SUMMARY

The discussion centers on measuring the resistance of an earthing system for a large building using the MI 2124 Earth tester from METREL. It is confirmed that while the MI 2124 can be used for measuring resistance, accurate results for a large earthing system may require additional equipment, particularly for measuring the resistance of the ring to a central earthing rod. The importance of using a test rod, potentially over 1000 feet away, is emphasized to ensure safety compliance with electrical systems.

PREREQUISITES
  • Understanding of earthing systems and their configurations
  • Familiarity with the MI 2124 Earth tester from METREL
  • Knowledge of resistance measurement techniques in electrical systems
  • Experience with test rod deployment for earthing resistance testing
NEXT STEPS
  • Research the specifications and capabilities of the MI 2124 Earth tester
  • Learn about the proper techniques for deploying test rods in earthing resistance testing
  • Investigate alternative instruments for measuring low resistance in large earthing systems
  • Study safety standards and regulations related to earthing systems in commercial buildings
USEFUL FOR

Electrical engineers, safety compliance officers, and technicians involved in the installation and testing of earthing systems in large commercial or industrial buildings.

rohollah200
Messages
3
Reaction score
0
HI ALL

We have a big building.there is a ring around the building as earthing system.

we put bare cooper wire in trench around building .

NOW,we are going to measure the resistance of earthing system with Earth tester. Our device is MI 2124 ,one production of METREL .

how I can measure the resistance of big earthing system? can I use MI 2124 for this purpose?
 

Attachments

  • Untitled.jpg
    Untitled.jpg
    53.6 KB · Views: 438
Engineering news on Phys.org
Hello Roho -

Been a while since I was in the field - but real meaningful Earth testing of commercial / industrial sites is a tricky subject.

There are 2 different things you may be measuring - the Resistance of ANY point within the Ring - to a central point - typically an Earthing Rod - I believe you may need a different instrument - Higher current and lower resistance because you are measuring the installed conductors. (This is a measure of the safety of the people / equipment in the facility relative to the electrical system )

To measure the Resistance of the Ring ( or this central point) to "EARTH" you will need to drive a Test Rod - in the cut sheet it says 30M max - that may work - but I have seen these tests run to a rod over 1000' Away. ( This is a measure of the safety of the Building relative to the utility supply)
 

Similar threads

Replies
53
Views
4K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 8 ·
Replies
8
Views
1K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 83 ·
3
Replies
83
Views
7K
  • · Replies 1 ·
Replies
1
Views
1K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 6 ·
Replies
6
Views
4K
  • · Replies 9 ·
Replies
9
Views
2K