m.s.j said:
Dear cabraham,
Which your reference book agree your idea (magnetizing current exist just in one side of loaded transformer) clearly. As you say, you know transformer inrush current. Whether it exists in primary side of transformer exclusively? I say No!
All phenomena which related to linkage flux ( magnetizing current) can be observed in both primary and secondary side of transformer, therefore magnetizing current exist in all closed circuit which involved to magnetizing flux.
Meanwhile I don't know why you and your friends in U.S or Europe don't like my website (
http://electrical-riddles.com), however can I record currently discussion in it?
Honestly, I like your web site. It is fun, informative, friendly, & challenging. I didn't know it is yours, but I'd like to say thank you for giving us a good forum.
Due to the different languages in the world, & this being a global forum, maybe it's a language barrier/communication issue. Let's first define the term "exciting curent".
According to Ampere's law, AL for short, for a given "H" field & path length "l", the integral of
H*d
l must equal the
net amp-turns. By *"net"* amp-turns, I mean not balanced by the other winding. In 3 phase units, this can mean that some exciting current harmonics are in the primary, with others in the secondary. I've already detailed this issue.
In single phase units, I'm not aware of this taking place. I never said it cannot happen, I just remarked that the example of a CT does not display exciting current in the secondary.
The primary is by definition the winding connected to the active source supplying power to the xfmr unit. In a CT, the primary is connected in series with the power source & load. A closed path is formed, & the CT provides a low burden, i.e. voltage drop, provided that the terminating impedance on the CT secondary presents an impedance to the CT primary much smaller than the load impedance.
Since the primary is connected to the load & power source circuit, the reactive power to energize & de-energize the core comes from the primary side. Can specific harmonics flow in the secondary, & not in the primary?
In 3 phase units, the triplen harmonics cannot flow in the primary if a high impedance at those frequencies prevents it. A Y primary w/ an open or very high impedance between source & xfmr primary neutrals presents a very high impedance to triplen harmonic currents. As soon as powered up, the flux will begin to distort w/ triplens in the flux waveform.
What happens next? The secondary has a closed path, a delta, w/ low impedance to triplen harmonic currents. The windings have a small wire resistance, plus a small reactance due to leakage inductance. The triplen flux distortion produces a triplen voltage in the secondary/primary. This small voltage across the low impedance of the delta results in triplen currents circulating in the delta.
This triplen current is exciting current, not load current, since it does not get counter-balanced in the primary. The primary cannot draw triplen current to cancel the triplen counter-flux because it has a high impedance to triplens. The triplen delta secondary current generates an mmf opposite in polarity, tending to reduce the triplen core flux.
The equilibrium condition is attained when the delta triplen current exactly cancels the triplen flux. Hence the flux is harmonic free because the triplen flux distortion is canceled by the delta secondary current triplen counter-mmf.
That is why the delta secondary current is regarded as a part of the exciting current. It does not find amp-turns balancing in the primary, & does not power the load, & is independent of loading.
With a CT this condition does not exist. A single phase CT has 2 leads into the primary. These 2 leads provide a low impedance path for exciting current. Are there current harmonics in the secondary? If so, would that be classified as "exciting current"? Maybe we need to examine this some more.
The mmf is pure sine, owing to the source-load circuit, & the CT low input impedance. The sine current results in a sine (no harmonics) mmf. The core flux will have a pure sine "H", & a "B" with harmonic distortion. So the voltages, Vsec & Vpri, will carry harmonics. But the voltage involved is well under 1% of the source voltage.
Hence the harmonics will be well under that 1%, likely 0.2% or so. This will result in very small harmonic current on the secondary side. But these harmonic secondary currents are only slightly canceled by the primary, since it is driven from a high impedance (relatively speaking) network, which looks like a constant current source. The secondary harmonics will generate a counter mmf, which tends to reduce the flux harmonics until equilibrium is reached.
But we are talking a fraction of a percent. You could argue that this secondary harmonic current is mostly unbalanced by the primary mmf, & hence can be considered "exciting current". I'll agree that there are tiny harmonics in the CT secondary unbalanced by primary mmf.
But consider the conventional voltage xfmr. The primary exciting current encounters a very low impedance path in the primary, at the fundamental freq, the 1st. But leakage inductance in said primary presents an impedance for the 3rd harmonic 3 times higher than the 1st. The 5th harmonic of the exciting current sees 5 times higher leakage reactance than the 1st.
Since harmonics of increasing order encounter a continuously increasing impedance due to increased leakage reactance in the primary, the core flux higher harmonics will be almost, but not completely suppressed. Hence the flux will be very slightly distorted. This harmonic voltage in the secondary will give rise to secondary harmonic currents when loaded. These currents are load dependent. Hence I don't think they are exciting current. They tend to cancel the flux harmonics, though, but they get balanced by primary mmf, but not completely due to secondary leakage inductance.
Hence, a small fraction of the secondary current could be classified as exciting current, but it is a very small fraction. Whan harmonic currents flow in the primary, we cannot expect the core flux to carry zero harmonic content. Every primary has wire resistance & leakage reactance. Even w/ superconducting windings, leakage reactance still exists.
How big in value must a secondary harmonic current be to be considered "exciting current"? It does exist, in the CT, as well as VT. So I see how one can make the case. I just feel that when a quantity is large enough to impact performance, safety, etc., it needs to be considered. If triplen harmonics in 3 phase xfmrs were inadequately suppressed, insulation could be stressed to the point of shortening life, & customer voltages have large peaks due to distortion.
Including secondary delta windings suppresses these harmonics, curing the ill effects. With single phase units, I'll concede that there is indeed some level of current harmonics in the secondary uncancelled by primary mmf. But is it enough to stress insulation, distort waveforms, reduce safety, etc.? If not, then it is clear that the
significant current which suppresses harmonics is found in the primary. The secondary harmonics are not strong enough to adequately suppress flux distortion.
Did I get it right? Anything else that needs mentioning?
Claude