DavBav1 said:
I found this picture on the web (see below), going back to my original image in post #1: Can we say that the currents with the fault will be the same as before, but phase A has the additional capacitative current?
And I assume this current is small, so small changes in line currents basically?
The simple answer to that question is "Yes" .
I really recommend you get a copy of "IEEE Green Book", standard 142.
Its early chapters explain clearly the basic principles on which the practice of grounding is built.
Familiarity with it makes a lot of the mysteries of the NEC disappear.
Once you train your brain to think of "ground" as just another wire that goes most everywhere these mysteries become almost intuitive.
DavBav1 said:
But I know the load will continue to work as normal, because its connected line to line and the system is "ungrounded", hence drawing power.
Yes your load current is hopefully so large compared to your capacitive current that the system operates, to all outward appearance, normally .
So it's tempting to make industrial systems ungrounded to promote fault tolerance.
But you need detection of that first fault because should a second one come along on a different phase, now you have a dead short and two electrical explosions one at each fault.
IEEE Green Book's first few chapters explains all this, at length in plain language , then the authors go into extreme detail .
In the real world of industry we
approximate an ungrounded system by grounding it through a considerable resistance - roughly equal to the capacitive reactance of the distributed system.
There's a clever reason for doing that, namely the phenomenon of "ferroresonance".
Should an inductance in the system, say a motor or transformer winding, happen to make a series resonant circuit with that distributed capacitance ,
well,
do you recall from your basic circuits course that the voltage gain of a series resonant circuit is its Q, which is its X/R? Ratio of energy stored to energy dissipated per cycle?( see wikipedia's entry for Q_factor )
That can really happen and the high voltages produced by resonance will pierce the insulation.
So we place some R across the X
C to prevent a high Q resonant situation.
And we monitor for presence of an unwanted ground so we can dispatch maintenance people to find and fix it before a second one comes along and disables the system.
And that's why Grounding is such an important subject.
As always the basics are straightforward. An appreciation of them will justify the highfalutin mathematical treatment given the subject elsewhere.
I said in another thread some years ago,
jim hardy said:
I feel that every EE curriculum should have a 1 credit hour course on IEEE 142, Green Book.
That so many electrical engineers graduate lacking understanding of "Ground" should be an embarrassment to the profession.
Just look at the questions we get here on PF about it.
That's my opinion.
I hope you'll become the 'resident expert' in your outfit.
You'll get a lot of mileage out of your basics..
Good luck in your career -