To measure the output watts of a 24 HP electric generator, it is essential to understand that the horsepower rating refers to the mechanical input power, while the electrical output is typically rated at 13 kW. To test the generator's actual output, a load must be connected; for example, plugging in a 100-watt light bulb will allow measurement of the power being delivered. Using a watt meter, such as a Kill-A-Watt, can help assess the actual wattage output when devices are connected. It's important to note that the generator's output will vary based on the load impedance, and running it with minimal load can lead to inefficiencies. Proper measurement requires connecting appropriate loads and using the correct tools to gauge the output accurately.
Jimmy Snyder
Messages
1,122
Reaction score
22
My friend has a 24 HP electric generator and wants to know the number of watts being delivered. My understanding is that the 24 HP refers to the power input to the generator and he wants to know the output power generated. Can someone tell me how to measure it?
 
Engineering news on Phys.org
Try getting a watt meter.
 
Depending on how it is connected you may justbe able to use a plug-in watt meter from home depot. Or you can use a clamp on ammeter and calculate it...and estimate the power factor.
 
You DO understand that the power generated depends on what you hook to the generator right?
 
Averagesupernova said:
You DO understand that the power generated depends on what you hook to the generator right?
Wrong. The spec says the generator is capable of outputting 13kW. How do I test it to see if it really can? More to the point, how can I test it to see if it really is?
 
Jimmy Snyder said:
Wrong. The spec says the generator is capable of outputting 13kW. How do I test it to see if it really can? More to the point, how can I test it to see if it really is?

Umm, no, you're wrong. If you run the generator with nothing hooked then it is not putting out any power. Hook a 100 watt light bulb on it and it is putting out 100 watts. If you want to test it then hook the appropriate load on and see what happens.
 
Averagesupernova said:
Umm, no, you're wrong. If you run the generator with nothing hooked then it is not putting out any power. Hook a 100 watt light bulb on it and it is putting out 100 watts. If you want to test it then hook the appropriate load on and see what happens.
Sorry, I meant you were wrong to assume that I understand that the power generated depends on what you hook to the generator. Please reread the post including your own question to me. I do not understand how to "see what happens". Is it the case that if I run a 24 HP generator with nothing loaded but a 100 watt light bulb, then only 100 watts are being generated regardless of the fact that it is rated for 13000 watts? What happens to the other 12900 watts? Will it cause the generator to overheat?
 
Good catch, averagesupernova...

Jimmy, if you just plug a 100 watt bulb into it, it will output 100 watts and input substantially less gas because the torque on the generator is lower. But it will be much less efficient than when running at rated output. It won't overheat, but it will reject more watts of heat per watt of electricity.
 
Jimmy Snyder said:
Is it the case that if I run a 24 HP generator with nothing loaded but a 100 watt light bulb, then only 100 watts are being generated regardless of the fact that it is rated for 13000 watts? What happens to the other 12900 watts? Will it cause the generator to overheat?

Think of the generator as a voltage source. The current drawn out depends on the load impedance, and thus the power drawn out depends on the load impedance. The generator is rated to supply up to 13kW into an appropriate load, and will supply less current and power into higher impedance loads.
 
  • #10
So, just because I think I am supplying 24 HP, doesn't meant that I actually am. If I load it with a 100 W light bulb I may only be supplying it with 200 W or less. Let's say, just for argument's sake that it takes 200 W input to get 100 W output. Let's also suppose that I am supplying it with 190 W, not enough for the bulb. I assume that the bulb will light up anyway, just not as brightly as designed. Am I right about that? So just because I see light coming from the 100 W bulb does not mean that I am actually getting 100 W out. How do I measure what I am actually getting? Think cook book, ingredients and procedures.
 
  • #11
Measure the line voltage. It should be within whatever the output spec of the generator is.

The generator probably has some form of feedback, to control the throttle of the engine to try to keep the output voltage within tolerance. If you switch on a heavy load all of a sudden, you will get a brief line voltage sag (and frequency sag) until the motor servos up. The generator probably also has some clipping diodes or similar, to keep from overvoltaging into the load when a heavy part of the load is removed, and the motor needs to servo back down.

Do you see any of this in the motor/generator spec sheet?
 
  • #12
I was hoping that the wikipedia article would talk more about output voltage regulation, but they don't say much that I can see:

http://en.wikipedia.org/wiki/Engine-generator

They do mention that for tighter output voltage regulation, a motor/inverter system is sometimes used.
 
  • #13
I don't know how to do it. If there's an engineer here who does know, won't you please take the time to tell me. What equipment do I need. What do I do with the equipment. Think cook book, think step 1, step 2, etc.
 
  • #14
Jimmy Snyder said:
My friend has a 24 HP electric generator and wants to know the number of watts being delivered. My understanding is that the 24 HP refers to the power input to the generator and he wants to know the output power generated. Can someone tell me how to measure it?


in theory, 24HP * 746W/hp = 17,904W. Your biggest problem with measuring this much output power is finding a load this big. You'll need a *big* resistor bank which can be expensive. What's the problem with just trusting that the generator can output 17904 W?

Are you sure 24HP is the input? That seems odd because 24HP sounds like output power.
 
Last edited by a moderator:
  • #15
Jimmy Snyder said:
I don't know how to do it. If there's an engineer here who does know, won't you please take the time to tell me. What equipment do I need. What do I do with the equipment. Think cook book, think step 1, step 2, etc.

Yeah, 13kW is a big load, dissipating a lot of heat.

Do you have a model number for the generator? A manual? Why do you and your friend doubt the manufacturer, and why do you want to experimentally verify their claimed max output?
 
  • #16
Jimmy Snyder said:
So, just because I think I am supplying 24 HP, doesn't meant that I actually am. If I load it with a 100 W light bulb I may only be supplying it with 200 W or less. Let's say, just for argument's sake that it takes 200 W input to get 100 W output. Let's also suppose that I am supplying it with 190 W, not enough for the bulb. I assume that the bulb will light up anyway, just not as brightly as designed. Am I right about that? So just because I see light coming from the 100 W bulb does not mean that I am actually getting 100 W out. How do I measure what I am actually getting? Think cook book, ingredients and procedures.
As said, the generator will be regulated, but to measure the watts if you just have a light bulb:

1. Buy one of these: http://reviews.homedepot.com/1999/100396600/kill-a-watt-reviews/reviews.htm
2. Plug everything in.
3. Turn everything on.
4. Read the watts off the watt meter.

Also, at low speed, the efficiency is certainly much worse than the 50% of peak your numbers imply. The generator probably runs at 10 or 20% of peak fuel flow just to keep it spinning.
 
  • #17
russ_watters said:
1. Buy one of these: http://reviews.homedepot.com/1999/100396600/kill-a-watt-reviews/reviews.htm
2. Plug everything in.
3. Turn everything on.
4. Read the watts off the watt meter.
I give up. I will ask elsewhere. Thanks, everyone, for your effort.
 
  • #18
I'm really not sure what the problem is, Jimmy. You asked for step by step instructions. What more do you want? :confused:
 
  • #19
in theory, 24HP * 746W/hp = 17,904W. Your biggest problem with measuring this much output power is finding a load this big. You'll need a *big* resistor bank which can be expensive.

Aren't toasters about a 1000 watts-maybe 2 slice or 4.
Plug in 1 and see if it pops.
Plug in 2 and see it both pop.
etc...
Until they don't pop no more, and that should be max output of the generator.
Anbody like a lot of cinamon toast?
 
  • #20
Jimmy Snyder said:
I give up. I will ask elsewhere. Thanks, everyone, for your effort.
A 13,000 watt load on the generator would stall a 17.5 hp engine, the 6.5 hp extra is the amount needed to keep the engine in a safe work load range. A small load on the generator would indeed waste a lot of fuel.
I can't tell you how, but someone else can say how to check the ohm's of the generator wiring and get the exact load rate of the unit.

Ron
 
  • #21
Jimmy took his generator and went home. :frown:

Now what are we supposed to do with all these light bulbs and toasters? :bugeye:
 
  • #22
I didn't realize people ever rated electrical outputs in horsepower -- I thought that was used solely for mechanical outputs, i.e. motors.

At any rate, 13 kW at 120V means drawing about 110 Amps of current. Or using the 1000W toaster approach, you'd need to hook up 13 toasters to this thing. And you'd be hard pressed to find anyone single device that consumes more than 1800W, since that is the maximum power a single 15A, 120V household outlet can supply.

EDIT:
russ_watters said:
As said, the generator will be regulated, but to measure the watts if you just have a light bulb:

1. Buy one of these: http://reviews.homedepot.com/1999/100396600/kill-a-watt-reviews/reviews.htm
2. Plug everything in.
3. Turn everything on.
4. Read the watts off the watt meter.

Also, at low speed, the efficiency is certainly much worse than the 50% of peak your numbers imply. The generator probably runs at 10 or 20% of peak fuel flow just to keep it spinning.
But if he wants to test the generator anywhere near the 13 kW maximum, the Kill-A-Watt does not measure power levels that high. When I tried to use one to measure the power of my neighbor's air conditioning system a couple years ago, the reading was off-scale.
 
Last edited:
  • #23
Redbelly98 said:
I didn't realize people ever rated electrical outputs in horsepower -- I thought that was used solely for mechanical outputs, i.e. motors.

The horsepower rating is for the gas-powered motor that drives the elecrical-output generator. That's where the 17kW --> 13kW decrease in efficiency comes from.

I miss Jimmy's generator... :frown:
 
  • #24
Redbelly98 said:
I didn't realize people ever rated electrical outputs in horsepower -- I thought that was used solely for mechanical outputs, i.e. motors.
Here is an advertisement for a 24 HP generator. I do not endorse it, it's just an example.

http://www.northerntool.com/shop/tools/product_36914_36914"

24 HP is the mechanical input, not the electrical output. However, it is possible to provide less than 24 HP at the input. The thing will still work, but it won't output 13 kW. Apparently, you can't even count on the 13/18 ratio (24 HP is roughly 18 kW). Since I am providing only a small but unknown amount of power to the generator (perhaps as little as 200 W), it is of little interest to know what the full capacity of the generator is. What I want to know is what power is coming out of the output. Adding lots of toasters won't help. What I propose to do is to load the output with a 100W light bulb and then measure the wattage coming out of the generator. I assume that if the measured value is less than 100 W, then I have my answer. If it is just 100 W, then I need to load a second bulb and measure again. Is that correct? It is unlikely in the extreme that I am delivering more than 300 W to the input so 2 bulbs ought to do it. I still don't know how to measure. I looked at the kill-o-watt, but it doesn't look like the right tool. It seems to say it would measure the efficiency of the lamp that holds the bulb, but that is not what I am interested in. I want to know in units of watts, how much power is coming out of the generator.
 
Last edited by a moderator:
  • #25
Berkeman, Jimmy, thanks for clearing up my question on the horsepower rating.

Jimmy said:
I looked at the kill-o-watt, but it doesn't look like the right tool.

The kill-o-watt will tell you the voltage, current, and power (in Watts) of whatever device is plugged into it. I know this because I own one myself and have used it. You plug the kill-o-watt into any standard outlet (as are found on the generator), and you plug the device of interest (lamp, toaster, etc.) into the kill-o-watt.

Assuming the kill-o-watt consumes negligible power itself, it will tell you how much electrical power the generator is producing. It will provide the measurement you are looking for.

It seems to say it would measure the efficiency of the lamp that holds the bulb
Well, to do that it would need to measure the power of the light being emitted by the bulb, which it can not do.
\text{Efficiency} = \frac{\text{Light power output of lamp}}{\text{Input power to lamp}}​
The kill-o-watt will only tell you the input power to the lamp which, as I mentioned before, is essentially equal to the output power of the generator, the quantity you are after.
 
  • #26
Here is a more practical answer, Your friend has a 17 KW generator for something, that size is what would run a whole house, say around 2500 Square feet, including AC.
If it is for a backup, hook up some stuff and see. An electric clothes dryer makes a VERY GOOD load test, but you would need 3 of them to get to 17KW. Also Dryers do not have the same start load as a 5 ton AC unit. If your friend is thinking about running computer equipment with this generator, also think about a big UPS to condition and clean up the power.
 
  • #27
Welcome to Physics Forums, johnbbahm.

I think Jimmy is interested in learning and understanding the details about the generator's capability. Just hooking stuff up to it and seeing if they work is not what he is after here, he is interested in measuring the actual wattage out of the generator.

Also, the electrical output turns out to be 12 to 13 kW, not 17 kW. The 24 hp (= 17.9 kW) figure is the rating of the motor output that would drive the generator.

johnbbahm said:
If your friend is thinking about running computer equipment with this generator, also think about a big UPS to condition and clean up the power.
Excellent idea, and definitely worth bringing up.
 
  • #28
Redbelly98 said:
Welcome to Physics Forums, johnbbahm.

I think Jimmy is interested in learning and understanding the details about the generator's capability. Just hooking stuff up to it and seeing if they work is not what he is after here, he is interested in measuring the actual wattage out of the generator.

Also, the electrical output turns out to be 12 to 13 kW, not 17 kW. The 24 hp (= 17.9 kW) figure is the rating of the motor output that would drive the generator.


Excellent idea, and definitely worth bringing up.

yeah you're right about 24hp being the mechanical output of the generator. 13KW is the electrical power output.
 
  • #29
Jimmy Snyder said:
So, just because I think I am supplying 24 HP, doesn't meant that I actually am. If I load it with a 100 W light bulb I may only be supplying it with 200 W or less. Let's say, just for argument's sake that it takes 200 W input to get 100 W output. Let's also suppose that I am supplying it with 190 W, not enough for the bulb. I assume that the bulb will light up anyway, just not as brightly as designed. Am I right about that? So just because I see light coming from the 100 W bulb does not mean that I am actually getting 100 W out. How do I measure what I am actually getting? Think cook book, ingredients and procedures.
The electricity supply to your house will be fused to limit the power supplied to your house (maybe 20kW), That doesn't mean that you are using (or paying for) 20kW all the time.
The only difference between the mains supply and your generator is that you tend to pay the same rate for your mains electrical energy, whatever the power you happen to be using. As has been mentioned above, because the efficiency of your generator depends on the actual load, then you pay more per kWh, effectively (fuel costs), when using just one lamp and less per kWh when you are using it at full output.
 
  • #30
I suspect a lot of generators of this type fudge a bit on the ratings. For instance, I have a Coleman generator with I believe a 10 HP gas engine. But NO SINGLE OUTLET can supply its continuous rated power. It has a duplex 120 volt outlet good for up to 20 amps. It has a single 120 volt outlet (Twist-lock) good for up to 30 amps. It has a single 240 volt outlet (also twist-lock) good for up to 20 amps. No single outlet will supply on its own the continuous rated power. I don't recall exact numbers, but I do know they fudge the specs. The duplex 120 volt outlet is on the same winding as the 240 volt outlet. Each half of it is technically good for 20 amps.
-
Jimmy, I think you've have been given enough to have a pretty good grasp of how to go about determining if the generator will do what it says. My original answer still stands. Put a load on it, see what happens. To calculate watts you need to measure the current as well as the voltage. To measure this kind of current you will need a clamp on type ammeter. Also, make sure the tractor driving it (I assume it is a tractor based on the Northern Tool ad) is running at the correct speed to get the required speed on the PTO shaft.
 

Similar threads

  • · Replies 38 ·
2
Replies
38
Views
4K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 0 ·
Replies
0
Views
1K
  • · Replies 3 ·
Replies
3
Views
3K
Replies
1
Views
3K
  • · Replies 8 ·
Replies
8
Views
5K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 5 ·
Replies
5
Views
3K
Replies
19
Views
2K
Replies
2
Views
1K