Delta Transformers on Wye Distribution System

  • Thread starter Josh111
  • Start date
  • #1
37
0
Hopefully this has not already been asked. It would be hard to do a forum search with the right words to find it if it has been already.

I am wondering if it is ever possible or common place to generate power in a Wye generation scheme and then connect it directly to a transformer with a Delta primary.

If this is done, what would be the major setbacks.

Also, how would one MCOV ratings of elbow arrestors at the high side of a transformer?
 

Answers and Replies

  • #2
1,184
223
I am wondering if it is ever possible or common place to generate power in a Wye generation scheme and then connect it directly to a transformer with a Delta primary.
Possible of course.
 
  • #3
jim hardy
Science Advisor
Gold Member
Dearly Missed
9,839
4,882
That's how our central station main generator is connected to the main stepup transformer. Generator neutral was resistance grounded .

I dont know anything about the surge arrestors.
 
  • #4
dlgoff
Science Advisor
Gold Member
3,940
1,914
That's how our central station main generator is connected to the main stepup transformer. Generator neutral was resistance grounded .

I dont know anything about the surge arrestors.
I found this Addressing Ground Faults on MV Generators from our old friend, http://ecmweb.com/. They address advantages/disadvantages of Low & high impedance grounding and single & multiple point grounding. Then they show an optimal Hybrid grounding solution.

907ecmPQfig7.jpg



I Love their site. :approve:
 
  • Like
Likes jim hardy
  • #5
1,184
223
Big sync generators (Sn>50 MVA) I know of, are directly grounded (at least that's the practice in my country). However, I know case where a relatively small generator (Sn< 10 MVA) is grounded via quite a large Petersen coil.
 
  • #6
jim hardy
Science Advisor
Gold Member
Dearly Missed
9,839
4,882
Big sync generators (Sn>50 MVA) I know of, are directly grounded (at least that's the practice in my country). However, I know case where a relatively small generator (Sn< 10 MVA) is grounded via quite a large Petersen coil.

I find that surprising. The reason for the resistor is to limit current to just a few amps should a ground fault develop, so there's not an electrical explosion.
Our machine was 894MVA at 22kv. Ten amps at 22kv is of course 220KW so the grounding resistor was big as a pickup truck. A relay monitors the voltage across it and trips the unit in case of a ground fault.
That design pays off - at another plant somebody left a wrench inside the generator. When it fell shorting one terminal to frame the unit tripped on "ground fault" with no damage, just had to go in and retrieve the wrench.
 
  • #7
1,184
223
I find that surprising. The reason for the resistor is to limit current to just a few amps should a ground fault develop, so there's not an electrical explosion.
Our machine was 894MVA at 22kv. Ten amps at 22kv is of course 220KW so the grounding resistor was big as a pickup truck. A relay monitors the voltage across it and trips the unit in case of a ground fault.
That design pays off - at another plant somebody left a wrench inside the generator. When it fell shorting one terminal to frame the unit tripped on "ground fault" with no damage, just had to go in and retrieve the wrench.
Jim, you are right! I rechecked my data and big generators in my country are also impedance-grounded on regular basis. I don't know why but seems I confused generators data with HV power transformers...o:)
 

Related Threads on Delta Transformers on Wye Distribution System

  • Last Post
Replies
2
Views
12K
Replies
5
Views
7K
Replies
1
Views
4K
Replies
5
Views
5K
Replies
7
Views
1K
Replies
1
Views
1K
  • Last Post
Replies
13
Views
54K
  • Last Post
Replies
5
Views
16K
Replies
5
Views
3K
Replies
1
Views
2K
Top