aspardeshi said:
KW, Volts, Amp always confuse me. I have a project of 10kw generator, how do you measure that it is 10kw at first instance. for example if the output is 1200 volts, can it become 10kw or be a 10kw generator etc. What is the power requirement standard of a home ? how to fit the 1200 volt generator of 10kw suitable for house use ? please help.
You would get the voltage and KVA rating from a maker's pad on the side of the generator.
To get this 1200 volts to 120 volts you would have to use a 1200 volt to 120 volt transformer.
The power supply power out depends on the power factor of the load.
If the transformer is rated at 10 KVA and you have a perfectly resistive load, the output power of the generator would be 10 KW. There would be losses in the stepdown transformer, but these are quite efficient, maybe 95 %.
The generator can only supply 10 KVA / 1200 volts or 8.33 amps maximum. If the load is less than this, of course it supplies less than this.
At the house end of the transformer you might get 95 % of (83.33 amps at 120 Volts). That is still a lot of power, but it depends on the appliances used in the house whether it is enough.
If the load is reactive and has a poor power factor, the generator might still provide 10 KVA but some of this will not be available as power.
Loads like motors and fluorescent lights can have poor power factors if they are not corrected.
There is an excellent article on power factor on Wikipedia:
http://en.wikipedia.org/wiki/Power_factor
The graphs show the effects of poor power factor very well.