Help Needed , 110V LED SWICHING CIRCUIT

  • Thread starter Thread starter jeancollin
  • Start date Start date
  • Tags Tags
    Circuit Led
Click For Summary

Discussion Overview

The discussion revolves around designing a circuit for a 110V LED indicator that activates when a switch is closed, specifically in the context of a timer circuit controlling a contactor for an A/C unit. Participants explore various configurations and components to achieve this while minimizing the number of wires used.

Discussion Character

  • Technical explanation
  • Debate/contested
  • Experimental/applied

Main Points Raised

  • One participant suggests placing the LED in parallel with a resistor to light it when the switch is closed, but notes the challenge of needing a ground nearby.
  • Another participant proposes using an additional resistor in series with the LED to manage voltage drops, indicating the need for specific resistance values to ensure proper operation.
  • There is confusion regarding whether the LED or neon bulb is suitable for the application, with some participants suggesting that a neon bulb might be more appropriate due to its characteristics.
  • A participant expresses a desire to keep using the neon bulb despite its limited lifespan, emphasizing the need for the indicator to function without a nearby ground.
  • Participants discuss the implications of using a magnetic reed switch and the requirement for the indicator to illuminate when the switch is closed, complicating the circuit design.
  • There are suggestions to connect the neon bulb across the load without a resistor, but concerns are raised about how to maintain functionality with only two wires running to the switch.
  • One participant acknowledges the potential need to run three wires if no solution can be found that meets the two-wire constraint.

Areas of Agreement / Disagreement

Participants express differing opinions on the best approach to integrate the LED or neon bulb into the circuit. There is no consensus on a definitive solution, and multiple competing views remain regarding the configuration and components to use.

Contextual Notes

Participants highlight limitations related to the availability of a ground connection and the necessity of using only two wires, which complicates the circuit design. There are unresolved questions about the appropriate resistor values and configurations for the LED or neon bulb.

Who May Find This Useful

Individuals working on electrical circuit design, particularly in applications involving indicators and timers, may find this discussion relevant. It may also be of interest to those facing similar constraints in wiring and component selection.

jeancollin
Messages
9
Reaction score
0
I have a simple circuit switching activating a 110V timer but would like to show an LED ON indicator at the switch SW when the switch is closed, I can do this easely enough if I run the wire from the LED to ground but this means I need a ground nearby, so my questions is it possible to place the LED in PARALLEL with a resistance R so that when the switch is closed the LED lights up !.

I only want to run 2 wires to/from my switch hence the problem. if I put my LED in series with the circuit it doesn't work if I put my LED across the switch it works in reverse IE the LED is on when the switch is open.

This must be a simple problem can anyone help ?

LED is 110V AC
 

Attachments

  • P1040349.JPG
    P1040349.JPG
    19.1 KB · Views: 534
Engineering news on Phys.org
That would only light when the timer has also closed the circuit except that there might be some leakage through the timer when it is not closed causing a feint glow You want another R (R2) in series with the LED. Select the main R to give you about 2.6 volts across it and R2 to put a few milliamps through the LED. The LED will have a about 1.6 V across so R2 needs to drop 1 volt. Putting an (another) LED and series R after the switch and then to N will light when SW is closed whether the timer has operated or not.
 
Pumblechook said:
That would only light when the timer has also closed the circuit except that there might be some leakage through the timer when it is not closed causing a feint glow You want another R (R2) in series with the LED. Select the main R to give you about 2.6 volts across it and R2 to put a few milliamps through the LED. The LED will have a about 1.6 V across so R2 needs to drop 1 volt. Putting an (another) LED and series R after the switch and then to N will light when SW is closed whether the timer has operated or not.

Thanks for your quick reply , I'm still confused The LED I have is 110V AC (it does however have a Resistor in series built into it) are you not giving me an answer as if I was using 3V LED or does it not matter can you give me a rough diagram or is that too complicated.

The layout I drew before was purely how I thought it might go but if you a have a better idea please feel free to explain, do you mean that what I have is nearly right but I need to add another R2 in series with the LED and keep R1 (R on my diag) where it is ? what would the values be for R1 and R2 approx so that the 110V LED lights (i think it draws about 0.8mA).

The Timer operates an ondelay to activate a NC contactor to switch off an A/C unit, it all works great its just that sometimes I don't have an Earth to locate onto so that my panel light is on when the contactor is operating.

thanks for you help so far...
 
Maybe it is neon you have? Sounds like it is not suitable. You need an LED which develops 1.6 - 2 volts with a few mA running through it.

R1 is in series the LED and the two are in parallel with R.
 
As pumblechook implies, this is often done with a neon bulb. You might be better off using a switch with integral neon lamp.
 
yes your right its a neon but I would like to continue using them if I can although I checked and they only last 5000 hours !

http://uk.rs-online.com/web/search/...d=searchProducts&searchTerm=237-0395&x=26&y=5

I'm sure it can still be done though, I'm using a reed switch and a magnet but the light must go on (since its a locating light) when the switch is closed ie when the magnet is removed away from the reedswitch
 
Phrak said:
As pumblechook implies, this is often done with a neon bulb. You might be better off using a switch with integral neon lamp.

Thank you for your suggestion but I must stick to my magnetic reed switch and the integral light must work when the switch is closed, in fact its easy to make it work the reverse you just put the light across the switch in Parallel.

the hard bit is the opposite when there is no obvious ground otherwise I would run another cable but I'm trying to stick to 2 cables, when there is an obvious ground like metal perlin then you connect the other side of the neon to it and bingo it works since when the switch is closed the live goes through the light onto the ground...

pumblechook please see pics too.

Regards to both for help, now what do I do ?
 

Attachments

  • P1040334.JPG
    P1040334.JPG
    26.6 KB · Views: 488
  • P1040335.JPG
    P1040335.JPG
    24.6 KB · Views: 518
  • P1040324.JPG
    P1040324.JPG
    48.1 KB · Views: 499
Last edited:
In that case you would want to place the neon bulb electrically across the load. No resistor is required. If you want it physically located at the switch, the bulb is connected to neutral and the switch wipper (per your sketch).
 
Phrak said:
In that case you would want to place the neon bulb electrically across the load. No resistor is required. If you want it physically located at the switch, the bulb is connected to neutral and the switch wipper (per your sketch).

I do want it located physically at the switch as that is the indicator that the system is in GREEN mode hence saving electricity when the timer is started . I understand what you mean when you say that I must connect it as per my diagram but what must be R so that it still sends 110V to the bulb and acts as a contact between the wiper and the load side of the timer, in other words if I just put the neon bulb in place of R it would not work right ? so then what resistance would be sufficient to give me a voltage drop of 110V and yet offer a circuit from wiper to timer on the live side.

I thank you again for your help and hope that you understand what I'm trying to say.

Criteria

Light on when Timer is on
Light Must be at switch
only 2 wires to switch (Neutral and Live)


Options

When there is a Earth nearby, yes its true that I can dump the neon neutral side to it but its not always the case when working with clients who don't have nearby Earth source or in Concrete walls ect...
 
  • #10
jeancollin said:
I do want it located physically at the switch as that is the indicator that the system is in GREEN mode hence saving electricity when the timer is started . I understand what you mean when you say that I must connect it as per my diagram ...

Hold on. I've confused you. Sorry. The switch has two ends. I'll call them "hot" and "load."

Connect one lead of the bulb to the neutral wire and other lead to the switch's load end.
 
  • #11
Phrak said:
Hold on. I've confused you. Sorry. The switch has two ends. I'll call them "hot" and "load."

Connect one lead of the bulb to the neutral wire and other lead to the switch's load end.

Yes that would work but then remember that the only part of 2 wires that run into the switch are the live and the switched live result and I don't really want to run 3 wires since the distance between the entrance switch and the fusebox may as much as 20 meters in some cases and I'm doing more than just one home installation.

If there is no solution then I will have to run 3 wires and in your case you are right any neutral or an Earth would work in fact the advantage of running 3 wires with an Earth is that if you cut the wire by accident you have a safety.

My switch wiper should be drawn the other way too ! I was just doing a quick illustrative sketch...

Is there really no way in which I can put the Neon in parallel with a Resistor so that the voltage drops to the Neon is 110V and yet there is enough juice to power the 1W Timer.
 
  • #12
jeancollin said:
Yes that would work but then remember that the only part of 2 wires that run into the switch are the live and the switched live result and I don't really want to run 3 wires since the distance between the entrance switch and the fusebox may as much as 20 meters in some cases and I'm doing more than just one home installation.

If there is no solution then I will have to run 3 wires and in your case you are right any neutral or an Earth would work in fact the advantage of running 3 wires with an Earth is that if you cut the wire by accident you have a safety.

My switch wiper should be drawn the other way too ! I was just doing a quick illustrative sketch...
no, it's fine either way
Is there really no way in which I can put the Neon in parallel with a Resistor so that the voltage drops to the Neon is 110V and yet there is enough juice to power the 1W Timer.

I don't understand why you need a third wire, no following where various curcuit elements are, but in any case...

The load is one Watt, you say, so it draws 10 milliamps. I think we can assume that it draws 10 milliamps whether it has timed-out or not. That's enough to light an LED rather dimely.

If I absolutely couldn't obtain neutral and switched-power where I wanted it, I would try two small LEDs in parallel with each other. Put them antiparallel to each other--anodes tied to cathodes. Put the pair between the switch and the load.
 
  • #13
Phrak said:
no, it's fine either way

I don't understand why you need a third wire, no following where various curcuit elements are, but in any case...

The load is one Watt, you say, so it draws 10 milliamps. I think we can assume that it draws 10 milliamps whether it has timed-out or not. That's enough to light an LED rather dimely.

If I absolutely couldn't obtain neutral and switched-power where I wanted it, I would try two small LEDs in parallel with each other. Put them antiparallel to each other--anodes tied to cathodes. Put the pair between the switch and the load.

OK will try that remember they are not LED as discoverred they are NEON's...will that still allow the current to flow to the load ? furthermore the LED needs to light up as much as poss to show the keyholder where he must place them in order to restore power upon returning to his condo in sometime dark entranceways.

Thank you so much for your help and will keep you posted on the parallel LED issue, as i might have to swap to LEDS as NEON green only have predicted lifespan of 5000 hours !

Also as an option could I use a standard 3V LED and a resistor and drop 3V across it thus giving me what I want ?
 
  • #14
At 10 mA a modern LED will be pretty bright. I have used some at less that 1 mA. So you could just put one in series with the timer (will only light when the timer is closed unless there is a small current when it is open). You will need a second LED (or a diode) in reverse parallel with the first if you are using AC.
 
  • #15
Phrak said:
no, it's fine either way

I don't understand why you need a third wire, no following where various curcuit elements are, but in any case...

The load is one Watt, you say, so it draws 10 milliamps. I think we can assume that it draws 10 milliamps whether it has timed-out or not. That's enough to light an LED rather dimely.

If I absolutely couldn't obtain neutral and switched-power where I wanted it, I would try two small LEDs in parallel with each other. Put them antiparallel to each other--anodes tied to cathodes. Put the pair between the switch and the load.

Pumblechook said:
At 10 mA a modern LED will be pretty bright. I have used some at less that 1 mA. So you could just put one in series with the timer (will only light when the timer is closed unless there is a small current when it is open). You will need a second LED (or a diode) in reverse parallel with the first if you are using AC.

Ok got some results using a range of R in Parallel with an LED if I use the LED on its own it lights but doesn't operate the timer I tried several LED together and they helped to start the timer but then failed when the small current the CONTACTOR draws.

So then I decided to use just one LED in Parallel with a range of R from 75k to 1k measuring the current in the circuit and observing the LED brightness and seeing if it operates the timer (30 sec ONDELAY) and contactor in turn

R mA LED TimerOK ConOK
75K 2.2 High Y N
22K 5.5 Med Y Y
10K 8.3 Med Y Y
5.6K 11.5 Low Y Y
1K 16.5 Off Y Y

from the above results it looks like I could get away with using a Resistance in the range 10 to 50K but anything outside that and the light either doesn't come on with low resistance or with high resistance the timer doesn't get enough Juice.
 
Last edited:
  • #16
jeancollin said:
Ok got some results using a range of R in Parallel with an LED if I use the LED on its own it lights but doesn't operate the timer I tried several LED together and they helped to start the timer but then failed when the small current the CONTACTOR draws.

So then I decided to use just one LED in Parallel with a range of R from 75k to 1k measuring the current in the circuit and observing the LED brightness and seeing if it operates the timer (30 sec ONDELAY) and contactor in turn

R mA LED TimerOK ConOK
75K 2.2 High Y N
22K 5.5 Med Y Y
10K 8.3 Med Y Y
5.6K 11.5 Low Y Y
1K 16.5 Off Y Y

from the above results it looks like I could get away with using a Resistance in the range 10 to 50K but anything outside that and the light either doesn't come on with low resistance or with high resistance the timer doesn't get enough Juice.

Phrak said:
no, it's fine either way

I don't understand why you need a third wire, no following where various curcuit elements are, but in any case...

The load is one Watt, you say, so it draws 10 milliamps. I think we can assume that it draws 10 milliamps whether it has timed-out or not. That's enough to light an LED rather dimely.

If I absolutely couldn't obtain neutral and switched-power where I wanted it, I would try two small LEDs in parallel with each other. Put them antiparallel to each other--anodes tied to cathodes. Put the pair between the switch and the load.

Pumblechook said:
At 10 mA a modern LED will be pretty bright. I have used some at less that 1 mA. So you could just put one in series with the timer (will only light when the timer is closed unless there is a small current when it is open). You will need a second LED (or a diode) in reverse parallel with the first if you are using AC.

OK I have measured the Current drawn By the timer at 16.5mA and the GREEN NEON light at 1mA, So what safe value Resistor shall I use to have the light on when the timer is on assuming the resistor is placed as per my orginal diagram. (in parallel with the NEON).

I have in practice made a 22K R work and the current draw in the circuit has dropped to 5.5mA when the green light is on and the timer is operating but why has the current dropped ? problem is the higher R the Brighter the LED but the less current is being passed to the Timer to the point where it won't operate at all.

Shall I just stick to 22K is that a safe value that won't overheat ? I want to understand the theory so if one of you guys could explain it to me what is happening ?

Also should this circuit be fused with a ?mA fuse just to be safe as I'm running on 110V on a 2x 20AWG sometimes distances of up to 20M, I know the current draw is small but what worries me is shorts in the even of a wire tear. Can I just put a little fuse near the timer on the Live side ?

Also I feed 220V to my contactor from the timer on similar cable 2x20AWG again its not the current draw I'm worried about (2.5W) its the fact that I haven't stepped down to a safe voltage and I would rather be safe a put a protection in there too. most of the cable is in trunking 7mm x12mm but still you never know !

Any coments ideas ? thanks guys...
 

Similar threads

  • · Replies 14 ·
Replies
14
Views
3K
  • · Replies 9 ·
Replies
9
Views
3K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 12 ·
Replies
12
Views
2K
  • · Replies 26 ·
Replies
26
Views
8K
  • · Replies 49 ·
2
Replies
49
Views
5K
  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 3 ·
Replies
3
Views
3K
Replies
4
Views
3K
  • · Replies 21 ·
Replies
21
Views
3K