Capacitor to be connected to increase power factor
To improve the power factor to unity in a circuit with a resistance of 80 ohms and an inductive reactance of 112 ohms, a capacitor must be connected that matches the inductive reactance. The initial calculations incorrectly used apparent power instead of focusing on the voltage across the resistor. It was noted that using a series capacitor for power factor correction can significantly increase total power, which may damage the load if not designed for it. A parallel capacitor is typically recommended for power factor correction to avoid these issues. Understanding impedance and reactance is crucial for accurate calculations in such circuits.
Nax13
A resistance 'R' ohm and inductance of 'L' henry are connected across 240V, 50Hz supply. Power distributed in the circuit is 300W, and the voltage across R is 100V. In order to improve the power factor to unity, the capacitor to be connected in series should have a value of __.
a) 43.7 uF b) 4.37 uF c) 437 uF d) 0.437 uF
Step 1) Using P=V/I, got I=1.25A
Step 2) Using R=VR/I, got R=80 ohm
Step 3) Now since total voltage is 240V, VL is 240-100=140V
Step 4) Using XL=VL/I, got XL=112 ohm.
Step 5) For power factor to be unity, XL=XC, which means that XC should also be equal to 112 ohm, which leads me to the answer that C is 28.4uF. (since XC=1/2πfC)
Where did I go wrong? Any help would be appreciated. :wink:
First line (ignoring the typo. P=V/I), you used P=VI to find I. This is incorrect, VI is the apparent power if you use the total voltage. If however you just use the voltage across the resistor ...
BTW. It is a poor exercise to refer to this a merely "power factor correction". Series resonating out a reactive element like this does a lot more than merely correcting power factor. In this case for example it increases the total power by a multiple of about 6. If the load was designed to run at 300W then it would likely be destroyed.
This is why PFC is normally done with a parallel capacitor.
Why is it necessary to calculate the impedance?
Btw, are all my other steps right?
Because you want to find the reactance "X". So find the resistance "R", find the impedance magnitude |Z| and use R^2 + X^2 = |Z|^2 to solve for X.
Thanks for your help, uart and tim! :)