Paralleled Transformers: Why Overload & How to Prevent It?

  • Thread starter Thread starter Nahian
  • Start date Start date
  • Tags Tags
    Transformer
Join the discussion
Registration is free. Ask a follow-up in this thread, or start your own.
3 replies · 1K views
Nahian
Messages
4
Reaction score
0
When transformers with the same turns ratio, but different kVA ratings are paralleled , it is possible for the smaller transformer to be overloaded and the larger transformer to be lightly loaded.Why is it so? Can anyone please show mathematical and theoretical explanation?And what can be done to stop the overloading of the transformer?
 
Engineering news on Phys.org
The impedances will be different. Therefore, the sharing of power and current between the parallel branches will not necessarily be in proportion to their KVA ratings.

If you can't do the calculations by hand, any load-flow program modeling those transformers in parallel will calculate the splits in current and power.
 
Nahian said:
When transformers with the same turns ratio, but different kVA ratings are paralleled
Then you are creating a loop - through transformer A and back through transformer B. Be very careful!