Well now it's getting interesting ! Troubleshooting !
I assume braking air is mighty important. Are there redundant compressors on the locomotive? Or are all the locomotives on a train connected by the brake air line?
serise dc motor running without load its speed increase rapidly and brocken the bearing and fan ventilator
Yes, a series motor that loses its load will speed up and destroy itself by centrifugal force. That's why you NEVER use one in a belt drive application.
Series motors draw horriific starting current and you probably have ample current available on a locomotive.
Bussman's site was down this morning, i wanted to direct you to their "Fuseology" .
Here's their motor protection guide
http://www.cooperindustries.com/content/dam/public/bussmann/Electrical/Resources/Solution%20Center/technical_library/BUS_Ele_Tech_Lib_Motor_Protection_Tables.pdf
Looking at last page, 159, for heavy start DC motors in your 210 amps current range , they indeed suggest the 300 amp fuse as "optimum", 350 maximum.
Can you look and see if your locomotive has one of these types,
Bussman LPJ, LPN, FRS ? That'd indicate somebody knowledgeable selected them.
Looking at their datasheets they all have pretty good let-through current for motor starting, and that's what they are designed for.
First thing i'd try is a fuse that's closer to motor's full load amp rating. A 200 amp FRS fuse will pass 1000 amps for about fifteen seconds, is that long enough time to start the motor?
If so i'd try a Bussman LPS or FRS 250 amp and see if the motor starts.
That smaller fuse will give the motor better overload protection.
That 350 amp is sized more to protect the branch circuit against short circiuts than to protect the motor against overloads.
Study these fuse datasheets:
http://www.cooperindustries.com/content/dam/public/bussmann/Electrical/Resources/Data%20Sheets/Bus_Ele_DS_1018_FRS-R(65-600)A.pdf
http://www.cooperindustries.com/content/dam/public/bussmann/Electrical/Resources/Data%20Sheets/Bus_Ele_DS_1020_FRN-R(70-600A).pdf
http://www.cooperindustries.com/content/dam/public/bussmann/Electrical/Resources/Data%20Sheets/Bus_Ele_DS_1004_LPN-RK_70-600A.pdf
in particular the time-current graphs. As you see a fuse designed to protect motor windings will tolerate surprising overloads. But so will a motor.
That's unlike a fuse designed to protect semiconductors, which have a reputation for being pretty effective fuse protectors..
That 350 amp recommendation for branch circuit assumes there's another overload protector between it and the motor, which is not your case.
Let's see if we can improve your overload protection first off.
Then figure out why the motor is being overloaded.
Does the pressure switch shut off the compressor at correct pressure?
Is there an ammeter for that motor?
old jim