Power Factor Correction (open leg on a floating wye)

Click For Summary
SUMMARY

The discussion centers on a switch failure in the A phase of a floating wye connected capacitor bank, which led to overcurrent issues in the B and C phases. The capacitor bank consists of six 400 Kvar capacitors and operates at 13.8 kV, providing power factor correction for industrial loads. The contractor confirmed that the open phase caused the overcurrent in the other phases, and the expected current reduction to 86.6% aligns with the observed behavior when considering the phase-to-phase voltage across the remaining phases.

PREREQUISITES
  • Understanding of floating wye capacitor bank configurations
  • Knowledge of power factor correction techniques
  • Familiarity with three-phase electrical systems
  • Basic principles of electrical load types, particularly constant-power loads
NEXT STEPS
  • Study the operation of floating wye capacitor banks in detail
  • Learn about the effects of open phases on three-phase systems
  • Research the characteristics of constant-power loads and their impact on current distribution
  • Explore advanced power factor correction methods and their applications in industrial settings
USEFUL FOR

Electrical engineers, power system analysts, and technicians involved in power factor correction and maintenance of capacitor banks in industrial environments.

RBloomer
Messages
2
Reaction score
0
We had a switch fail to close on the A phase of a floating wye connected capacitor bank. The C phase fuse was found to be bad and was replaced, however the B phase fuse then blew. The bad switch was then found and replaced. After that the system operated normally. The contractor said the open phase caused the overcurrent on the other two phases. I would have thought that the current on the remaining circuit would reduce to 86.6% of normal. What am I missing?
 
Engineering news on Phys.org
RBloomer said:
We had a switch fail to close on the A phase of a floating wye connected capacitor bank. The C phase fuse was found to be bad and was replaced, however the B phase fuse then blew. The bad switch was then found and replaced. After that the system operated normally. The contractor said the open phase caused the overcurrent on the other two phases. I would have thought that the current on the remaining circuit would reduce to 86.6% of normal. What am I missing?
Welcome to the PF.

Others will be able to give you a better answer than I can, particularly @anorlunda but it would help to know more about the situation. What is the nature of the load? If the load is mostly a constant-power type of load (like switching power supplies), then the current will go up in the other phases to try to supply the same power.
 
The capacitor bank consists of 6 400 Kvar capacitors, 2 in parallel per phase, connected in a floating wye. Each leg has a series 11.5 mH inductor. It operates at 13.8 kV. It is doing power factor correction for typical industrial loads i.e. many motors, ac inverter drives etc.
 
With a floating wye connection, each phase of the capacitor bank sees 13.8/sqrt(3) kV or 57.7% of the phase to phase voltage under normal conditions.

If you energize the same capacitor bank with A phase open (i.e., switch fails to close on this phase), you still have phase to phase voltage across the other two phases. Under this condition, these two phases would be seeing 13.8/2 kV or 50% of the phase to phase voltage.

So my conclusion is that you are not missing anything at all. 50/57.7 is the 86.6% that you expected if you are dealing with the current to the capacitor bank and not the line current.
 

Similar threads

  • · Replies 9 ·
Replies
9
Views
8K
  • · Replies 3 ·
Replies
3
Views
11K
  • · Replies 32 ·
2
Replies
32
Views
7K
Replies
2
Views
1K
  • · Replies 2 ·
Replies
2
Views
3K
  • · Replies 55 ·
2
Replies
55
Views
9K
Replies
8
Views
12K
Replies
6
Views
4K
Replies
40
Views
10K
  • · Replies 6 ·
Replies
6
Views
2K