A Technologist in Training seeks assistance with motor acceleration simulations in ETAP, specifically regarding setup questions and hand calculations for startup scenarios. Key concerns include understanding the relationship between Locked Rotor Torque (LRT), Locked Rotor Amps (LRA), and voltage flicker regulation during motor startup. The user aims to validate ETAP simulations by calculating voltage drops for both Soft Starter and Direct On Line (DOL) methods. They report a simulation showing a 10.1% voltage drop and request guidance on determining voltage drop by hand. The discussion highlights the need for clarity on motor startup impacts and simulation accuracy.
Suerbatica
Messages
10
Reaction score
0
Hi everyone, I'm a Technologist in Training, except that I'm not getting much training. I have a tonne of questions regarding Motor Accel Simulation in ETAP. I'm hoping someone here might be kind enough to lend some insight, or point me to a place where I can find some.

First off, has anyone done this in ETAP? I've got some setup questions that I'd like to post, but will spare for now until I know there is someone who can help.
Second, can anyone tell me how this is done outside of ETAP (or other sim software)? I know how to find LRT, LRA, etc But how does this relate to startup and Voltage Flicker Regulation? (I do not know at this time if the 1100hp motor is being started under load or not). Essentially, how is this done by hand so I can validate my simulation?

I have to do a simulated startup and confirm that we need a SS instead of doing DOL, because the DOL lowers our voltage below Fortis' 5% minimum standard.

Cheers if anyone can lend a hand. Thanks Gents,

Suer
 
Engineering news on Phys.org
Welcome to PF. What do the acronyms ETAP, LRT and LRA stand for? Can you give a pointer to a web page describing the simulations that you are asking about?
 
Sorry for my late reply, I've been busy at work setting up this simulation. And I also made a quick reply earlier this week, but it was deleted by a moderator. I said or did something that violated the posting rules.
ETAP - is the software package I am using to run the simulation, I cannot provide any links to this software package' website as it will violate the terms of posting.
LRT - Locked Rotor Torque
LRA - Locked Rotor Amps

%Voltage drop is a differential equation and a very simple one, but what I'm having trouble figuring out is how do I determine the voltage drop of the motor when I have a Soft Starter, and when I don't? I'm assuming that since there is a controlled application of voltage to the motor, there is a controlled application of power. If it is gradually increased, the emerging magnetic field does not demand such a high in-rush current during start-up. What my problem is, is, how do I determine this by hand to verify my computer simulation in ETAP? I'm not sure how to determine voltage drop of a motor when using Soft Starting, or DOL (Direct Over Line, No Soft Start) starting. The difference between the two on the same motor will give me my %Vreg.

Again any help you can provide is appreciated.

Suer
 
Well my simulation is showing 10.1% Voltage Drop.

If anyone can provide any assistance please let me know.

Suer
 
For anyone interested:

Vm = Zm / (Zm + Zl)
Where:
Vm= Voltage during start-up
Zm= Locked Rotor Impedance
Zl= Impedance sum of source, line, xformer impedance
*All values I used were per unit rectangular.

As taken from the "Large Motors On Limited Capacity Transmission Lines" article by H.W. Lewis, Member IEEE, Williams Brothers Engineering Company and F.A. Woodbury, Member IEEE, Westinghouse Electric Corporation. Conference Record 77CH1229-4-LA, Paper Number PCI-77-41 Dated February 12, 1985.

Suerbatica
 
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Thread 'Electromagnet magnetic field issue'
Hi Guys We are a bunch a mechanical engineers trying to build a simple electromagnet. Our design is based on a very similar magnet. However, our version is about 10 times less magnetic and we are wondering why. Our coil has exactly same length, same number of layers and turns. What is possibly wrong? PIN and bracket are made of iron and are in electrical contact, exactly like the reference design. Any help will be appreciated. Thanks. edit: even same wire diameter and coil was wounded by a...
Thread 'Beauty of old electrical and measuring things, etc.'
Even as a kid, I saw beauty in old devices. That made me want to understand how they worked. I had lots of old things that I keep and now reviving. Old things need to work to see the beauty. Here's what I've done so far. Two views of the gadgets shelves and my small work space: Here's a close up look at the meters, gauges and other measuring things: This is what I think of as surface-mount electrical components and wiring. The components are very old and shows how...
Back
Top