices and the correct configuration of components.

Contextual Notes

Participants note the importance of ensuring that the positive terminals of the transformers are not connected to avoid paralleling the transformers. There are also unresolved questions about the derivation of the DC signal and the correct orientation of circuit components.

Shady Artin
Messages
4
Reaction score
0
The situation:
I have one BMS (Building Management System) controller supplied from TR1 (220Vac to 24Vac transformer) and provides an analog control signal (0-10VDC) with the (-) of that DC being the same as the Neutral of the controller (from TR1) and should control a valve actuator.

The controlled valve actuator uses 24Vac supplied control circuit...supplied from TR2 (same as TR1 and primary winding are supplied from the same source "220Vac outlet").
The actuator control circuit has terminals:
1- G "24Vac"
2- G0 "Neutral and DC reference point"
3- X "control signal...DC 0-10V"

Now, the problem I'm afraid to face:
The actuator should have the control signal (0-10VDC) with a reference (-) that should be at the same time the 24Vac source neutral...Should I SHORT CIRCUIT TR1 and TR2 secondary winding neutrals or do what??

Note: Unfortunately, I cannot use one transformer for both the controller and actuator.

Thanks
 
Engineering news on Phys.org
Shady Artin said:
Should I SHORT CIRCUIT TR1 and TR2 secondary winding neutrals or do what??
You can. I am a pessimist, and would insert a 1Ω resistor between them.
 
  • Like
Likes   Reactions: Shady Artin
Shady Artin said:
The situation:
I have one BMS (Building Management System) controller supplied from TR1 (220Vac to 24Vac transformer) and provides an analog control signal (0-10VDC) with the (-) of that DC being the same as the Neutral of the controller (from TR1) and should control a valve actuator.

The controlled valve actuator uses 24Vac supplied control circuit...supplied from TR2 (same as TR1 and primary winding are supplied from the same source "220Vac outlet").
The actuator control circuit has terminals:
1- G "24Vac"
2- G0 "Neutral and DC reference point"
3- X "control signal...DC 0-10V"

Now, the problem I'm afraid to face:
The actuator should have the control signal (0-10VDC) with a reference (-) that should be at the same time the 24Vac source neutral...Should I SHORT CIRCUIT TR1 and TR2 secondary winding neutrals or do what??

Note: Unfortunately, I cannot use one transformer for both the controller and actuator.

Thanks
As long as the "positive" terminals of the transformers are not connected two (to avoid paralelling the transformers) there should be no problem with the connection you are proposing. Indeed, if you are using a TN scheme, the neutral points should be common and at ground potential
 
  • Like
Likes   Reactions: Shady Artin
Svein said:
You can. I am a pessimist, and would insert a 1Ω resistor between them.
What power rating should that resistor have?
 
xareu said:
As long as the "positive" terminals of the transformers are not connected two (to avoid paralelling the transformers) there should be no problem with the connection you are proposing. Indeed, if you are using a TN scheme, the neutral points should be common and at ground potential
Thanks
 
The resistor is not advisable. As I explained before, the neutrals must be solidly connected. If you want to protect the circuits (you should), you can used Miniature Circuit Breakers in each phase leg (not in the neutral in this particular case).
 
Shady Artin said:
What power rating should that resistor have?
0.25W is more than enough. The only current that should pass through the resistor is the current due to the control signal. The actuator should be connected directly to its transformer. The purpose of the 1Ω resistor is to break up any ground loops.
 
The transformers neutral must be solidly interconnected, without the resistor . Please check neutral earthing schemes. The control voltages are 0-10 V and fed from the controllers. As for the control signal: most probably the internal circuitry of the controllers isolate the 0-10 Vdc from the 24 Vac so no common ground will be expected. If you place a resistor in the control loop, you are disturbing the voltage signal (it´s not a 4-20 mA loop).
 
there's an unanswered question...

Shady Artin said:
The actuator control circuit has terminals:
1- G "24Vac"
2- G0 "Neutral and DC reference point"
3- X "control signal...DC 0-10V"
How is that DC from TR1 derived?

EDIT i cut and pasted pictures below without checking closely enough
that author drew his diode bridges rotated 1/4 turn from correct orientation
rotate them 90 degrees CCW before using
see dave's post below
thanks Dave
(chagrin icon) :eek:

diode-bridge-single-supply.png


or

full-wave-rectifier-lc-choke-filter.jpg

or

diode-bridge-split-supply.png


In either of the latter two your TR1 transformer's centertap is already circuit common
so you also could tie the TR2 transformer to circuit common .
If the first, don't connect TR1's winding to TR2's winding.
 
Last edited:
  • #10
jim hardy said:
there's an unanswered question...How is that DC from TR1 derived?

diode-bridge-single-supply.png


or

full-wave-rectifier-lc-choke-filter.jpg

or

diode-bridge-split-supply.png


In either of the latter two your TR1 transformer's centertap is already circuit common
so you also could tie the TR2 transformer to circuit common .
If the first, don't connect TR1's winding to TR2's winding.
Those bridge diodes are incorrectly connected
whoever drew them didn't see their mistake or don't understand

take the top circuit

diode-bridge-single-supply.png


voltage from the 1/2 cycle coming out the top of the transformer winding is going both to ground and the V+ output
don't think that will work too well ... the same error is perpetrated in bottom drawing as well

correctly drawn example ...
upload_2016-3-2_9-46-8.png
Did I miss something in the discussion, @jim hardy ?
Did you show those incorrectly on purpose to make a point ?Dave
 
  • Like
Likes   Reactions: jim hardy
  • #11
  • Like
Likes   Reactions: davenn
  • #12
jim hardy said:
Not at all and good catch ! Thank you !

I cut and pasted from a google search without checking close enough - mea culpa and THANK YOU

That guy pasted his bridge into his drawing 90degrees out !
http://www.interfacebus.com/Glossary-of-Terms-full-wave-bridge-rectifier-circuit.html
shame on him and me both.Sorry about that ...
no probs ... just wanted to make sure you weren't trying to teach the OP something and see if he could pick the problem LOLD
 
  • #13
xareu said:
If you place a resistor in the control loop, you are disturbing the voltage signal (it´s not a 4-20 mA loop).
A 1Ω resistor? Even if your activation signal is as greedy as old-fashioned TTL (1.6mA), the voltage drop will be 1.6mV!
 
  • #14
Svein said:
A 1Ω resistor? Even if your activation signal is as greedy as old-fashioned TTL (1.6mA), the voltage drop will be 1.6mV!
This is a matter of engineering, not laboratory tampering with circuits.
 
  • #15
At any rate, this circuit belongs to a "power" rectifier, but I believe that for the 0...10 Vdc the control circuitry isolates the variable 0...10 Vdc from the 24 Vac input
 

Similar threads

  • · Replies 17 ·
Replies
17
Views
3K
  • · Replies 12 ·
Replies
12
Views
16K
Replies
6
Views
4K
Replies
7
Views
15K
Replies
2
Views
4K
  • · Replies 6 ·
Replies
6
Views
3K
Replies
138
Views
26K
  • · Replies 16 ·
Replies
16
Views
5K
  • · Replies 3 ·
Replies
3
Views
4K
  • · Replies 1 ·
Replies
1
Views
7K