Negative Power Factor on a motor?

Click For Summary
SUMMARY

The discussion centers on the unexpected negative power factor (PF) readings observed in 9 out of 11 three-phase delta-connected motors during an energy audit of a 15-story commercial building using a Fluke Power Quality Analyzer. A negative power factor indicates that the motors are acting as a capacitive load, supplying power back to the service, which is atypical for inductive motors. Participants suggest potential causes, including incorrect meter settings, reversed polarity in measurements, and the possibility of mechanical interactions between motors causing them to function as generators.

PREREQUISITES
  • Understanding of three-phase power systems
  • Familiarity with power factor concepts and calculations
  • Experience with power quality analyzers, specifically Fluke models
  • Knowledge of motor types, particularly delta-connected and synchronous motors
NEXT STEPS
  • Investigate the settings and calibration of the Fluke Power Quality Analyzer
  • Learn about the implications of capacitive loads in three-phase systems
  • Research mechanical interactions in motor systems that may lead to reverse power flow
  • Explore power factor correction techniques and devices
USEFUL FOR

Electrical engineers, energy auditors, and facility managers involved in optimizing motor performance and power quality in commercial buildings.

dahlungril
Messages
12
Reaction score
0
Negative Power Factor...on a motor??

Howdy Folks,

I don't post too much here, but I have run into a bit of a stumper.

I am in the process of interpretting some data for an energy audit of a commercial building, it is a 15 story office building, heated by heat pumps.

We hooked up our Fluke Power Quality Analyzer, which records the whole shebang, P, S, Q, PF, DPF, Vrms and I to each of the 11 pumps which supply hot water to the baseboards throughout the building and also for their water supply.

The motors are 3 phase delta connected so the meter was setup accordingly.

Upon reviewing the data record we've found that the power factor was negative for 9/11 of the pumps...the other two were fine. This negative power factor means that the motors are a capacitive load and are actually supplying power back to the service. This makes no sense to me whatsoever.

So my question is this, what else could the observed negative power factor and in turn negative real power, physically mean when measuring the 3 phase power across the lines of a delta connedcted motor.

Thank you for your time and thoughts in advance.
-Dave

PS- All I can think of is that perhaps in the meter there is a setting to switch the meter from capacitive load to inductive load...I will investigate this further, but I am skeptical that this will solve the problem.
 
Engineering news on Phys.org
I think if your measurement of current in reverse polarity there is a chance for negetive pf instead of positive pf.

dahlungril said:
Howdy Folks,

I don't post too much here, but I have run into a bit of a stumper.

I am in the process of interpretting some data for an energy audit of a commercial building, it is a 15 story office building, heated by heat pumps.

We hooked up our Fluke Power Quality Analyzer, which records the whole shebang, P, S, Q, PF, DPF, Vrms and I to each of the 11 pumps which supply hot water to the baseboards throughout the building and also for their water supply.

The motors are 3 phase delta connected so the meter was setup accordingly.

Upon reviewing the data record we've found that the power factor was negative for 9/11 of the pumps...the other two were fine. This negative power factor means that the motors are a capacitive load and are actually supplying power back to the service. This makes no sense to me whatsoever.

So my question is this, what else could the observed negative power factor and in turn negative real power, physically mean when measuring the 3 phase power across the lines of a delta connedcted motor.

Thank you for your time and thoughts in advance.
-Dave

PS- All I can think of is that perhaps in the meter there is a setting to switch the meter from capacitive load to inductive load...I will investigate this further, but I am skeptical that this will solve the problem.
 
speak2ranjith said:
I think if your measurement of current in reverse polarity there is a chance for negetive pf instead of positive pf.

ya that's what i was thinking immediately, maybe you have your polarities switched from what the measurement device reads?
 
You did not mention if all the motors are rated the same, or if they are totally isolated from each other, but it sounds a little like a design of a rotary phase converter where a larger three phase motor supplies power to several smaller units ??

I know nothing about commercial systems, and only have looked into the basics of single phase conversion to three phase power for my shop.
 
Essentially, the power factor is a comparison of the power used by the load (real power) divided by the power supplied to the load (apparent power). The difference between the real power and the apparent power is the reactive power. That is to say that it is the ratio of the useful work performed by an electrical circuit compared to the maximum useful work that could have been performed at the supplied voltage and amperage.

The negative sign just means that the current is leading the voltage. The net effect is a predominately capacitive load, i.e. the motors aren't absorbing all of the reactive power that is being supplied by the source.

Do you have some type of power factor correction device on the line? Typically motors produce magnetic fields, which are absorbers of reactive power, so you would typically have the opposite of what you are describing, unless you have some type of power factor correction (devices that produce electric fields which generate reactive power).

The whole point is to get the power factor as close to unity as possible by varying the reactive power.
 
speak2ranjith said:
I think if your measurement of current in reverse polarity there is a chance for negetive pf instead of positive pf.
Yep. I've never seen an inductive motor with a negative pf.

But maybe a little capacitive reactance will help the overall PF of your building.:biggrin:
 
First of all I doubt if it's a measurement issue as if it was then the power analyzer would show either current or voltage as a negative quantity.

The only place where you can get a leading pf is as you said a capacitive load which can be done using a synchronous motor in the overexcited state? So, Are you using a synchronous motor?
 
unplebeian said:
First of all I doubt if it's a measurement issue as if it was then the power analyzer would show either current or voltage as a negative quantity.

The only place where you can get a leading pf is as you said a capacitive load which can be done using a synchronous motor in the overexcited state? So, Are you using a synchronous motor?

Negative voltage and current readings in an AC system?
 
Is it possible that water being pushed by some of the motors in the system is mechanically forcing other motors to turn so that they input power back into the circuit (essentially turning the motors into generators)? I suppose if that were happening, you'd see a big increase in energy consumption by the other motors at the same time you're getting the surpluss from those in question.
 
  • #10
Averagesupernova said:
Negative voltage and current readings in an AC system?

If you hook up the ammmeter of a power analyzer in the reverse way you'll get a negative current measurement.
 
  • #11
unplebeian said:
If you hook up the ammmeter of a power analyzer in the reverse way you'll get a negative current measurement.
No, you don't. A/C is A/C. Power flows in both directions.

That said, there is no guarantee that the phases are correctly labeled or hooked up in order on the panel. I use a power meter like this (an Amprobe power meter and, in fact, I used it today) and often get negative reactive power readings on it. I just fix it in Excel.
 
  • #12
russ_watters said:
No, you don't. A/C is A/C. Power flows in both directions.

That said, there is no guarantee that the phases are correctly labeled or hooked up in order on the panel. I use a power meter like this (an Amprobe power meter and, in fact, I used it today) and often get negative reactive power readings on it. I just fix it in Excel.

Sorry guys, I was having a dumb day. You are right, AC is AC, but what I meant was that if you hook up the voltmeter and ammeter on the power analyser (any one of them) with reverse polarity, you'll end up with -vs pf (NOT -ve V and I readings.)

Sorry.

P.S. I think 'speak2ranjith' mentioned this before.
 
  • #13
I can give a better explaniation if you say leading or lagging. Lagging is inductive. Either side of the zero power factor is bad but it is best to keep it one RCH (the finest known measurement in electronics) on the lagging side for strictly monitary purposes.
 
Last edited:
  • #14


Flip your current clamp and you get negative readings including PF.
 

Similar threads

  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 8 ·
Replies
8
Views
2K
  • · Replies 19 ·
Replies
19
Views
4K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 55 ·
2
Replies
55
Views
9K
  • · Replies 4 ·
Replies
4
Views
4K
  • · Replies 6 ·
Replies
6
Views
4K
  • · Replies 9 ·
Replies
9
Views
8K
  • · Replies 2 ·
Replies
2
Views
3K