Differential protection and auto transfer system

AI Thread Summary
In a low voltage substation with two incoming circuit breakers and a coupling system, a short circuit in one transformer caused the differential relay to trip only the medium voltage circuit breaker, leaving the low voltage bus bar dead. The auto transfer system then closed the coupling circuit breaker, re-energizing the faulted bus bar despite the low voltage circuit breaker not opening in time. Investigations revealed no issues with the low voltage circuit breaker mechanism or circuits. The discussion suggests that miscalibration due to high side impedance may be a factor, and proposes implementing an interlock to prevent auto transfer during such faults. The need for effective protective measures in low voltage systems is emphasized.
m.s.j
Messages
212
Reaction score
1
In a low voltage substation, including two incomings and a coupling circuit breakers, incoming C.Bs are connected to two individual power transformers which are fed from upstream medium voltage system. The two low voltage bus bars are equipped by a fast auto transfer system which is considered for coupling C.B auto closing when one of two bus bars is dead.
Also each transformer is protected by standard differential relay that must trip medium and low voltage C.Bs via fast interposing trip relays.
The problem observed when a short circuit occurred in one of two transformer windings. The differential relay operated and only relevant medium voltage circuit breaker tripped. The fault clearing stage was done successfully and related low voltage bus bar was dead. In this case the auto transfer system closed the low voltage coupling circuit breaker, and the short circuit point energized again.
Indeed, the relevant low voltage C.B of faulty transformer couldn't open on time. Last investigation didn't show any problem in low voltage C.B mechanism or related circuits.
How can you explain the reason of low voltage C.B inactivity?


BEST REGARDS
MSJ


-----------------------------------------------------------------
Creative thinking is enjoyable,Then think about your surrounding things and other thought products. http://electrical-riddles.com
 

Attachments

  • 22.GIF
    22.GIF
    2.3 KB · Views: 483
Engineering news on Phys.org
Perhaps miscalibrated because of abnormal high side impedance.

The solution should be an interlock preventing auto transfer.
 
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...
Hello dear reader, a brief introduction: Some 4 years ago someone started developing health related issues, apparently due to exposure to RF & ELF related frequencies and/or fields (Magnetic). This is currently becoming known as EHS. (Electromagnetic hypersensitivity is a claimed sensitivity to electromagnetic fields, to which adverse symptoms are attributed.) She experiences a deep burning sensation throughout her entire body, leaving her in pain and exhausted after a pulse has occurred...