Current Transformer Accuracy Under %5 Load Level

AI Thread Summary
Current transformers (CTs) exhibit varying accuracy based on load levels, with manufacturers providing specifications primarily for loads above 5%. Below this threshold, accuracy can be uncertain, leading to potential readings of 0.00mA in the secondary circuit when primary currents are low, such as 50A in a 4000/5A CT. Some manufacturers label this as an "unstable zone," indicating that performance may not be guaranteed. Special accuracy classes (0.2S and 0.5S) have lower limitations of 1%, but conventional classes maintain a 5% threshold. Additionally, low burden conditions can also contribute to accuracy loss, raising concerns about the reliability of readings in such scenarios.
HakanEryurt
Messages
2
Reaction score
0
Hello , I would like to ask one question. Current transformers has one of the major component in electricity but we know that per load level, VA, temperature ext accuracy of these transformers can change. CT manufacturers gives accuracy diagrams for different load levels from %5 load to full load. But what is happening when the load level is lower than %5. For example if you have 4000/5 current transformer to measure current and if you have load that can go down for sometime to 50A in primary, is it possible that you can have 0.00mA in secondary?

Some CT manufacturers written specs as <%5 zone unstable zone, where there is no value for accuracy or there is no warranty that CT's are working probably. Is there any technical study that investigate <%5 load conditions?
 
Engineering news on Phys.org
Yes, for conventional measuring transformers with accuracy class of 0.1, 0.2, 0.5,1,3 and 5 this limitation is %5 but for special current transformers with accuracy class of 0.2S and 0.5S this limitation is %1. Error limits for measuring current transformer cores is defined by DIN VDE 0414-1 and IEC 60185

For Measuring core rated output: 2.5 – 5.0 – 10 – 15 – 30 VA; burden output factor = 0.8

Classes: 0.1 – 0.2 – 0.5 – 1: valid in the range of 25 % and 100 % of the rated burden.
Classes: 0.2 s and 0.5 s: For special applications (electrical meters that measure correctly between 50 mA and 6 A, i.e. between 1% and 120% of the rated current of 5A)
Classes: 3 – 5: valid in the range 50% to 100% of the rated burden Label: measuring cores are identified by a combination of the rated output with the overcurrent limit factor and with the class, e.g.

15 VA class 0.5 FS 10
15 VA class 0.5 ext. 150%

-----------------------------------------------------------------
Creative thinking is enjoyable, Then think about your surrounding things and other thought products. http://electrical-riddles.com
 
Thank you for your answer. So if you have Class 0.5 current transformer for reactive power compansation, and if utility has 0.5s current tranformer for billing your compansation will not work properly and you can be charged for reactive energy.

But I need to understand why we read 0.00mA or very less current compared to primer in current transformer when there is 50A primer current in 4000/5A current transformer. Where are we loosing this secondary current?

As far as I understood these classes are specified in maximum burden. So my second question is if have a CT of 30VA burden and if we have load of max 0.3VA . Is there any accuracy loss also due to low burden?
 
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
Thread 'How Does Jaguar's 1980s V12 Dual Coil Ignition System Enhance Spark Strength?'
I have come across a dual coil ignition system as used by Jaguar on their V12 in the 1980's. It uses two ignition coils with their primary windings wired in parallel. The primary coil has its secondary winding wired to the distributor and then to the spark plugs as is standard practice. However, the auxiliary coil has it secondary winding output sealed off. The purpose of the system was to provide a stronger spark to the plugs, always a difficult task with the very short dwell time of a...
Back
Top