High voltage transformer windings position

Click For Summary
SUMMARY

The discussion centers on the configuration of windings in high voltage transformers, specifically the placement of low voltage (LV) windings closest to the core and high voltage (HV) windings on the outside. Participants highlight several reasons for this arrangement, including reduced insulation requirements, easier access for tap changers, and lower leakage reactance. The specific transformer in question is a Generator Step-Up transformer transitioning from 840V to 33kV, with aluminum windings. The conversation also touches on the thermal management of HV insulation and the complexities of leakage inductance.

PREREQUISITES
  • Understanding of high voltage transformer design principles
  • Familiarity with Generator Step-Up transformers and their applications
  • Knowledge of electrical insulation requirements for transformers
  • Basic concepts of leakage reactance and inductance in electrical systems
NEXT STEPS
  • Research the design and operational principles of Generator Step-Up transformers
  • Explore the impact of winding configurations on transformer efficiency and performance
  • Learn about insulation materials and their thermal properties in high voltage applications
  • Investigate leakage inductance calculations and their significance in transformer design
USEFUL FOR

Electrical engineers, transformer designers, and professionals involved in high voltage power systems will benefit from this discussion, particularly those focused on optimizing transformer performance and efficiency.

GreatWhiteWine
Messages
5
Reaction score
3
Good morning all!

I have a quick question regarding high voltage transformers, can someone explain why we need to put the low voltage winding the closest to the core and the high voltage winding on the "outside"?

Have a nice day!
 
Engineering news on Phys.org
Welcome to PF. :smile:

Could you post links to the kinds of HV transformers you are referring to? There are many applications of HV transformers, and each will have different engineering considerations that lead to different winding orders/techniques. Are you asking mainly about 50/60HZ power distribution systems, or more about power conversion systems (like power supplies, flyback transformers, etc.)?
 
  • Like
Likes   Reactions: GreatWhiteWine
Thanks for the welcome!

You are right, I was a little light on details. I am talking about a Generator Step-Up transformer going from 840V to 33kV, let's say around 5MW, 3 phases with aluminum windings, is that enough? Do you think that some HV transformer have their HV windings on the "inside" of the complete winding?

Have a nice day!
 
Ah, thanks, that helps. If it were questions about the power conversion transformers for power supplies, displays, etc., I could help. But for that application, it's best for me to page @anorlunda and @Baluncore :smile:
 
  • Like
Likes   Reactions: GreatWhiteWine
  • Like
  • Informative
Likes   Reactions: Klystron, GreatWhiteWine, Windadct and 3 others
For practical purposes sure, separate the windings and put the LV closer to core but IIRC for best mutual coupling I think it was best to stack the two sides layer on top of layer in an alternating way where one layer is primary and one secondary and then repeat.
At least this is how it's done in many "audio" transformers for tube amps
I once had to rewind one such transformer and it was a pain
 
Initially I thought that I²R would be critical for the lower voltage, higher current windings. By placing the LV winding inside, the length of copper will be less and the resistance lower. But then I get the feeling that the distribution of copper in a transformer, can always be optimised by changing wire diameter, to get the same regulation and energy efficiency, for the same mass of copper. Maybe I need to think again.
 
Thanks a lot all of you! That was quick.

So first reduced insulation between LV and center core than with HV and center core (meaning smaller and cheaper transformer). Make sense.

Then second, it's easier to place the tap changer on the outside than on the inside of the winding, ok I guess it's plausible even if I am not fully convinced, however I do see the interest in connecting the tap changer to the HV side for the reduced cable cross-section compared to the higher current LV side.

And finally, a lower leakage reactance, this one is not clear for me, I understand why it's good to have a lower leakage reactance for the losses, but I don't understand why it is getting lower when the LV is closer to the core. I mean, the leakage must be proportional somewhat to the distances between the HV and LV to the core, I don't see why having the LV side next to the core reduce the leakage more than having the HV side next to the core, is it linked to the higher currents?

Again thanks a lot for your time! @cnh1995 @Baluncore @artis @anorlunda @berkeman
 
  • Like
Likes   Reactions: DaveE and berkeman
  • #10
GreatWhiteWine said:
Thanks a lot all of you! That was quick.

So first reduced insulation between LV and center core than with HV and center core (meaning smaller and cheaper transformer). Make sense.

Then second, it's easier to place the tap changer on the outside than on the inside of the winding, ok I guess it's plausible even if I am not fully convinced, however I do see the interest in connecting the tap changer to the HV side for the reduced cable cross-section compared to the higher current LV side.

And finally, a lower leakage reactance, this one is not clear for me, I understand why it's good to have a lower leakage reactance for the losses, but I don't understand why it is getting lower when the LV is closer to the core. I mean, the leakage must be proportional somewhat to the distances between the HV and LV to the core, I don't see why having the LV side next to the core reduce the leakage more than having the HV side next to the core, is it linked to the higher currents?

Again thanks a lot for your time! @cnh1995 @Baluncore @artis @anorlunda @berkeman
Yes, me too. The insulation argument makes sense. Particularly if you consider that the outer windings will probably be cooled better, so less thermal stress on the HV insulation.

The other arguments may be true but I'm not very convinced by them. It seems there are pros and cons for each configuration for those issues. I wonder if others could elaborate?
 
  • #11
Perhaps one way of looking at Leakage Inductance is to consider that not all the flux is traveling thru the core or the windings.

There is a fringing field of flux extending past the ends of the windings which potentially misses a few turns. Also consider that some flux lines flow thru the insulation between layers, thus avoiding the core altogether.

Here are a couple of videos, neither particularly easy to follow, that may help.




The first one seems the better of the two (I did not fully watch either), the presenters accent on the second one is pretty heavy but it has text captions.

(above found with:
https://www.google.com/search?&q=leakage+inductance+calculation)

Cheers,
Tom
 
  • Informative
  • Like
Likes   Reactions: anorlunda and cnh1995

Similar threads

  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 9 ·
Replies
9
Views
3K
  • · Replies 27 ·
Replies
27
Views
3K
Replies
17
Views
956
  • · Replies 3 ·
Replies
3
Views
2K
Replies
8
Views
2K
Replies
37
Views
10K
Replies
14
Views
3K
  • · Replies 20 ·
Replies
20
Views
4K
  • · Replies 49 ·
2
Replies
49
Views
5K