KVA's and electrical connections to a residential development

  • Thread starter Thread starter teslaspal
  • Start date Start date
  • Tags Tags
    Electrical
AI Thread Summary
The local electricity company has indicated that the existing infrastructure cannot support the electrical load for a residential development, requiring the installation of a new transformer. The current three-phase transformer can only provide 200kVA, while the development needs 600kVA. There is confusion regarding the transformer capacity, as it is believed that the KVA rating does not multiply with the number of phases. The discussion highlights the misunderstanding of how transformer capacity works in relation to load requirements. Clarification on this issue is essential for moving forward with the electrical connection.
teslaspal
Messages
1
Reaction score
0
Hi there, new to the forum and had a question I was hoping that you folks could help out with.

I have recently made application to our local electricity company for electrical connections to a residential development.

I have given them a breakdown of all the loads which are single phase domestic.

They have come back and mentioned that they don't think the infrastructure can support the load and they need us to pay for a new transformer.

They only have 200kva available from the existing three phase transformer and I need 600kva.

Now, I am slightly confused with this, as surely the 200kva (three phase) will support my 3 x 200kva requirements?
 
Engineering news on Phys.org
The transformer KVA does not get multiplied by the number of wires.
That is a total.
So if you draw 1 line x 600, 2 lines x 300 or 3 lines x 200, it still adds up to 600kva that the transformer sees.
 
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Thread 'Electromagnet magnetic field issue'
Hi Guys We are a bunch a mechanical engineers trying to build a simple electromagnet. Our design is based on a very similar magnet. However, our version is about 10 times less magnetic and we are wondering why. Our coil has exactly same length, same number of layers and turns. What is possibly wrong? PIN and bracket are made of iron and are in electrical contact, exactly like the reference design. Any help will be appreciated. Thanks. edit: even same wire diameter and coil was wounded by a...
Thread 'Beauty of old electrical and measuring things, etc.'
Even as a kid, I saw beauty in old devices. That made me want to understand how they worked. I had lots of old things that I keep and now reviving. Old things need to work to see the beauty. Here's what I've done so far. Two views of the gadgets shelves and my small work space: Here's a close up look at the meters, gauges and other measuring things: This is what I think of as surface-mount electrical components and wiring. The components are very old and shows how...
Back
Top