Circuit Breaker Sizing for Distribution Board (D.B1 & D.B2): Confusion Resolved

AI Thread Summary
The discussion centers on the sizing of miniature circuit breakers (MCBs) for two distribution boards (D.B1 and D.B2) in Sudan, focusing on their compliance with safety standards. D.B1 operates at 400V with various feeders using 16A and 25A MCBs, while D.B2 operates at 230V with feeders using 16A and 32A MCBs. Participants emphasize the importance of adhering to IEC standards for low voltage equipment and ensuring proper short circuit protection and load isolation. Key considerations include the normal and inrush current ratings, fault isolation, and coordination of protection devices. The conversation highlights the critical role of well-designed distribution systems in maintaining operational safety and reliability in UPS applications.
Ahmed Fadl El
Messages
2
Reaction score
0
I have Distribution board, Outgoing (D.B1)
But I got confuse for MCB sizing:
The busbar 400V, 125A, 50Hz, 4P, 10KA for 1Sec.
The part of Outgoing Rates as the followings:
Feeder-1: 2.5 KVA used 25A MCB 2P
Feeder-2: 3.5 KVA used 25A MCB 2P
Feeder-3: 2.0 KVA used 25A MCB 2P
Feeder-4: 1.0 KVA used 16A MCB 2P
Feeder-5: 1.5 KVA used 16A MCB 2P

Onother one (D.B2):
The busbar 230V, 100A, 1PH, 50Hz, 4P, 10KA for 1Sec.
The part of Outgoing Rates as the followings:
Feeder-1: 2 KW used 16A MCB 2P
Feeder-2: 2 KW used 16A MCB 2P
Feeder-3: 2 KW used 32A MCB 2P
Feeder-4: 2 KW used 32A MCB 2P
Feeder-5: 1 KW used 16A MCB 2P

Is the above Rating acceptable, since they used different rate with same load in the D.B2
 
Engineering news on Phys.org
Ahmed Fadl El said:
I have Distribution board, Outgoing (D.B1)
But I got confuse for MCB sizing:
The busbar 400V, 125A, 50Hz, 4P, 10KA for 1Sec.
The part of Outgoing Rates as the followings:
Feeder-1: 2.5 KVA used 25A MCB 2P
Feeder-2: 3.5 KVA used 25A MCB 2P
Feeder-3: 2.0 KVA used 25A MCB 2P
Feeder-4: 1.0 KVA used 16A MCB 2P
Feeder-5: 1.5 KVA used 16A MCB 2P

Onother one (D.B2):
The busbar 230V, 100A, 1PH, 50Hz, 4P, 10KA for 1Sec.
The part of Outgoing Rates as the followings:
Feeder-1: 2 KW used 16A MCB 2P
Feeder-2: 2 KW used 16A MCB 2P
Feeder-3: 2 KW used 32A MCB 2P
Feeder-4: 2 KW used 32A MCB 2P
Feeder-5: 1 KW used 16A MCB 2P

Is the above Rating acceptable, since they used different rate with same load in the D.B2

Welcome to the PF.

What country are you in? What government regulating body sets the safety standards for these components? What publication has these safety standards and component sizing requirements in it?
 
berkeman said:
Welcome to the PF.

What country are you in? What government regulating body sets the safety standards for these components? What publication has these safety standards and component sizing requirements in it?


Dear berkeman,
Thanks a lot for your response,
My Country : Sudan
The government regulating body sets the safety standards for these components: The latest edition of the following codes, regulations and standards:
• IEC 60146 Low voltage switchgear and control gear
• IEC 60269 Low voltage fuses
• IEC 60408 Low voltage air break switches, air break disconnectors, air break
switch disconnectors and fuse combination units

So these Outgoing Distribution board for 230V AC UPS, 20KVA for FPF Feild Production Facilities in oil field.

The part of Outgoing Rates as the followings:
Feeder-1: 2.5 KVA used 25A MCB 2P For Building fire alarm system
Feeder-2: 3.5 KVA used 25A MCB 2P For Emergency Shutdown System
Feeder-3: 2.0 KVA used 25A MCB 2P For Operator Station
Feeder-4: 1.0 KVA used 16A MCB 2P For Microwave system
Feeder-5: 1.5 KVA used 16A MCB 2P For PAGA System

Onother one (D.B2):
The busbar 230V, 100A, 1PH, 50Hz, 4P, 10KA for 1Sec.
The part of Outgoing Rates as the followings:
Feeder-1: 2 KW used 16A MCB 2P For Building fire alarm system
Feeder-2: 2 KW used 16A MCB 2P For Emergency Shutdown System
Feeder-3: 2 KW used 32A MCB 2P For Operator Station
Feeder-4: 2 KW used 32A MCB 2P For Microwave system
Feeder-5: 1 KW used 16A MCB 2P For PAGA System
 
There are three critical functions of a well designed UPS ac distribution system. First, short circuit protection of all underground conductors; second, isolation of panel pull-down during a branch fault; and third, isolation of the critical loads from electrical noise coupled through the static bypass. The power distribution system will usually consist of a panelboard, with circuit-breakers or fuses to protect the individual branch circuit conductors which will usually be run in conduits dedicated to these uninterruptible circuits. Indeed each distribution panel has related output cable circuit running which dictates its suitable feeder protection selection.
Branch circuit breakers are selected based upon the voltage rating, the normal full load current of each branch circuit load (continuous and intermittent loads), the inrush current and its duration for each branch circuit load, the maximum time each connected load can tolerate a loss of voltage without failure (time for failure), and the available short circuit current at the uninterruptible ac main bus through the inverter or the bypass circuit when a static transfer switch is used (to be obtained from the UPS system vendor or calculated). When a fault (or short circuit) occurs on a branch circuit, the branch circuit breaker or fuse must isolate the fault before the UPS protective devices operate and trip the entire system. When this condition is fulfilled, the protection system is said to be coordinated. Fuses or circuit breakers of different ratings can be coordinated, so a main panelboard may supply a downstream panel if necessary, however, it rarely is necessary and should be avoided. Molded case circuit breakers (miniature circuit breakers) are instantaneous in action at currents above 8 to 10 times their continuous current rating. Since the UPS has limited output current, additional power for clearing fault currents rapidly may be provided from an alternate high power source by the use of a static switch. When a fault occurs on any branch circuit, the inverter reaches the current limit condition and the bus voltage falls almost to zero, thus depriving all branch circuit loads of power. The permissible duration of this loss of power must be longer than the clearing time of the breaker plus the transfer switching time in the UPS if the coordination is to be obtained.



------------------------------------
Creative thinking is enjoyable, Then think about your surrounding things and other thought products. http://electrical-riddles.com
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Thread 'Beauty of old electrical and measuring things, etc.'
Even as a kid, I saw beauty in old devices. That made me want to understand how they worked. I had lots of old things that I keep and now reviving. Old things need to work to see the beauty. Here's what I've done so far. Two views of the gadgets shelves and my small work space: Here's a close up look at the meters, gauges and other measuring things: This is what I think of as surface-mount electrical components and wiring. The components are very old and shows how...

Similar threads

Replies
42
Views
4K
Back
Top