Pressure Difference measurement using Pressure Sensors / Transducers

Click For Summary
SUMMARY

This discussion focuses on selecting appropriate pressure sensors or transducers for measuring pressure differences in a circular cylinder model within a wind tunnel, specifically for use with LabVIEW software. Key recommendations include exploring products from manufacturers such as National Instruments, Omega Engineering, Ashcroft, and Rosemount. The discussion emphasizes the importance of choosing the right price range, differential pressure range, and interface method. Additionally, it highlights the need for signal smoothing in LabVIEW due to the noisy nature of flow measurements.

PREREQUISITES
  • Understanding of pressure measurement concepts
  • Familiarity with LabVIEW software for data display
  • Knowledge of differential pressure transducers
  • Basic principles of fluid dynamics and turbulence
NEXT STEPS
  • Research National Instruments pressure sensors compatible with LabVIEW
  • Explore Omega Engineering's differential pressure transducers
  • Investigate the specifications of Rosemount's differential pressure transmitters
  • Learn about signal smoothing techniques in LabVIEW for noisy data
USEFUL FOR

Engineers, researchers, and students involved in fluid dynamics experiments, particularly those utilizing pressure sensors in wind tunnel applications and LabVIEW for data visualization.

MajSid
Messages
2
Reaction score
0
Dear All,

I am not sure if this is the right place or not for this post so i apologise in advance if not.

I am trying to find some pressure sensors / transducers to measure the pressure difference (with respect to static pressure) at points on a circular cylinder model installed inside a Wind Tunnel. This is the classic Flow over Cylinder experiment, but for the project I am working on, I am supposed to use pressure sensors / transducers to measure the pressure difference and display it in LabVIEW software.

The installed model (cylinder) has ten tapping points to which tubes are connected, and there is an additional tube that gives the static head inside the wind tunnel.

In LabVIEW, I want to display the ten pressure difference values (all with respect to static pressure).

I hope someone could help me out with some suggestions.

Thanks in advance.
 
Physics news on Phys.org
You didn't ask a question. What are you hoping we can help you with?
 
Apologies. Here's the question:

What I really want to know is what pressure sensor / transducer (make / manufacturer) I should be using for this task.

Pardon me for my ignorance, but I've never worked with pressure sensors / transducers before.

I am hoping to measure the pressure difference by connecting the tubes to the pressure sensor / transducer, and to display the pressure difference values in LabVIEW.

Any help / pointers would be highly appreciated.
 
You might start with National's introduction

http://www.ni.com/white-paper/3639/en/

there are at least a zillion transducers to choose from

here's a hobby site's smorgasboard
http://www.jameco.com/1/3/differential-pressure-sensor
probably the same ones as this industrial outfit offers
http://www.omega.com/pptst/px170.html
and their smorgasboard is
http://www.omega.com/toc_asp/subsectionSC.asp?subsection=B02&book=Pressure



Ashcroft is an old name in industrial & commercial equipment
http://www.ashcroft.com/products/pressure_transducers_transmitters/low/

here's what we used in the nuclear plant
http://www.instrumart.com/assets/Rosemount_2051_datasheet.pdf

pick your price range first, your differential pressure range second, then your preferred method of interface .

Be aware flow is a "noisy" process due to turbulence. Rosemount makes differential pressure transmitters for flow measurement as well as for level measurement which is a quieter process.
Your Labview i would think allows you to tailor signal smoothing as needed.
 
Last edited by a moderator:
jim hardy said:
Be aware flow is a "noisy" process due to turbulence. Rosemount makes differential pressure transmitters for flow measurement as well as for level measurement which is a quieter process.
Your Labview i would think allows you to tailor signal smoothing as needed.

I second pretty much everything you already said. This part here is likely a non-issue, though. Most likely the transfer function associated with any sort of tubing attached to his pressure ports is going to attenuate any high-frequency pressure fluctuations and read back nearly the mean. If the actual desire is to resolve the higher frequencies, moving to something like a Kulite or an Endevco transducer may be necessary.
 
Hey there, think I may have found something helpful here at this blog:

https://www.telematic.com/Blog/post/2014/07/16/Characteristics-Of-Pressure-Transmitters-Pressure-Sensors-And-Pressure-Transducers

Some of the info in here should answer some of your questions.
 

Similar threads

Replies
9
Views
3K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 26 ·
Replies
26
Views
2K
  • · Replies 11 ·
Replies
11
Views
2K
Replies
0
Views
2K
  • · Replies 2 ·
Replies
2
Views
3K
  • · Replies 24 ·
Replies
24
Views
3K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 45 ·
2
Replies
45
Views
6K
  • · Replies 9 ·
Replies
9
Views
4K