Popping noise from speakers when I turn the fan off

  • Thread starter Thread starter grandpa2390
  • Start date Start date
  • Tags Tags
    Fan Noise
AI Thread Summary
The popping noise from the speakers when turning off the ceiling fan is likely due to electromagnetic interference caused by the fan's motor and the wiring in the house. When the fan is turned off, arcing at the switch contacts creates a rapid change in current, which can induce noise in nearby devices like speakers. The discussion also highlights the possibility of improper wiring, where neutrals may be tied together, creating loops that exacerbate the issue. Some users suggest that using the fan's pull chain instead of the wall switch can eliminate the popping noise. Overall, the problem seems to stem from electrical interactions rather than a fault in the speaker or switch itself.
grandpa2390
Messages
473
Reaction score
14
I just noticed this and it is crazy. I have a little speaker that I plug into my computer. it is being charged by the usb port. I got up and turned off the fan in my room and I heard a popping noise. It worried me a bit, so I turned the fan back on (no noise), then I turned it off and I heard the popping noise again. It sounded like it came from the speaker, but I had to turn the fan on/off another 6 times to verify that everytime I turn off the fan, the speaker pops.

Why would it do this? if it was due to electricity draw, wouldn't it affect my laptop first? wouldn't affect it when turning on the fan also? Maybe it is an electromagnetic field or something? This is strange.

by the way, this is a ceiling fan. I was not aware they were on the same circuit, but it is entirely possible since this is a bedroom.

edit: I unplugged the speaker and tested it again, and it does pop (though not as loudly) when it is not plugged into the computer. It has a rechargeable battery in it. So it must be magnetic. right?
 
Engineering news on Phys.org
It is possible that your house wiring makes a big loop on the way to the ceiling fan.
That's a transmitting antenna for rapidly changing current.
The fan motor being inductive does not allow a large rate-of-change of current when switch closes.
But upon opening, there's arcing at the switch contacts and rapid change of current , much like when points open on an automobile ignition.

I have opposite problem. Turning my computer ON makes my touch-dimmer lamps turn OFF. Computer is a capacitive load so rapid current change happens on switch closure instead.

Move your switch real slowly and listen for noise. I had a defective switch causing awful interference with a nearby PA amplifier.
My electrician was surprised when replacing the switch fixed the PA.
Yours might be in process of contact failure from corrosion or weak contact pressure.

old jim
 
  • Like
Likes grandpa2390
jim hardy said:
It is possible that your house wiring makes a big loop on the way to the ceiling fan.
That's a transmitting antenna for rapidly changing current.
The fan motor being inductive does not allow a large rate-of-change of current when switch closes.
But upon opening, there's arcing at the switch contacts and rapid change of current , much like when points open on an automobile ignition.

I have opposite problem. Turning my computer ON makes my touch-dimmer lamps turn OFF. Computer is a capacitive load so rapid current change happens on switch closure instead.

Move your switch real slowly and listen for noise. I had a defective switch causing awful interference with a nearby PA amplifier.
My electrician was surprised when replacing the switch fixed the PA.
Yours might be in process of contact failure from corrosion or weak contact pressure.

old jim

it's a brand new switch. I have been remodeling my house since hurricane Katrina and I just installed that switch a year ago. and, since this is a spare bedroom, I am just now beginning to use the switch because I have converted the room into an office. I don't think it is a failing switch. but your loop theory sounds like my theory with the magnetic field. If the fan is on the circuit with the outlets, then it would make a loop around the room. I'm not sure how it all works. my brother said a while back that the wiring is an old style of wiring. something like the hot goes straight to the fan or something. I don't know.

as for the touch lamp. I have a touch lamp (not dimmer) that does the opposite. every time I lose power, when the power comes back on, the lamp does also. Are you saying that is because of the rapid current change running through the walls in a loop?

edit: I did what you recommended, testing it real slow. and when I move the switch real slow, it does pop when turning the fan on. and it makes a real bad noise when turning the fan off. Like rather than popping, it makes radio static type noise when turning the fan off if I move the switch really slow.
 
The switch being new, it could be faulty since manufacture, then. Or perhaps the fan is lacking a suppresor condenser.
 
  • Like
Likes grandpa2390
The switch may be acting as a spark gap transmitter. As you open and close the switch an arc is jumping the contacts (and even more so when you do it slowly).

Oh, I see Jim already covered this idea.
 
  • Like
Likes grandpa2390
it was just weird. :)
didn't realize there was such a powerful magnetic field in the room changing so drastically due to the ceiling fan. :)
 
grandpa2390 said:
didn't realize there was such a powerful magnetic field in the room changing so drastically due to the ceiling fan. :)

It takes very little radiated E/M power to cause things like that :)

Dave
 
  • Like
Likes grandpa2390
grandpa2390 said:
my brother said a while back that the wiring is an old style of wiring. something like the hot goes straight to the fan or something. I don't know.

Yes, if the hot and neutral are not run together then there's a loop. Pretty common in old houses where an electrician tied several neutral wires together, or connected the wrong white wires together in a junction box.

Every circuit starts with a black and a white wire at the circuit breaker.
The black wire is the one with the smoke in it, called "Hot". It's at 120 volts to earth.
The white one is the return, called Neutral. It's zero volts to earth.
All the current that goes out a black wire should come back through its own white wire, not through another circuit's white wire.

If two white neutrals get swapped in a box someplace, current is happy to return through that neutral instead of its own.
But it takes a different physical route, maybe along another wall making a loop around a whole room. Current in a loop makes an electromagnet...

If several neutrals get tied together, current has several return paths to choose from so will likely divide among them.

Here's a guy who explains such things well.

http://www.mikeholt.com/technical.php?id=grounding/unformatted/emf&type=u&title=Electro Magnetic Fields (EMF)
Typically this is the kind of error we find: sometimes at the end of the run of two branch circuits, the circuits share a junction box. One may feed, say, some outside lights. The other load served through the junction box may be, say, bedroom lights. One load is fed by one branch circuit; the other is fed by the other branch circuit. The hot conductors are wire nutted to their respective circuits, but when it comes to the neutrals, sometimes they are all twisted together with one big wire nut. What does this do? Suppose the bedroom lights are on. The neutral return current, since it is joined with the neutrals of both branch circuits, splits and returns to the panel through both neutrals. This creates two net currents: one by robbing the bedroom circuit of some of its balancing neutral current and the second by putting neutral current on the outdoor light circuit, which gives off an equal magnetic field.
Connecting neutrals in this way creates a parallel path and violates 310-4. Also, it makes the second neutral a part of the first circuit, but since the second neutral runs in another path, there is a violation of 300-3(b). Why does Code prohibit these net-current producing connections? Because it increases the impedance of the circuit and may lead to inductive heating, particularly if the circuits run in metal conduits or metal clad cable. Also the magnetic fields produced often cause problems in electronic equipment
see also
http://www.mikeholt.com/technical.php?id=powerquality/unformatted/EMIKarl&type=u&title=Power Quality Article
 
Last edited:
  • Like
Likes grandpa2390
Thankyou all. I better get back to studying relativity.
 
  • #10
a totally non-tech solution that worked for me was to turn the ceiling fan off with the pull chain instead of the wall switch. Never a pop, I just leave the fan on at the wall and use the chain...
 