How system frequency is controlled on the electricity transmission system

Click For Summary
SUMMARY

This discussion focuses on the control of system frequency in electricity transmission systems, specifically highlighting Isochronous Speed Control and Droop Speed Control as key methods. Isochronous Speed Control maintains a constant frequency by adjusting the prime mover governor speed, while Droop Speed Control allows multiple generators to operate in parallel and share load effectively. Historical context is provided, noting that frequency control was less precise prior to 1992, with variations in AC line frequency due to changing loads. The use of PLCs for error signal processing to adjust generator speed is also emphasized.

PREREQUISITES
  • Understanding of Isochronous Speed Control and Droop Speed Control
  • Familiarity with AC generator operation and synchronization techniques
  • Knowledge of PLC (Programmable Logic Controller) functionality
  • Basic principles of frequency measurement and control in electrical systems
NEXT STEPS
  • Research the implementation of Isochronous Speed Control in modern generators
  • Explore the principles of Droop Speed Control in multi-generator systems
  • Study the role of PLCs in frequency control and automation in power systems
  • Investigate historical advancements in frequency control technologies since 1992
USEFUL FOR

Electrical engineers, power system operators, and anyone involved in the design and operation of electricity transmission systems will benefit from this discussion.

Freddy_Turnip
Messages
72
Reaction score
0
Hi can anyone direct me to some good information on how system frequency is controlled on the electricity transmission system?
 
Engineering news on Phys.org
It used to be rather crude. Increasing the steam increased the torque This in turn caused the particular generator to lead phase / try to pull the system to a higher frequency. As I recall, increasing the field current also tried to induce phase lead.

In engineering, they taught us that generators came one line by matching the speeed and phase of the existing generators. This was done with three lamps. One for each phase between the starting generator and the network. Steam was controlled to get the perfect phase match, and field strenght was controlled to get a perfect voltage match. Then, the switches could be engaged and the generator would hold lock with the system.

I don't know how they communicate to keep an average of 60 Hz, but I know it wasn't perfect as of about 1992. I was working on an inverter back then, and the crystal controlled signal sources matched each other perfectly, but the AC lines' frequency continuelly varied by fractions of a Hz.
 
As long as loads change across the grid, the frequency will deviate. At the generation stations, the grid frequency is measured and compared to the generator speed and the error signal is used by a PLC or some controller to ramp the generator up or down.

In a nutshell, Isochronous Speed Control refers to the prime mover governor speed control mode that controls the frequency (speed) of an AC generator (alternator) and Droop Speed Control refers to the prime mover governor speed control mode that allows multiple AC generators (alternators) to be operated in parallel with each other to power large electrical loads, or to "share" load.

http://www.control.com/1026221805/index_html"
 
Last edited by a moderator:

Similar threads

  • · Replies 7 ·
Replies
7
Views
2K
  • · Replies 2 ·
Replies
2
Views
1K
  • · Replies 14 ·
Replies
14
Views
3K
  • · Replies 21 ·
Replies
21
Views
3K
  • · Replies 3 ·
Replies
3
Views
3K
Replies
40
Views
4K
  • · Replies 28 ·
Replies
28
Views
2K
Replies
1
Views
2K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 53 ·
2
Replies
53
Views
7K