Delta Transformers on Wye Distribution System

Click For Summary

Discussion Overview

The discussion revolves around the feasibility and implications of connecting a Wye generation scheme directly to a transformer with a Delta primary. Participants explore grounding practices for generators and the use of surge arrestors in this context, raising questions about potential setbacks and safety measures.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested

Main Points Raised

  • One participant questions the commonality and feasibility of connecting a Wye generation scheme to a Delta primary transformer, seeking insights on major setbacks.
  • Another participant confirms that such connections are possible, referencing their own experience with a central station main generator connected to a step-up transformer.
  • Grounding practices for generators are discussed, with one participant noting that large synchronous generators are typically directly grounded, while smaller generators may use a Petersen coil.
  • Concerns are raised about the purpose of grounding resistors, particularly in preventing electrical explosions during ground faults, with an example provided of a successful ground fault trip without damage.
  • One participant acknowledges a previous misunderstanding regarding grounding practices, clarifying that large generators in their country are also impedance-grounded regularly.

Areas of Agreement / Disagreement

Participants express differing views on grounding practices for generators, with some advocating for direct grounding and others noting the use of impedance grounding. The discussion remains unresolved regarding the best practices and implications of connecting Wye generation to Delta transformers.

Contextual Notes

Participants reference specific grounding methods and their advantages or disadvantages, but the discussion does not resolve the technical details or assumptions behind these practices.

Josh111
Messages
37
Reaction score
0
Hopefully this has not already been asked. It would be hard to do a forum search with the right words to find it if it has been already.

I am wondering if it is ever possible or common place to generate power in a Wye generation scheme and then connect it directly to a transformer with a Delta primary.

If this is done, what would be the major setbacks.

Also, how would one MCOV ratings of elbow arrestors at the high side of a transformer?
 
Engineering news on Phys.org
Josh111 said:
I am wondering if it is ever possible or common place to generate power in a Wye generation scheme and then connect it directly to a transformer with a Delta primary.
Possible of course.
 
That's how our central station main generator is connected to the main stepup transformer. Generator neutral was resistance grounded .

I don't know anything about the surge arrestors.
 
jim hardy said:
That's how our central station main generator is connected to the main stepup transformer. Generator neutral was resistance grounded .

I don't know anything about the surge arrestors.
I found this Addressing Ground Faults on MV Generators from our old friend, http://ecmweb.com/. They address advantages/disadvantages of Low & high impedance grounding and single & multiple point grounding. Then they show an optimal Hybrid grounding solution.

907ecmPQfig7.jpg
I Love their site. :approve:
 
  • Like
Likes   Reactions: jim hardy
Big sync generators (Sn>50 MVA) I know of, are directly grounded (at least that's the practice in my country). However, I know case where a relatively small generator (Sn< 10 MVA) is grounded via quite a large Petersen coil.
 
zoki85 said:
Big sync generators (Sn>50 MVA) I know of, are directly grounded (at least that's the practice in my country). However, I know case where a relatively small generator (Sn< 10 MVA) is grounded via quite a large Petersen coil.

I find that surprising. The reason for the resistor is to limit current to just a few amps should a ground fault develop, so there's not an electrical explosion.
Our machine was 894MVA at 22kv. Ten amps at 22kv is of course 220KW so the grounding resistor was big as a pickup truck. A relay monitors the voltage across it and trips the unit in case of a ground fault.
That design pays off - at another plant somebody left a wrench inside the generator. When it fell shorting one terminal to frame the unit tripped on "ground fault" with no damage, just had to go in and retrieve the wrench.
 
jim hardy said:
I find that surprising. The reason for the resistor is to limit current to just a few amps should a ground fault develop, so there's not an electrical explosion.
Our machine was 894MVA at 22kv. Ten amps at 22kv is of course 220KW so the grounding resistor was big as a pickup truck. A relay monitors the voltage across it and trips the unit in case of a ground fault.
That design pays off - at another plant somebody left a wrench inside the generator. When it fell shorting one terminal to frame the unit tripped on "ground fault" with no damage, just had to go in and retrieve the wrench.
Jim, you are right! I rechecked my data and big generators in my country are also impedance-grounded on regular basis. I don't know why but seems I confused generators data with HV power transformers...o:)
 

Similar threads

  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 8 ·
Replies
8
Views
3K
Replies
9
Views
2K
  • · Replies 11 ·
Replies
11
Views
6K
  • · Replies 1 ·
Replies
1
Views
5K
  • · Replies 5 ·
Replies
5
Views
6K
  • · Replies 16 ·
Replies
16
Views
4K
Replies
14
Views
3K
  • · Replies 18 ·
Replies
18
Views
5K
  • · Replies 8 ·
Replies
8
Views
11K