The discussion centers on the installation of 120VAC and 24VDC conductors within an enclosure, where the electrician plans to run both types of cables in parallel for about 2 feet. The 120VAC line carries a maximum of 1.9A, while the 24VDC lines carry up to 0.5A. Concerns were raised about the voltage drop, with the longest run potentially delivering 22V to the locking device, which is just above the minimum operational voltage. However, it is noted that the power supply typically outputs around 25.6VDC, providing a sufficient margin within the acceptable tolerance for the locking mechanism. Overall, the consensus suggests that the short parallel run will have a negligible impact on performance.
sgtpepper777
Messages
4
Reaction score
0
I have an enclosure that has numerous 18AWG cables running through it. These conductors carry 24VDC which power locking mechanisms throughout a building. The enclosure also has a 10AWG cable run to it carrying 120VAC. This is used to power the 24VDC power supply.

The electrician wants to bring the conductor carrying 120VAC in from the bottom left-hand part of the enclosure and route it up the side and across the top to hit the power supply. The 24VDC cables will come in from the bottom right-hand part of the enclosure and run along the bottom and up the same side as the 120VAC conductor.

If we do it this way, we'll have about 2ft where the 120VAC line and the 24VDC lines are in parallel. There is no data communication involved, so I'm thinking the short parallel runs will not have a significant impact on the equipment, but I just want to confirm that before I give the OK.

I don't know if this matters, but the current on the 120VAC line will be a maximum of 1.9A. The current on the DC lines will be a maximum of 0.5A. The locking device can operate at a minimum of 21.6V (=24+/- 10%). The longest run will give me a voltage of 22V at the locking device after the line loss.

Any thoughts? Thanks in advance.
 
Engineering news on Phys.org
0.4V of margin after line loss seems pretty slim to me. Does this include tolerance of the 24V power supply output? I would be more worried about this than crosstalk from 60Hz over a few feet.
 
In actuality, the power supply will be putting out a bit more than 24VDC, so I wasn't too concerned about the 0.4V margin. 25.6VDC is typical, which would be within the maximum 24VDC+10% tolerance of the lock and would end up being ~23.6V at the lock with my longest run. When I do the figures I typically use 24VDC for all calculations so that I have that built in safety cushion.

Based on your answer, though, it sounds like you're of the opinion that any impact from the short parallel run is negligible.
 
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...
Hello dear reader, a brief introduction: Some 4 years ago someone started developing health related issues, apparently due to exposure to RF & ELF related frequencies and/or fields (Magnetic). This is currently becoming known as EHS. (Electromagnetic hypersensitivity is a claimed sensitivity to electromagnetic fields, to which adverse symptoms are attributed.) She experiences a deep burning sensation throughout her entire body, leaving her in pain and exhausted after a pulse has occurred...