The discussion centers on the efficiency of using flat wire versus round wire for copper windings in generators. It highlights that magnetism penetrates copper only at the surface, leading to potential inefficiencies in round wire due to wasted material. Flat wire may be more efficient because it allows for better packing and reduces eddy current losses, especially in AC applications. The skin depth in copper is noted to be about 8 mm at 60 Hz, influencing the choice of wire shape based on the magnetic field orientation. Overall, the orientation and dimensions of the conductor are crucial for optimizing performance in generator windings.
R3KR
Messages
7
Reaction score
0
Hello all, I have a simple question about copper windings on generators.

From what I have read, magnetism only penetrates the skin of a copper wire by very little.
Dosnt this mean that most of the copper in a winding is wasted ?

And wouldn't it be more efficient to use flat wire "-" instead of round "o" ?
 
Engineering news on Phys.org
Magnetism completely penetrates copper at dc or very low frequencies. At ac frequencies, the penetration depth is called the skin depth. There are two situations where the copper dimensions are important. 1) For current being carried in copper conductor, the ac current tends to be carried on the surface, limited to the skin depth, so sometimes rectangular wire is perferred (but also for packing efficiency and mechanical considerations). Hollow water-cooled copper conductor is always square or rectangular. 2) Eddy currents can be generated (and dissipated) in copper wires exposed to ac magnetic fields. this leads to heat dissipation that has to be removed. The orientation of the flat surfaces of the conductor relative to the magnetic field direction is important.
Bob S
 
Last edited:
Thanks for reply!

Was thinking in terms of 3 phase AC, don't know if "frequency" would be considered to be DC. 50-200Hz ?

When you say "orientation", I am assuming that the "plane side" of flat wire is perpendicular to the magnets pole,
 
Skin depth in copper is about 8 mm at 60 Hz, and varies inversely as sqrt(frequency). For rectangular copper conductors, the long dimension should be parallel to the magnetic field.
Bob S
 
Very basic question. Consider a 3-terminal device with terminals say A,B,C. Kirchhoff Current Law (KCL) and Kirchhoff Voltage Law (KVL) establish two relationships between the 3 currents entering the terminals and the 3 terminal's voltage pairs respectively. So we have 2 equations in 6 unknowns. To proceed further we need two more (independent) equations in order to solve the circuit the 3-terminal device is connected to (basically one treats such a device as an unbalanced two-port...
suppose you have two capacitors with a 0.1 Farad value and 12 VDC rating. label these as A and B. label the terminals of each as 1 and 2. you also have a voltmeter with a 40 volt linear range for DC. you also have a 9 volt DC power supply fed by mains. you charge each capacitor to 9 volts with terminal 1 being - (negative) and terminal 2 being + (positive). you connect the voltmeter to terminal A2 and to terminal B1. does it read any voltage? can - of one capacitor discharge + of the...