A 1450 RPM pump with a bronze impeller is recommended for pumping chilled water due to its resistance to corrosion from water treatment chemicals, unlike aluminum or steel impellers. The specific RPM is crucial as operating at maximum RPM can reduce the pump's lifespan. The required gallons per minute (GPM) and head pressure are determined by the project’s Mechanical Engineer, who calculates the system's needs based on cooling coil tonnage. These calculations guide the pump manufacturer in selecting the appropriate impeller and motor specifications. Replacing a motor with one outside the recommended RPM range can lead to flow issues and premature motor failure.
maxx_payne
Messages
86
Reaction score
0
why is it recommended to use a 1450 rpm pump with a bronze impeller for pumping chilled water to the chillers ?
 
Engineering news on Phys.org
Ask the chiller manufacturer or whoever made the recommendadtion.
 
it depends on national codes or proejct's specs. Sometimes the impeller is better to be SS than bronze. And the rpm rating is the recommended for any pump because using the pump at its maximum rpm would shorten its life cycle... hope it did u any good
 
The bronze impeller part is the easiest to answer. The use of bronze is because the chemicals used to treat the water will corrode an aluminum impeller, the water will rust a steel impeller, and a stainless steel impeller is about 3 to 4 times the cost of a bronze impeller with no noticable improvement in performance.

The rotation per minute (RPM) of the pump drive motor vary greatly depending on things like gallon per minute (GPM) needed in the system, head pressure of the system (the force to push the water through the piping), impeller size and pitch, etc. Some pumps may have a 1075 RPM drive motor, some may have a 1350 RPM drive motor, while others may have an 800 RPM drive motor.

The project Mechanical Engineer determines the GPM of water needed for the system based on the tonnage of the cooling coils present on the project. They then figure the length and rise of the piping needed on the project. These calculations are then submitted to the pump manufacturer who then sizes the impeller needed with the drive motor to match based on these calculations along with the voltage and amperage ratings submitted by the Mechanical Engineer.

If replacing the drive motor, it is always best to replace the motor with the exact RPM range of the motor. If it is not it can cause issues such as a loss in GPM, an increase in GPM (which can be worse than being under in flow), and can cause the drive motor to have an over design in amperage causing premature failure in the drive motor.
 
Posted June 2024 - 15 years after starting this class. I have learned a whole lot. To get to the short course on making your stock car, late model, hobby stock E-mod handle, look at the index below. Read all posts on Roll Center, Jacking effect and Why does car drive straight to the wall when I gas it? Also read You really have two race cars. This will cover 90% of problems you have. Simply put, the car pushes going in and is loose coming out. You do not have enuff downforce on the right...
Thread 'Physics of Stretch: What pressure does a band apply on a cylinder?'
Scenario 1 (figure 1) A continuous loop of elastic material is stretched around two metal bars. The top bar is attached to a load cell that reads force. The lower bar can be moved downwards to stretch the elastic material. The lower bar is moved downwards until the two bars are 1190mm apart, stretching the elastic material. The bars are 5mm thick, so the total internal loop length is 1200mm (1190mm + 5mm + 5mm). At this level of stretch, the load cell reads 45N tensile force. Key numbers...
I'm trying to decide what size and type of galvanized steel I need for 2 cantilever extensions. The cantilever is 5 ft. The space between the two cantilever arms is a 17 ft Gap the center 7 ft of the 17 ft Gap we'll need to Bear approximately 17,000 lb spread evenly from the front of the cantilever to the back of the cantilever over 5 ft. I will put support beams across these cantilever arms to support the load evenly
Back
Top