Insulating PEX Tubing for Radiant Floor Heating

  • Thread starter Thread starter n_delta89
  • Start date Start date
  • Tags Tags
    Insulation
AI Thread Summary
Using insulation on top of PEX tubing for radiant floor heating may not be advisable, as it can hinder heat transfer to the floor. Best practices recommend starting with a cold feed and gradually increasing the temperature to avoid thermal shock, which can damage new flooring. The suggested maximum contact temperature for comfort is 85°F, and a delta T of 20°F is considered too high for effective radiant heating. Manufacturers typically recommend R-19 insulation under floors and 2 inches of foam under slabs, with water temperatures usually kept between 100-140°F. Proper temperature management is crucial to ensure the system operates effectively and safely.
n_delta89
Messages
1
Reaction score
0
Hello Everyone.
As an engineering student, I've been reviewing this forum many years. This is my first question.
My team and I are designing a radiant floor heating system using pex tubing.
The inlet water to pex tubing is 180 F, we assume that the outlet temperature will have a delta T loss of 20 F. This return temperature will be mixed with a mixing valve and sent back to the floor at a temperature between 160-170 F. The second loop will again have a 20 F loss and again this returning water will be mixed giving a temperature of 150-160 and thus the eventually the temperature in the tubes will be lowered down to 120-130 F and maintained there until the house zone temperature is reached.

My Question is:
Will it be viable to install insulation on top of pex tubing to protect the cork floor since the inlet water is at such a high temperature. The manufacture recommends that the cork floor be subjected to 120-130 F temperatures. Since the system uses a mixing valve we can lower the temperature down to this point, but there will be a delay(not sure exactly how long).

So, is it viable to use insulation to protect the floor. Since this seems rudimentary that we are insulating against something that we are trying to heat, I'm really not sure.


Thank You.
 
Engineering news on Phys.org
Hi, normally you don't start with a hot feed temp and then let it cool down gradually.
The thermal shock is often to much for a new floor to handle.

Best practice calls for a cold startup, so total re-circulation, with blending valve set to full floor return. Once running, you SLOWLY blend in the warm water, in increments of 5 degC and leave it for a few hours, before again increasing the temp.

If you follow this method, to the max allowable temp, then the floor will be just fine and no insulation will be needed.
Insulation will will only ever hamper the heat transfer to the floor which is waht you want to avoid!

Never take the floor to the max allowable temp. There are always tolerances on your control systems and response times to temperature readings and subsequent controls.

Good Luck!
 
I am not an ME. Just a Master Plumbing, Heating and Air contractor. Radiant flooring must be designed at a contact temp not to exceed 85 deg F. This is a comfort issue. Try walking barefoot across asphalt at 90 deg and tell me how comfortable it is.

My question is the installation method. Most pex manufacturers have recommendations for at least an R-19 underfloor installation and at least 2" of foam under a slab. In either case, we usually only send 100-110 deg water to the slab and only as high as 140 to under floor applications that utilize aluminum heat transfer plates. In either method, we temper the water via a mixing valve before sending it to the floor distribution manifold.

As previously stated, the thermal shock of slowly cooling the fluid is too great.

Also, 20 deg delta T is too high for radiant. Most residential and commercial systems that I have been involved with over the last 20 something years are lucky to see 10 deg deltas.

Good Luck. Sorry if my non-educated opinion is unwanted.
 
meplumber said:
I am not an ME. Just a Master Plumbing, Heating and Air contractor. Radiant flooring must be designed at a contact temp not to exceed 85 deg F. This is a comfort issue. Try walking barefoot across asphalt at 90 deg and tell me how comfortable it is.

My question is the installation method. Most pex manufacturers have recommendations for at least an R-19 underfloor installation and at least 2" of foam under a slab. In either case, we usually only send 100-110 deg water to the slab and only as high as 140 to under floor applications that utilize aluminum heat transfer plates. In either method, we temper the water via a mixing valve before sending it to the floor distribution manifold.

As previously stated, the thermal shock of slowly cooling the fluid is too great.

Also, 20 deg delta T is too high for radiant. Most residential and commercial systems that I have been involved with over the last 20 something years are lucky to see 10 deg deltas.

Good Luck. Sorry if my non-educated opinion is unwanted.

Of course your opinion is welcome, we want to hear what works, not what people (engineers, myself included) think will work.
 
Thank you MRFMEngineer.

My son is an aspiring engineer and physics nut. He visits this site frequently.

I wanted to comment on this thread and one other, but was unsure of the boards rules as they apply to us "unlearned" ones.
 
Posted June 2024 - 15 years after starting this class. I have learned a whole lot. To get to the short course on making your stock car, late model, hobby stock E-mod handle, look at the index below. Read all posts on Roll Center, Jacking effect and Why does car drive straight to the wall when I gas it? Also read You really have two race cars. This will cover 90% of problems you have. Simply put, the car pushes going in and is loose coming out. You do not have enuff downforce on the right...
Thread 'Physics of Stretch: What pressure does a band apply on a cylinder?'
Scenario 1 (figure 1) A continuous loop of elastic material is stretched around two metal bars. The top bar is attached to a load cell that reads force. The lower bar can be moved downwards to stretch the elastic material. The lower bar is moved downwards until the two bars are 1190mm apart, stretching the elastic material. The bars are 5mm thick, so the total internal loop length is 1200mm (1190mm + 5mm + 5mm). At this level of stretch, the load cell reads 45N tensile force. Key numbers...
I'm trying to decide what size and type of galvanized steel I need for 2 cantilever extensions. The cantilever is 5 ft. The space between the two cantilever arms is a 17 ft Gap the center 7 ft of the 17 ft Gap we'll need to Bear approximately 17,000 lb spread evenly from the front of the cantilever to the back of the cantilever over 5 ft. I will put support beams across these cantilever arms to support the load evenly
Back
Top