Isolating transformer in the UK

  • Thread starter Thread starter f95toli
  • Start date Start date
  • Tags Tags
    Transformer Uk
Click For Summary

Discussion Overview

The discussion centers around the challenges of ground loops in measurement setups, particularly in thermometry applications. Participants explore the use of isolation transformers to address these issues, specifically looking for suppliers in the UK that offer transformers capable of breaking the connection to safety ground.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • One participant describes issues with ground loops in their thermometry setup and suggests using an isolation transformer where the secondary earth is not connected to the primary safety ground.
  • Another participant mentions that in the US, isolation transformers typically do not isolate the earth ground, which is intended to prevent ground faults.
  • A participant asserts that transformers do exist which can isolate ground, sharing their experience with a large transformer that is impractical for their current needs.
  • Concerns are raised about the interference from 50Hz noise and other higher frequencies affecting sensitive measurements, with a request for a drawing of the setup to explore alternative solutions.
  • One participant suggests using doubly-shielded cable to mitigate noise pickup and ground loop issues, referencing a related discussion on high input impedance amplifier circuits.

Areas of Agreement / Disagreement

Participants express differing views on the availability and functionality of isolation transformers, with some asserting that such transformers can isolate ground while others maintain that typical models do not. The discussion remains unresolved regarding the specific needs and solutions for the participant's measurement setup.

Contextual Notes

Participants mention various technical details about their setups, including the use of specific measurement equipment and the challenges posed by grounding in sensitive environments. There is an acknowledgment of the complexity of the systems involved and the evolving nature of the setups.

f95toli
Science Advisor
Messages
3,510
Reaction score
1,073
For a while now I have been having some problems with ground loops that are due to the diagnostics (in this case thermometry) in the my measurement setup.
Unfortunately there is no "easy" way to solve this problem without breaking the connection to Earth (=safety ground) and let some of the measurement electronics float or be grounded via the measurement leads.

Now, the obvious solution to this problem is to use an isolation transformer where the "earth" on the secondary is not connected to safety ground on the primary.
However, I can't seem to find a supplier of this type of transformer here in the UK.

There are plenty of "isolation transformers" available from RS, Farnell etc but they are really "safety transformers", they won't break the connection to ground which is what I need. The only types that I have seen that DO let equipment float are intended to be used on boats ("shorecraft") and are not really suitable for a lab.

Does anyone know of a company that sells these things here in the UK?
I don't need a big transformer, something like 300VA would do, but ideally it should be portable (i.e. not meant for permanent installation) and have 2-3 outlets.

(I should say that I used transformers of this type when I was still working in Sweden, so I am aware of all potential problems when it comes to safety etc).
 
Engineering news on Phys.org
f95toli said:
For a while now I have been having some problems with ground loops that are due to the diagnostics (in this case thermometry) in the my measurement setup.
Unfortunately there is no "easy" way to solve this problem without breaking the connection to Earth (=safety ground) and let some of the measurement electronics float or be grounded via the measurement leads.

Now, the obvious solution to this problem is to use an isolation transformer where the "earth" on the secondary is not connected to safety ground on the primary.
However, I can't seem to find a supplier of this type of transformer here in the UK.

There are plenty of "isolation transformers" available from RS, Farnell etc but they are really "safety transformers", they won't break the connection to ground which is what I need. The only types that I have seen that DO let equipment float are intended to be used on boats ("shorecraft") and are not really suitable for a lab.

Does anyone know of a company that sells these things here in the UK?
I don't need a big transformer, something like 300VA would do, but ideally it should be portable (i.e. not meant for permanent installation) and have 2-3 outlets.

(I should say that I used transformers of this type when I was still working in Sweden, so I am aware of all potential problems when it comes to safety etc).

Try posting on CR4.globalspec.com. There's a bunch of UK guys on there who know all kinds of sources.
 
At least in the US, isolation transformers only isolate Hot and Neurtal -- the Earth ground connection goes straight through as you say. The purpose is to eliminate the potential for a ground fault at the output causing a ground current.

Can you maybe post a drawing of your setup, so that we can offer other ideas for eliminating the interference you are seeing? Is it 50Hz noise that is getting into your sensor measurements?
 
berkeman said:
At least in the US, isolation transformers only isolate Hot and Neurtal -- the Earth ground connection goes straight through as you say. The purpose is to eliminate the potential for a ground fault at the output causing a ground current.

Can you maybe post a drawing of your setup, so that we can offer other ideas for eliminating the interference you are seeing? Is it 50Hz noise that is getting into your sensor measurements?

No, there are definitely transformers that also isolate ground. I have, as I wrote above, used one before. We even have (at least) one where I work now, but it is a huge things (several kVA) and not very practical (I don't even think I would be able to move it into the screened room).

I don't have a drawing at the moment. It is a very complicated system and it keeps evolving to I keep most of the "drawings" related to grounding in my head:rolleyes:

My work mainly consists of doing very sensitive measurements (DC and microwave frequencies) at low temperatures (I am using a dilution fridge, the temperature is about 20 mK). I have been doing this for over 8 years now so I am reasonbly good at it.

My problem at the moment is that the cable from AC-bridge that I use to measure the resistance of the RuO2 thermometers is creating a ground loop between the cryostat (which needs to be grounded to the screened room) and Earth ground; I can't disconnect the shield of the cable from the bridge because then I pick up too much noise from the air which in turn heats the sensors (and in worst case the whole fridge) a few mK. The excitation voltage is 3 or 10 uV (resulting in a dissipation of a a few fW in the sensor, any more would heat it up).

The loop means that there is more 50 Hz in there than I need, there are also some higher frequencies in there which I suspect are generated by vacuum pumps etc. But the main problem with the loop it that is also makes the actual measurements more difficult, the thermometery is after all mainly used for diagnostics of the fridge.
The company that builds these bridges actually recommend that they be used with isolation transformers.

I do have a nuclear orientation setup as well (Co-60 source +gamma detector) which I can use but it is very slow, it takes about 45 minutes to get enough data to accuratly measure the temperature (but the advantage is of course that it is a primary thermometer, so it is still useful) so it is useless for making measurements vs. temperature.
 
Wow, impressive. My next suggestion would be to use doubly-shielded cable, with the outer shield Earth grounded to the cryostat, and the inner shield bootstrapped to the sensor ground (driven by an active driver to the same potential as the average common mode voltage of the two (twisted) sensor wires). Kind of like we discussed in this other thread about very high input impedance ampilifier circuits and how to drive their guards:

https://www.physicsforums.com/showthread.php?t=212030

The outer shield will help protect you from 50Hz pickup and the higher frequency noise that you are seeing, and the inner shield will keep you from having ground loop noise couple into your sensor's balanced twisted pair.
 

Similar threads

  • · Replies 6 ·
Replies
6
Views
2K
  • · Replies 21 ·
Replies
21
Views
3K
Replies
6
Views
4K
Replies
12
Views
3K
  • · Replies 9 ·
Replies
9
Views
3K
  • · Replies 3 ·
Replies
3
Views
3K
Replies
7
Views
12K
  • · Replies 17 ·
Replies
17
Views
6K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 12 ·
Replies
12
Views
37K