- #1
littlej040
- 10
- 0
I am using an isolation transformer in a VFD circuit to prevent a GFCI from tripping (due to harmonic noise getting back on the line.) This solved my GFCI problem, but brought about another issue due to the inrush current the transformer created on this circuit.
Due to UL requirements, i placed a 10A (K curve for increased holding current due to inductive loads) in series with the transformer primary. Occassionally if the power is interrupted then recovered (during a storm etc.) The breaker is tripping due to the high inrush current.
My resolution was to install a NTC thermistor in series with the breaker that is capable of handling almost twice the rated current of the circuit. While this solved my issue, I feel their may be a more elegant solution that will remove this Hot component from my circuitry. I considered placing a PTC device in series with the transformer primary (and removing the 10 A breaker), but it appears these devices are not intended for high voltage high current situations (115 V, 8 A in this situation.)
Does anyone have any suggestions?
Thanks,
Jeff
Due to UL requirements, i placed a 10A (K curve for increased holding current due to inductive loads) in series with the transformer primary. Occassionally if the power is interrupted then recovered (during a storm etc.) The breaker is tripping due to the high inrush current.
My resolution was to install a NTC thermistor in series with the breaker that is capable of handling almost twice the rated current of the circuit. While this solved my issue, I feel their may be a more elegant solution that will remove this Hot component from my circuitry. I considered placing a PTC device in series with the transformer primary (and removing the 10 A breaker), but it appears these devices are not intended for high voltage high current situations (115 V, 8 A in this situation.)
Does anyone have any suggestions?
Thanks,
Jeff