How long can a 1000W UPS power a 100W device?

  • Context: High School 
  • Thread starter Thread starter KFC
  • Start date Start date
  • Tags Tags
    Time
Click For Summary
SUMMARY

A 1000W Uninterruptible Power Supply (UPS) does not guarantee a runtime of 4 to 5 hours for a 100W load. The actual duration depends on the energy capacity of the UPS battery, typically measured in watt-hours (w-h). Most home-use UPS systems utilize small sealed batteries (3, 4.5, or 7 Ah), which provide less than 1 hour of runtime for a 100W device. For extended usage, users should consider adding larger batteries or using AGM batteries, which offer higher efficiency and faster charging times.

PREREQUISITES
  • Understanding of UPS specifications and battery types
  • Knowledge of watt-hours (w-h) and amp-hour ratings
  • Familiarity with battery chemistry, specifically lead-acid and AGM batteries
  • Basic electrical concepts, including power consumption and efficiency
NEXT STEPS
  • Research APC UPS models and their wattage vs runtime graphs
  • Learn about the differences between AGM and lead-acid batteries
  • Explore methods for calculating UPS runtime based on load and battery capacity
  • Investigate safety considerations for using lead-acid batteries in confined spaces
USEFUL FOR

This discussion is beneficial for IT professionals, home users considering UPS solutions, and anyone interested in optimizing power backup systems for electronic devices.

KFC
Messages
477
Reaction score
4
Hello, today I am going to buy a UPS (Uninterruptible Power Supply) of Power 1000W. I am thinking if we have device (100W) as load and how long can the UPS supply power to that device?

I was told by sales that usually, UPS can work for 4 to 5 hours but do they get that time?
 
Physics news on Phys.org
Last edited by a moderator:
You could make your own...

Battery charger plugs into the wall and charges a 12.6 volt deep cycle battery. An inverter is connected to the battery and powers your devices. At long as the battery charger is getting power from the wall the battery stays at full charge and the power flows directly from the charger to the inverter. When the charger looses power the battery supplies power until it is discharged. This way you can increase your run time simply by adding extra batteries in parallel, without even powering down the system. In a pinch you could run some jumper cables in through your window and power it from your car for as long as you have gas.

This, of course, is a rather crude way of doing it that sacrifices efficiency for simplicity. If your charger and your inverter are both 80% efficient then you will loose 36% of the electrical energy that passes through the device. I don't know if that concerns you or not.
 
Last edited:
KFC said:
I was told by sales that usually, UPS can work for 4 to 5 hours but do they get that time?
Never believe salesmen! They may work 4-5 hrs if not supplying anything probably.
Just check what battery your UPS contains.
5 hrs of 100W is a capacity of typical car battery (48 Ah at 12V), but rather not of those small ones, which are usually built into UPS's.
Most UPS-es for home usage utilise 3, 4.5 or 7 Ah sealed batteries - less than 1hr of 100W.
 
Last edited:
I agree with the above comments...
UPS can work for 4 to 5 hours but do they get that time?

Of course how long it lasts depends on the energy of the battery and the power condumed by the load. For a typical 12 volt battery, you'll see various ratings...CCA (starting power at zero degrees) and the one of interest is the 20 hour amp hr rating...how long the battery will provide 20 amps until flat dead...but it best not to discharge a lead acid wet cell battery much past 50% as that shortens life...

Depending on what you are doing also consider an AGM battery,,,it will be a lot more expensive initially but will have the lowest life cycle cost per amp hour...in other words, it costs more but puts out a lot more amp hours...and it charges four to five times faster than a typical wet cell lead acid battery...

Also wet cell lead acid batteries give of hydrogen gas and some acidic fumes...so if the battery will be heavily used that may be a consideration in some environments. The AGM is sealed and so gives off no gases nor fumes...
 
On a side note, the USA doesn't require battery makers to include capacity in battery descriptions (most European contries do require this), so capicity is not stated for a lot of batteries sold in the USA (except for ones used for radio control models). In this case, you'll need to find the specs from the UPS maker, such as the APC chart linked in post #2.
 

Similar threads

  • · Replies 32 ·
2
Replies
32
Views
4K
  • · Replies 6 ·
Replies
6
Views
3K
  • · Replies 33 ·
2
Replies
33
Views
2K
  • · Replies 7 ·
Replies
7
Views
3K
  • · Replies 69 ·
3
Replies
69
Views
16K
Replies
61
Views
9K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 9 ·
Replies
9
Views
2K
  • · Replies 46 ·
2
Replies
46
Views
7K
Replies
19
Views
3K