About the manual shutdown of Ohi NPP unit 1 (decline of pressure at accumulator C)
Ohi NPP unit 1 (pressurized water reactor, nominal output 1,175,000 kW, nominal thermal power 3,423,000 kW) was undergoing a test run as part of inspection No.24 when the "high/low pressure, accumulator※ C" alarm was issued, at 10:46 PM, 15 July 2011.
When we checked the pressure gauge, instead of the normal 4.60 MPa, the pressure was 3.65 MPa, which is below the safety limit of 4.04 MPa. For this reason, we started bringing nitrogen using the nitrogen supply line at 11:20 PM and at 11:45 PM the pressure had risen back to 4.09 MPa, satisfying the 4.04 safety standard.
The supply of nitrogen was completed at 12:38 AM, today, and a visual inspection of the accumulator and nearby valves was undertaken, but no abnormality was observed. The pressure was stabilized at 4.08 MPa.
As we prioritize safety, in order to inspect the causes of the pressure decline and to implement countermeasures, we decided to start decreasing the output at around 1 PM today, and at around 9 PM we shut down the reactor.
This event is not causing radiological consequence to the environment.
※ Accumulator : Accumulators are tanks storing borated water. Each of the 4 primary cooling systems is installed with one. During a loss of coolant or other accident, when the pressure in a primary cooling system drops lower than the pressure of the nitrogen-pressurized accumulator, borated water flows into that primary cooling system.About the manual shutdown of Ohi NPP unit 1 :
http://www.kepco.co.jp/pressre/2011/__icsFiles/afieldfile/2011/07/16/0716_1j_01.pdf (pdf 28.6 KB)
Source :
http://www.kepco.co.jp/pressre/2011/0716-1j.html (my translation)