Capacitance of a Transmission line

24 replies · 9K views · last reply
jaus tail
Messages
613
Reaction score
48

Homework Statement


A single phase transmission line has 2 parallel conductors 1.5 metres apart. The diameter of each conductor being 0.5 cm. Calculate the line to neutral capacitance for a line 80 km long[/B]

Homework Equations


CAN = 2(3.14)(permittivity)/Loge [D/r] This gives capacitance per metre
Where D is the distance between conductors and r is the radius.
Multiplying above answer into length of line gives capacitance

The Attempt at a Solution


D = 1.5 metres = 150 cm
r = radius = 0.5 / 2 = 0.25 cm
Substituting in above equation I get CAN = 8.69 * 10-12 F / m
Multiplying this with 80 km or 80,000 m I get 0.69 micro farad.
Book answer is 3.48 micro farad

I guess they've used formula for line capacitance CAB instead of line to neutral capactiance.
 
jaus tail said:
I guess they've used formula for line capacitance CAB instead of line to neutral capactiance.

What is your definition of line capacitance CAB and your definition of line to neutral capacitance?

Note that the problem did not give you the height of the line above the ground, so it can't be the line to ground capacitance.
 
  • Like
Likes   Reactions: Delta2
jaus tail said:

Homework Statement


A single phase transmission line has 2 parallel conductors 1.5 metres apart. The diameter of each conductor being 0.5 cm. Calculate the line to neutral capacitance for a line 80 km long[/B]

Homework Equations


CAN = 2(3.14)(permittivity)/Loge [D/r] This gives capacitance per metre
Where D is the distance between conductors and r is the radius.
Multiplying above answer into length of line gives capacitance

The Attempt at a Solution


D = 1.5 metres = 150 cm
r = radius = 0.5 / 2 = 0.25 cm
Substituting in above equation I get CAN = 8.69 * 10-12 F / m
Multiplying this with 80 km or 80,000 m I get 0.69 micro farad.
Book answer is 3.48 micro farad
The book answer is off by an order of magnitude.
I guess they've used formula for line capacitance CAB instead of line to neutral capactiance.
That is correct. I think they assumed the "neutral" is the second wire. They did specify a single-phase system which will have 2 wires, not 3.
 
I'm a bit rusty but..

If the question is about a phase and neutral pair then I don't think there should be a factor of 2 in the equation in the OP?
 
CWatters said:
I'm a bit rusty but..

If the question is about a phase and neutral pair then I don't think there should be a factor of 2 in the equation in the OP?
I think the same ...
 
Still, without the factor of 2 the book answer is ahead by a factor of 10 (if I did the calculations correctly). MAYBE the line length is 800km instead of 80km?
 
But why should the factor of 2 not be there?
In the book they've derived the formula as:
Textbook page with formulas for capacitance of a two-wire line, C_AB = Q/V_AB = 2πε0 / log_e(d/r) F/m, followed by diagrams: Fig. 9.22 shows conductors A and B with capacitance C_AB between them, and Fig. 9.23 shows A, neutral N and B with C_AN = 2C_AB and C_BN = 2C_AB.

So as per the book formula the factor of 2 must be there.
 
Attachments
  • Textbook page with formulas for capacitance of a two-wire line, C_AB = Q/V_AB = 2πε0 / log_e(d/r) F/m, followed by diagrams: Fig. 9.22 shows conductors A and B with capacitance C_AB between them, and Fig. 9.23 shows A, neutral N and B with C_AN = 2C_AB and C_BN = 2C_AB.
    upload_2017-12-27_8-37-2.png
    74.6 KB · Views: 2,744
  • Like
Likes   Reactions: Tom.G
Diagram of two parallel cylindrical conductors in cross-section, with a dashed circle around the left one labelled x and its diameter labelled 2r, and the distance between the conductors labelled Dist.

I’ll try not to boring you with this theory and I’ll endeavor to be as brief as I can.

Let’s define:

E(x)=electrostatic field at radius x from the first conductor center

D(x)=the electric flux density[displacement] at the same radius x

Q=electric charge

V=voltage between the two wires

Then :

Q=∫D.ds=D(x).2.π.x.length

D(x)=ε.E(x)

E(x)=Q/ ε /2/π/x/length

V=∫E(x).dx|x=r to x=Dist|

Since the electric field is more complex in the inner part of the conductor a correction it is required. So instead of r we use r’=e^(-1/4)r'=0.778801.r

V=Q/length/ ε /2/π.ln(Dist/r') or

C/length=Q/V= 2.π. ε/ln(Dist/r') [F/unit length]

For more information see-for instance:

http://alphard.ethz.ch/Hafner/Vorles/PhysicalMod/chapter1.pdf
 
Attachments
  • Diagram of two parallel cylindrical conductors in cross-section, with a dashed circle around the left one labelled x and its diameter labelled 2r, and the distance between the conductors labelled Dist.
    upload_2017-12-27_9-12-5.png
    2.3 KB · Views: 1,948
  • Like
Likes   Reactions: jaus tail
jaus tail said:
But why should the factor of 2 not be there?
In the book they've derived the formula as:
View attachment 217463
So as per the book formula the factor of 2 must be there.
Your book clearly derives CAB without the factor of 2.
The confusion arives because your problem uses "neutral" as the second, not the third, wire. There is no third wire.
 
Last edited:
  • Like
Likes   Reactions: jaus tail
The example on that website calculates the capacitance between two wires that have opposite polarity eg when one is positive the other is negative. It then modifies that equation to give one for the capacitance between either wire and a virtual neutral mid way between them.

Your situation is different. In your case one of the wires is neutral not the opposite polarity. So the neutral point in your case is physically twice as far away from the line as their example.
 
  • Like
Likes   Reactions: jaus tail and anorlunda
Can I assume that the book answer is wrong?
I thought 0.7788 factor was for inductance and not for capacitance. That's what the book says.
 
You are right, jaus tail. My mistake. Thank you. Since the electric field it is E=ro.J and the current is zero in the conductor core due to skin effect- in a.c.- the electric field is also zero inside the wire.
On the other hand this reasoning is valid only for a single charged wire. If there are two opposite charged wires the electric field is different. See Figure 1.4. Graphical representation of the electrostatic field from the above mentioned article.
 
  • Like
Likes   Reactions: jaus tail
So, jaus tail, you said: “Book answer is 3.48 micro farad”. It could be 3.48E-01 ?
 
  • Like
Likes   Reactions: Delta2
Where does the divide by 2 part come from? I'm getting answer as 0.69 micro farad. I've pasted the book page in post#7
 
jaus tail said:
Where does the divide by 2 part come from? I'm getting answer as 0.69 micro farad. I've pasted the book page in post#7
Your posted book page clearly states CAB = πε0/ln(d/r) and is correct.
Assimilate post 9!
 
jaus tail said:
Where does the divide by 2 part come from?
The book gives the distance between "A" and "B" conductors and shows an "N" conductor half way between them. It then asks for Capacitance between a main conductor (A or B) and "N".

What happens to the capacitance between conductors when the distance between them changes?
 
The capacitance increases when the distance between plates/wires reduces.

I'm still not getting it. This is what the book page says:
Consider a single phase overhead transmission line consisting of 2 parallel conductors A and B placed d metres apart. Let their respective charge be +Q and -Q C/metre length.
Diagram of two parallel circular conductors, the left labelled +Q and the right labelled -Q, with radius = r on the right conductor and distance = d marked between their centres.

CAB = 3.14(permittivity)/log(d/r) F/m

Now for Capacitance to neutral:
Book says:
Above equation gives Capacitance between the conductors of a two-wire line. Often it is desired to know the capacitance between one of the conductor and a neutral point between them. Since the potential of the mid-point between conductors is zero, the potential difference between each conductor and ground or neutral is half the potential difference between the conductors. Thus the capacitance to ground or capacitance to neutral for the two-wire line is twice the line-to-line capacitance as shown in the figure below.
Two schematic diagrams of a two-wire line: top shows +Q and -Q conductors (radius = r, distance = d) joined by capacitor Cab; bottom adds a neutral point N between them, with Can = 2Cab and Cbn = 2Cab.

There is no separate neutral wire. The Neutral is a point at zero potential and Can = 2Cab. In the main question posted in post#1 they are asking to calculate line to neutral capacitance. And they are saying a single phase line has 2 charged conductors. So one would be +Q and the other -Q. Just like in diagram above. I'm really confused. There is one solved example but that requires to calculate line to line capacitance and they've substituted formula Cab.
 
Attachments
  • Diagram of two parallel circular conductors, the left labelled +Q and the right labelled -Q, with radius = r on the right conductor and distance = d marked between their centres.
    upload_2018-1-3_9-0-45.png
    1.2 KB · Views: 1,652
  • Two schematic diagrams of a two-wire transmission line: top shows +Q and -Q conductors joined by capacitor Cab, radius r and distance d; bottom adds a neutral point N with Can = 2Cab and Cbn = 2Cab in series.
    upload_2018-1-3_9-6-47.png
    3.3 KB · Views: 726
  • Two schematic diagrams of a two-wire line: top shows +Q and -Q conductors (radius = r, distance = d) joined by capacitor Cab; bottom adds a neutral point N between them, with Can = 2Cab and Cbn = 2Cab.
    upload_2018-1-3_9-7-0.png
    3.3 KB · Views: 1,644
Oh I guess you'll are saying that in the question in post#1 one conductor is charged whereas other is neutral. But how? There is one solved example like this:
Worked example 9.11 from a textbook: capacitance of a single-phase transmission line with two parallel conductors 3 m apart, conductor radius 1 cm, solved using C = pi*eps0 / log(d/r) giving 0.4875 x 10^-11 F/m, or 0.04875 uF/km.
 
Attachments
  • Worked example 9.11 from a textbook: capacitance of a single-phase transmission line with two parallel conductors 3 m apart, conductor radius 1 cm, solved using C = pi*eps0 / log(d/r) giving 0.4875 x 10^-11 F/m, or 0.04875 uF/km.
    upload_2018-1-3_9-22-43.png
    43.8 KB · Views: 2,081
I found this from google:
Worked solution for capacitance of a single-phase two-wire line with D = 3 m and conductor radius 0.6 cm, giving C_a = 8.94 nF/km to neutral and C_ab = 4.47 nF/km between conductors.

Here also they haven't divided by 2 for neutral wire.
 
Attachments
  • Worked solution for capacitance of a single-phase two-wire line with D = 3 m and conductor radius 0.6 cm, giving C_a = 8.94 nF/km to neutral and C_ab = 4.47 nF/km between conductors.
    upload_2018-1-3_9-27-3.png
    15.8 KB · Views: 2,973
jaus tail said:
I'm still not getting it
Hmmm. Me neither. I hope someone here can come up with a good explanation. Sorry. :frown:
 
Speaking only of line-to-line capacitance, the answer is what I said in post 15, i.e. C = πε/ln(d/r). This can be derived by invoking two Gaussian surfaces, one for each charged wire, with superposition for the two wires, each charged with charge Q.

I have further confirmed this by computing inductance L, setting Z0 = √(L/C) which gives Z0 = 120 ln(D/r) and which agrees with my radio engineers' handbook.

But if one of the wires has zero charge, which is how you can think of a "neutral", the capacitance is doubled since the potential difference between the two wires would now be halved and C=Q/V.
 
There is a problem with the word 'neutral'. A real 'neutral' carries no current, whether it be a third grounded wire or a fictional plane. In my (older) house the wiring is 2 wires, not 3, & one of them (the white one) is called 'neutral' but it carries all the return current & so is in every sense a 2-wire system with no real 'neutral', and the inter-wire capacitance is πε/ln(D/r). It's called 'neutral' because it's connected to Earth ground so its potential is zero.