  1. Dec 21, 2015 #1
    I have a 40x60 by 14 foot garage... 3 walls are R19... one wall maybe about a R10 (garage doors, somewhat well sealed) ceiling is R30...

    (how would I calculate in BTU for raising the temperature from 40 degrees F to 60 degrees F in say four hours with an outdoor temperature of 20 degrees with a humidity of 60%?
    It's been a long time since HS physics, and any abbreviations you use, please explain label (delta equals change, etc)


    (online calculators that I have found only figure in for it to be in a constant on/off cycle like a usual house, not a garage that I only want to heat once a week.)

    Feel free to guesstimate any variables I may have missed

    right now, with a underfloor heating working 15 minutes a day to keep the pipes from freezing, it keeps the garage at a pretty constant 40 degrees when it is 20 degrees out.

    Feel free to just explain given a sealed box with no heat loss .. im having a heck of a time trying to figure out any of this.. .. im just trying to figure out how to go about this... any help would be appreciated.
     
  2. jcsd
  3. Dec 21, 2015 #2
    A thermostat, some kind of simple heater, and a cheap timer?
     
  4. Dec 21, 2015 #3
    im trying to figure out how much more heat output i need to accomplish this feat.. I have underfloor heating in 1/3 of it, and it is a very slow process to heat the garage... (12 hours having it on went from 40 to 45 degrees)

    trying to figure out how much more heat i need to accomplish this feat.
     
  5. Dec 21, 2015 #4
    I dont like using the salamander (oil fired unvented heater) in there..

    Want to use hot water radiators with blowers
     
  6. Dec 22, 2015 #5

    russ_watters

    User Avatar

    Staff: Mentor

    It's pretty difficult to calculate the transient case because you need to know the thermal inertia of the space; how much thermal energy the structure and everything in it can hold. But 4 hours is a pretty long time to figure as a warm-up time, so once you calculate the steady state load and add a safety factor (say, 50%), you should be able to achieve what you are trying to get.

    So, the heat transfer through each wall in steady state is 1/R*A*dT. I'm not clear on the floor - is it insulated as well, under the radiant heating? I suppose the floor won't matter too much since you aren't going to make the garage much warmer than the ground under the floor.
     
  7. Dec 22, 2015 #6
    ummm... I took a simple physics class back in like 9th grade...

    1/(radiancy?) times area times change in temperature?
    (is trying to study radiancy, but honestly am not getting it)

    I havent even been able to figure out the heat required even if there is no heat loss at all...
     
  8. Dec 22, 2015 #7
    Russ had the right idea, assuming his 50% safety factor is in the ballpark for the effect of the thermal inertial of the walls, floor, and air. Since the current steady state operating point of your system is already established, it is simpler just to look at the incremental changes relative to the present steady state operation. You are trying to raise the inside temperature 20 F, with no change in the outside temperature. During the heat-up, the incremental temperature difference for heat loss is going to rise from 0 F to 20 F. So, as a worst case, you can just assume that the temperature difference is 20 F the entire time. This will give you an upper bound on the heat supply required. So, for each of the walls, you use a 20 F incremental temperature difference across the wall, and calculate the incremental heat loss over 4 hours using Russ's equation (20)A(3600 sec x 4)/R, where A is the area of the wall.

    In lieu of Russ's 50% factor, now that you've established that the temperature difference across each wall is going to be 20 F higher, you can calculate the additional heat required by thermal inertia of the walls using the heat capacity of each wall, the mass of each wall, and an average temperature rise of 10 F. You can also do the same thing for the room air (although this probably won't be too significant).

    Chet
     
  9. Dec 22, 2015 #8

    russ_watters

    User Avatar

    Staff: Mentor

    That was 1/R-Value. You have all of the information in your first post, but I want you to take a swing at it. :wink:
     
  10. Dec 22, 2015 #9

    russ_watters

    User Avatar

    Staff: Mentor

    FYI, I actually picked it because of a lack of confidence in the inputs.
     
  11. Dec 22, 2015 #10

    OmCheeto

    User Avatar
    Gold Member
    2016 Award

    This simplifies things greatly. How long do you plan on staying in the garage, for this one day of the week?
     
  12. Dec 22, 2015 #11

    sophiecentaur

    User Avatar
    Science Advisor
    Gold Member

    A bit of experimenting could help. Would this be possible?
    There really is no substitute for a situation like this as it's probably not similar enough to domestic heating situations for the tables and calculators to be reliable.
     
  13. Dec 25, 2015 #12
    Plan to stay in the garage at least half a day if i go through the trouble of heating it. I placed a vertical air modine style heater in.... (a hot water (180 degree)radiator with a fan on it, that I have a hard time getting information on to figure out what kind of output it should be. (Dunham-Bush 0-300-GA) (300,000 btu?, but that designation is probably on steam, not 180 degree water, so maybe an output of 200,000?)
     
  14. Dec 25, 2015 #13
    also have 1000 sq feet of underfloor heating in it, but even with 24 hours of use, is difficult to get temp where I would like. I ran both the underfloor and the modine for 12 hours, with a 20 degree outside temperature, garage started at 40 degrees (the floor is on a timer for 15 minutes a day to keep it warm enough under the floor so the lines dont freeze)... and the best I had with both systems is 50 degrees. air inlet temperature of the modine was 40 degrees and outlet 55, (i dont know how many CFM, the motor is different, and like i said, i cant find information on it)

    another day, used it for 12 hours, outdoor temp 40 degrees, starting temperature was 40 degrees and I got it up to 55 in 12 hours
     
  15. Dec 25, 2015 #14

    russ_watters

    User Avatar

    Staff: Mentor

    Doesn't that heater have a nameplate with a make and model number on it?

    Did you do the calculation I suggested for the load?
     
  16. Dec 27, 2015 #15
    sorry.. been working the last few days.

    using an outside temp of 20 and an intended temp of 60 degrees (40 degree diference)
    garage is 40 x60 x14ft ... so the walls together ((40x2) + (60x2)) x14 x (1/19) x 40 degrees + (40x60 x (1/30) x40 degrees Ceiling
    7073 + 3200
    what do i do for the ceiling and the air itself?

    the model is a dunham-bush 0-300-GA but i havent been able to find any information at all!
     
  17. Dec 27, 2015 #16
    (i used r19 for the wall with the garage doors too for this calculation
     
  18. Dec 27, 2015 #17

    OmCheeto

    User Avatar
    Gold Member
    2016 Award

    How is the floor heated?
    The floor heater numbers look kind of goofy:
    900 seconds of operation yields an average temperature of 40°F over 24 hours
    42300 seconds of operation yields an average temperature 45°F over 12 hours​
     
  19. Dec 27, 2015 #18
    I think I found the reason for all of my confusion about R.... I am referring to the R value of the insulation itself, for instance, around here, northern Michigan, expected R values 4 walls are part 19 - 25, and ceiling. I'm thinking you are talking about. Only can access my phone at this point, so can't do much more research tonight
     
  20. Dec 28, 2015 #19
    The floor in the north third of the floor (13 foot by 60) has a grid of 1/2 inch pex aproximately 9 inches apart running 180 degree water through it. (not in it)..(it was a like 20 years ago, so i dont remember the spacing exatly)
     
  21. Dec 28, 2015 #20

    OmCheeto

    User Avatar
    Gold Member
    2016 Award

    Do you know the fluid capacity of the tank, and its wattage rating?
     