The discussion addresses a problem involving mixed loads on an AC supply, including a heating load of 15 kW, a motor load of 40 kVA at a 0.6 power factor, and a 20 kW load at a 0.8 lagging power factor. The total load is calculated to be 59 kW and 75.4 kVA, resulting in a power factor of 0.782. To improve the power factor to unity, a capacitor with a kVA rating of 47 kVA is required. Participants are encouraged to show their calculations using the power triangle to decompose the loads into real and reactive power. The discussion emphasizes the importance of understanding power factor and its correction in mixed load scenarios.
fan_103
Messages
24
Reaction score
0
Hi guys I am having problems with this question,can u help me?!?thnks

3. The loads taken from an a.c. supply consist of:
(a) a heating load of 15 kW;
(b) a motor load of 40 kVA at 0.6 power factor; and
(c) a load of 20 kW at 0.8 lagging power factor.
Calculate:
(i) the total load from the supply in kW and kVA and its power factor,
(ii) the kVA rating of the capacitor to bring the power factor to unity.
Draw the power triangle and show how the capacitor would be connected to the
supply and the loads.

Power factor=Cosine angle(between supply voltage and current)
ANS:59kW, 75.4 kVA, 0.782; 47 k Ar
 
Physics news on Phys.org
As per the forum rules, you need to show some work. I'll help you out, however: decompose each of these loads (into real and reactive power) using the power triangle, and then find the resultant of real and reactive powers to find your total apparent power.

EDIT: Power triangle:
http://en.wikipedia.org/wiki/Electric_power#Alternating_current
 