Generator neutral grounding (NGR)

Click For Summary
SUMMARY

The discussion focuses on Generator Neutral Grounding (NGR) and the implications of closing earthing switches during parallel operation of generators. It is established that if one earthing switch is closed, it is permissible to close the earthing switches of generator-2 or generator-3 simultaneously, provided there are no simultaneous faults on different machines. Additionally, the resistor used in the NGR must be appropriately sized according to the distributed capacitance of the connected generators.

PREREQUISITES
  • Understanding of Generator Neutral Grounding (NGR)
  • Knowledge of earthing switch operations in parallel generator systems
  • Familiarity with electrical fault conditions in generators
  • Basic principles of resistor sizing for electrical systems
NEXT STEPS
  • Research the design and sizing of resistors for Generator Neutral Grounding systems
  • Study the operational protocols for earthing switches in parallel generator configurations
  • Learn about fault detection and management in multi-generator setups
  • Explore case studies on the impact of simultaneous faults in generator systems
USEFUL FOR

Electrical engineers, power system operators, and professionals involved in the design and maintenance of generator systems will benefit from this discussion.

Asghar Hussain
Messages
3
Reaction score
0
Dear All

here we have two examples of Generator Nuteral Grounding my question about Earth switch closing

Example -1

if three generators are in operation and one earthing switch is closed, can we close generator-2 or generator-3 earthing switch closed at a time of parallel operation? yes or not ?
if not please explain in detail

example 2

this operation has separate NGR no confusion we can closed individually.
 

Attachments

  • DSC04745.JPG
    DSC04745.JPG
    31 KB · Views: 858
Engineering news on Phys.org
I'm sorry you are not finding help at the moment. Is there any additional information you can share with us?
 
if three generators are in operation and one earthing switch is closed, can we close generator-2 or generator-3 earthing switch closed at a time of parallel operation? yes or not ?


Why would you want to close more than one ? Any one grounds all generators that are connected to the bus.

On the other hand, it would hurt nothing provided there are not two simultaneous faults on different machines .

And the resistor should be sized according to distributed capacitance of however many machines you intend it to serve.
 
Most likely this can only be answered by an "old timer". I am making measurements on an uA709 op amp (metal can). I would like to calculate the frequency rolloff curves (I can measure them). I assume the compensation is via the miller effect. To do the calculations I would need to know the gain of the transistors and the effective resistance seen at the compensation terminals, not including the values I put there. Anyone know those values?

Similar threads

  • · Replies 26 ·
Replies
26
Views
3K
Replies
19
Views
2K
  • · Replies 12 ·
Replies
12
Views
4K
  • · Replies 38 ·
2
Replies
38
Views
7K
  • · Replies 33 ·
2
Replies
33
Views
3K
Replies
7
Views
3K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 32 ·
2
Replies
32
Views
4K
  • · Replies 13 ·
Replies
13
Views
6K
  • · Replies 11 ·
Replies
11
Views
4K