Power in delevering electricity to a factory

  • Thread starter Thread starter melissa_y
  • Start date Start date
  • Tags Tags
    Electricity Power
AI Thread Summary
The discussion focuses on calculating power loss in a factory's electrical delivery system, specifically comparing two voltage levels: 45200V and 13900V. To determine power loss, the initial current can be calculated using the formula P=I^2R, where resistance is given as 2.72 Ohms. By substituting voltage into the equations P=VI and P=RI^2, the current can be found for each voltage scenario. The power dissipated in the wires can then be compared to assess how much less power is wasted at the higher voltage. Ultimately, this analysis highlights the importance of voltage levels in minimizing energy loss during electricity transmission.
melissa_y
Messages
17
Reaction score
0
A power station delivers 513kW of power to a factory through wires of total resistance of 2.72Ohm. How much less power is wasted if the electricity is delivered at 45200V rather than 13900V?

I have no idea where to even begin except that I should find the intial current which is found by equation P=I^2R

Please help me!
 
Physics news on Phys.org
you can also use the fact of p = I^2R = V^2 / R
 
Voltage is equal to: V=IR

So, if the power is equal to P=RI^2, then it's also equal to P=VI

The current being delivered to the circuit comes from the Power and Voltage relationsip.

To find how much power is lost, you have a new problem that uses the result of the first (you had to solve for I). You use the P=RI^2 to find out how much power is dissipated by the wire.

Change the value of the voltage and repeat. Compare the two results.
 
I multiplied the values first without the error limit. Got 19.38. rounded it off to 2 significant figures since the given data has 2 significant figures. So = 19. For error I used the above formula. It comes out about 1.48. Now my question is. Should I write the answer as 19±1.5 (rounding 1.48 to 2 significant figures) OR should I write it as 19±1. So in short, should the error have same number of significant figures as the mean value or should it have the same number of decimal places as...
Thread 'Collision of a bullet on a rod-string system: query'
In this question, I have a question. I am NOT trying to solve it, but it is just a conceptual question. Consider the point on the rod, which connects the string and the rod. My question: just before and after the collision, is ANGULAR momentum CONSERVED about this point? Lets call the point which connects the string and rod as P. Why am I asking this? : it is clear from the scenario that the point of concern, which connects the string and the rod, moves in a circular path due to the string...
Thread 'A cylinder connected to a hanging mass'
Let's declare that for the cylinder, mass = M = 10 kg Radius = R = 4 m For the wall and the floor, Friction coeff = ##\mu## = 0.5 For the hanging mass, mass = m = 11 kg First, we divide the force according to their respective plane (x and y thing, correct me if I'm wrong) and according to which, cylinder or the hanging mass, they're working on. Force on the hanging mass $$mg - T = ma$$ Force(Cylinder) on y $$N_f + f_w - Mg = 0$$ Force(Cylinder) on x $$T + f_f - N_w = Ma$$ There's also...