cktan22 said:
room size : 3 m x 7 m, height 3 m
heat load : 10000 btu/h
cfm : 644
velocity: 6 m/s
temperature : from 30 celsius to 22 celsius
chilled water flow rate : 30.8 liter/minute
altitude : sea level
Ok. You have a mixture of units so I will use the MKS units. 10000 BTU/h = 2.9 kW = 2900 J/sec.
I am not sure what the heat load means but since I asked for the rate at which energy is removed from the room, I will assume that this is that rate.
Volume of air in room = 63 m
3;
Pressure = 1 atm = 101325 Pa;
Initial T =303K
number of moles of air in room = n = PV/RT = 2534 mol.
The heat capacity of air at constant pressure is Cp = 7R/2 = 29 J/mol K
So to reduce the temperature of that room of air by 8 degrees you have to remove:
Q = 29nΔT = 29 x 2534 x 8 = 588,000 Joules
Since the air conditioner removes 2900 Joules/sec. you would need 588000/2900 = 203 seconds or about 3.5 minutes to cool that room.
I take it that you wanted a ballpark figure. The above assumes that the air flow through the cooling coils of the air conditioner is optimal, ignores the slight increase in mass of the room air as temperature decreases at constant pressure, and ignores the need to remove heat from that extra mass.