Powering a 10HP 460VAC 3-phase AC motor from a standard 120VAC outlet is impractical due to insufficient wattage and the lack of a 3-phase supply. A single-phase outlet typically cannot support the required 10kW for the motor. The discussion suggests that using a 240VAC supply with a transformer to step up to 460VAC is a more viable solution, although this may still require a Variable Frequency Drive (VFD) for proper operation. Additionally, local utility regulations may restrict such high power loads in office settings. Reevaluating the power requirements or considering a motor compatible with available electrical supply could simplify the setup.
smiddleton
Messages
18
Reaction score
0
Does anyone of a transformer that can step up 120vac to 460vac? Or do I need to use two transformers and step it up twice? It is powering a 10hp 460vac 3phase ac motor. Thanks.
 
Engineering news on Phys.org
smiddleton said:
Does anyone of a transformer that can step up 120vac to 460vac? Or do I need to use two transformers and step it up twice? It is powering a 10hp 460vac 3phase ac motor. Thanks.
First question, the 120V AC you plan to use...is that available in 3 phases?
 
NascentOxygen said:
First question, the 120V AC you plan to use...is that available in 3 phases?
Normal ac outlet in office building
 
smiddleton said:
Normal ac outlet in office building
I think that's "No three phase available" answer? So that's a serious setback to your planning.

Despite this, go ahead and work out how many watts equate to 10 hp, and compare this figure with the typical wattage rating in your country for ordinary office outlets.
 
...er, you can't power a 10 hp motor (8kW) from a 120V office outlet (2 kW).
 
  • Like
Likes Alec Dacyczyn
I am also trying to figure out how the OP figures a regular office building 120 volt outlet will provide 3 phase.
 
Averagesupernova said:
I am also trying to figure out how the OP figures a regular office building 120 volt outlet will provide 3 phase.
True. I would need some big caps, it's about 10000 watts to power the motor how we want.
 
Caps will not help - we are taking about power ( 10Kw ~ 460 x 12.6A x Sqrt(3) for the 3 Ph motor - at 120 Single phase 10Kw ~ 120V x 83Amps) . If you have access to the Circuit panel you could wire a Variable Frequency Drive set up for single phase input with 3 phase output, but that still will not "step up" the voltage you need.

Preferably you can get 240VAC (most 120V systems in the USA are split phase 120/240) - so then use a 12+ KVA 240 to 460 single phase transformer. Then a Drive that can provide 10 HP with single phase input, I am sure it exists, but that it pretty large for the single phase and I have not found on in a quick search. Typically drive will have poor power factor and high harmonics ( THD) - requiring more hardware - filters etc...

Try to find a 460V Source.
 
Oh - also such a large single phase load may not be allowed by your utility and or local code.
 
  • #10
10 HP is a lot of power for a machine in an office - are you sure you actually need that much ??

Is there a possibility of thinking afresh with a new lower assessment of power requirement ??

Dropping power requirement and selecting a motor suitable for purpose and which will run on available electric supply will make life a lot easier for you .

If using original 10HP motor is essential then only solution is to have a proper three phase supply with suitable power rating installed .
 