In AC circuits, capacitors and inductors do not consume energy, yet they affect the power factor by causing fluctuations in energy usage. Power providers charge for low power factor because it increases the required capacity of generators and wiring, which are rated based on amperage rather than wattage. While real power is linked to fuel consumption at power plants, apparent power must still be managed to prevent increased losses due to higher amperage. Correcting phase shifts typically involves adding capacitors, and distributed generation can help adjust power factor by operating out of phase. Ultimately, managing power factor is crucial for efficiency and cost-effectiveness in power distribution.
daredevil
Messages
12
Reaction score
0
In AC circuits, it seems that there is no energy used for capacitors and inductors.

I was wondering how is the energy used causing it to increase and decrease the power factor?. And also, why does the power provider have to supply power(apparent power) for something that is ultimately not even used

Thanks..
 
Engineering news on Phys.org
Apparent power is not supplied as real power by the generator. The reason the power company gets annoyed at (and charges you for) low power factor is that the capacity of generators and wires is based on amperage, not wattage.
 
Thankss..

So, aren't there are generators made based on wattage??.. or can we ignore the apparent power and use a generator to supply for the real power only?

And also when the current returns to distribution point.. different cables with be with different power factors.. so will there be any problem caused by that
 
Pwr comes to us in three phases, each 120 degrees out of phase with the next. We derive pwr by flowing current between the phases. If the phases change from their ideal 120 degrees, you still have full pwr flowing thru each phase, which is what we get charged for. But we now have slightly less voltage between the phases at each instant in time, so we get less usable pwr between the phases.

Correcting this phase shift normally means adding capacitors. But with expanded use of distributed generation; we can run the DG generators out of phase in the opposite direction to help correct the PF on the grid. This is how generator owners sell VARS to the power company.
 
Last edited:
daredevil said:
Thankss..

So, aren't there are generators made based on wattage??.. or can we ignore the apparent power and use a generator to supply for the real power only?
The real power is "real" in the sense that it directly relates to how much fuel the power plant burns. That's why it is the main component of a commercial bill. But how hot a wire or generator gets is a function of amperage, so the worse the power factor the higher the amperage so the larger the wires and generator need to be or the higher the losses will be.
 
Hi all, I have a question. So from the derivation of the Isentropic process relationship PV^gamma = constant, there is a step dW = PdV, which can only be said for quasi-equilibrium (or reversible) processes. As such I believe PV^gamma = constant (and the family of equations) should not be applicable to just adiabatic processes? Ie, it should be applicable only for adiabatic + reversible = isentropic processes? However, I've seen couple of online notes/books, and...
I have an engine that uses a dry sump oiling system. The oil collection pan has three AN fittings to use for scavenging. Two of the fittings are approximately on the same level, the third is about 1/2 to 3/4 inch higher than the other two. The system ran for years with no problem using a three stage pump (one pressure and two scavenge stages). The two scavenge stages were connected at times to any two of the three AN fittings on the tank. Recently I tried an upgrade to a four stage pump...