Pressure regulator model: how to study its stability

  1. Feb 2, 2014 #1
    Hi all,

    I need a model of a pneumatic pressure regulator. The model should be as simplest as possible and use an optimization solver to identify the regulator parameters in order to fit the performance I find in the datasheet of a commercial pressure regulator. I have already done a model using simpscape and I guessed the regulator parameters. In this condition the system is stable and it works as expected. When I run the optimization routine, the solver changes slightly the parameters and the system is not stable anymore, so the solver doesn't understand how to optimize the cost fuction. The model is non linear. How could I do for analyzing were the unstability arises?

    Thanks
     
  2. jcsd
  3. Feb 9, 2014 #2

    Baluncore

    User Avatar
    Science Advisor

    You must understand the feedback mechanisms available in your model.
    Reality and non-linear models will oscillate at pressure dependent flow rates.
    You must restrict model parameter search variation to the domain that is free of oscillation.
    You will therefore have to study the bounds of stability before further optimisation.

    Unfortunately the best operating point is often right on the edge or regeneration.
    There is a trade-off, maybe by optimisation you are designing an unreliable product.
     
  4. Feb 9, 2014 #3
    Thanks Baluncore, is there any systematic way to search for that boundary or should I do by trials?
     
  5. Feb 9, 2014 #4

    Baluncore

    User Avatar
    Science Advisor

    Trial and error is the simple learning approach. A programmed grid search in several parameters would work if you could quickly and reliably identify the onset of oscillation.
    Don't forget you are only fine tuning the simplified model, not the real world device you believe you have modelled.
     
  6. Feb 9, 2014 #5

    Q_Goest

    User Avatar
    Science Advisor
    Homework Helper
    Gold Member

    Can you provide a cross sectional picture of the regulator you are trying to model? Can you describe your model so far? Things like the mass of the moving parts (poppet, stem, diaphragm backing plate, spring, etc...), flow restrictions through the valve (give consideration to how far open the valve actually is at any one point in time), how upstream and downstream pressure reacts to the opening of the valve, etc... Can you provide a diagram of forces on the moving parts? What kind of time step you are using and is it is a variable in your program? What kind of output are you creating?
     
  7. Feb 12, 2014 #6
    Hi all,

    @Baluncore: thanks for your reply I'll try with a programmed grid.

    @Q_Goest:

    here a cross sectional picture of the regulatore I'm trying to model:

    valve_pitot.png

    Yes, I can describe the model and I'm developing a simscape model to reproduce the dynamic of the pressure regulator. Here a sketch with the forces of the moving parts:

    valve_sketch.png

    Xop, xopp: free length of the poppet and piston spring
    Xp, xpp: piston and poppet displacement
    Fcp,pp: contact force between the poppet and the piston
    Fcps,pp: contact force between the poppet and the poppet seat
    kp, kp: stiffness of the piston and poppet spring
    Fr: friction force
    mp, mpp: mass of the piston and the popet


    I use a constant time step solver and the time step is 0.001s

    I'm trying to reproduce the pressure - flow rate curve of the pressure regulator I see in the datasheet and its step response. Here the pressure - flow rate curve I'm trying to fit:

    [ vppm.png

    I'm using an optimization solver to find the parameters that minimizes the SSE between the datasheet curves and the ones of the model. Moreover I have added non linear constraints to comply the valve step response specifications (i.e. rise and settling time and peak overshoot).

    In order to get a similar dynamic behaviour of the pressure regulator with any set of paramaters, I have parametrized the spring stiffness in function of the valve max displacement (i.e. valve cross area) and the pressure differential between the outlet and the setpoint. In this way the valve is completely open with a specific pressure differential. This worked very well with a valve with the following kind of pressure - flow rate curve, because the max flow rate doesn't change with outlet pressure

    [ chart_3.jpg

    But for the valve before mentioned graph the situation is different, higher pressure, higher flow rate, so I believe the area changes with pressure, but I didn't understand how to do it in my model. This is another open issue of my model. Maybe the spring parametrization is wrong?

    Hopefully to have well stated my problems. Any suggestions is very appreciated.

    cheers
     
  8. Feb 12, 2014 #7

    Baluncore

    User Avatar
    Science Advisor

    The only mode of oscillation I can see in your poppet valve model is the delay in piston movement to counter the valve when it approaches closure. By changing the poppet valve for a spool valve the positive feedback chatter should be eliminated. Attached is an edit of your diagram.
     

    Attached Files:

  9. Feb 12, 2014 #8

    Q_Goest

    User Avatar
    Science Advisor
    Homework Helper
    Gold Member

    Hi serbring. Those graphs you posted show how a regulator responds to changes in flow rate given a fixed pressure setting on the regulator. For example, the regulator might be set at 1.2 bar at zero flow (ie: "lockup") and as the demand for flow increases, the pressure on the regulator outlet decreases as can be seen in the first graph.
    vppm.png
    The reason the outlet pressure on the regulator drops with an increase in flow isn't really a "dynamic" issue. The poppet in the regulator isn't changing position when that happens, it is in one position and it stays there while the system flows at the given flow rate. So when flow increases to 450 l/min, the pressure on the regulator has dropped to roughly 0.9 bar as shown on the graph. Note that I wouldn't trust the second graph you provided. It doesn't look like any actual data or any theoretical model of the regulator was taken into account on that one to be honest. A real graph of pressure versus flow for a regulator looks like the first graph you provided with a gradual drop off of pressure as flow increases. So I'll ignore the second graph for this discussion.

    The diagram you provided is ok, though I didn't try to look at it in detail. I do see a few problems though. First, as mentioned before, the graph is looking at a valve without movement of the poppet or diaphragm. So there's no need to consider time rate dependant forces on the regulator. You also can neglect frictional forces if you'd like since those are generally small compared to the spring and pressure forces. If you're trying to model that graph you provide, you want to look at a static force diagram of the regulator with pressure causing a force on the poppet and diaphragm and spring forces causing forces where they exist.

    Next, you will need to model the flow somehow. The valve poppet has some balance of forces when the valve is closed and pressure is at the set pressure of the regulator. At that point, the spring is providing a force exactly equal to the pressure forces when the poppet is closed. In reality, there's a problem with this simplistic model and that is that the seat needs to have a high enough contact force to seal the fluid, so the spring load is actually lower than the pressure forces at that point since you need some additional force to create the seal but for simplicity, I'll neglect that. We can come back to it later if you want.

    The valve is closed at a given set pressure so we'll assume flow is zero at that point. That point on the graph shown above for example might be 1.2 bar with 0 flow (l/min). That's the point where forces are balanced and the poppet is touching the seat. Now the valve opens as pressure downstream where it is being sensed, drops. As pressure drops, the force on the diaphragm and poppet drop to a new, lower value. Since that force is lower, the spring will push the poppet open and come to equilibrium at a new location. When the spring extends like this, the force goes down according to the spring rate times the change in length of the spring, so the spring also has a lower force which must equal the lower pressure force. That's the point you need to determine for a given 'flow rate'. Actually what you need to determine is how far the poppet opens at that point and what the corresponding flow coefficient will be. It obviously won't be "full open" since that won't happen till the pressure decays enough to fully extend the spring and push the poppet to that point. So the full open point can be determined by determining the location of the poppet, the spring load at that point and the corresponding pressure load that puts the entire assembly into static equilibrium. That pressure will necessarily be lower than the set pressure which is why the curves on the graph drop as flow rate increases.

    More on how to calculate the flow restriction of the poppet if you need it, just ask.

    If you really want to understand how the regulator responds to a sudden change in pressure or an oscillating change in flow rate, then that would be a dynamic issue that requires calculating not just the instantaneous position and flow of the valve but also the inertia of the moving assembly and also the variation in pressure under the diaphragm if there is a restrictive orifice as you show in the diagram. That gets a bit more complicated, but I think you need to figure out how to model the valve flow restriction first and understand how that can create the graph you posted before moving on to a true dynamic model of a regulator.
     
  10. Feb 13, 2014 #9
    I'll model the pressure force on the valve. Thanks!

    I got it, but if there will be 0.4bar of pressure differential between the outlet pressure and the setpoint, the spool displacement is 1mm (consequently a specific cross valve area) independently of the outlet pressure , right?

    with my model I'm able to fit that chart, using the before mentioned spring parametrization: with 0.1bar of pressure differential between the outlet pressure and the setpoint the valve is completely open and it doesn't seem to happen to the valve of the following chart.

    [GRAPH 1]
    vppm.png

    After a meditation, I'm wondering how would it be the GRAPH 1 if for each pressure level the regulator would be test to a 0 bar? Would it be something like that?

    [GRAPH 2]
    pneumatic_drive.png

    As far as I have understood in a chocked condition the valve flow rate is not dependent by the outlet pressure but only by the inlet pressure, the sonic conductance, the cross area and so on. So I would believe all the lines will drop to the same flow rate. In the GRAPH 1 all the lines don't look to drop at the same flow rate, right? So could it be possible that for the GRAPH 1 the inlet pressure at 6 bar test is different than the one at 10 bar test?

    The piston/diaphram dynamic is modelled, look at the rough sketch, xp is the piston displacement.

    I modelled the flow using that simscape block:
    http://www.mathworks.it/it/help/physmod/simscape/ref/variableareapneumaticorifice.html

    But I didn't model the flow force to valve, but I'm gonna do it.

    I got it...I'll try first to model flow force to the poppet first.

    Thanks to all, hopefully my doubts are clearly stated...if not, please ask me. :)
     
    Last edited: Feb 13, 2014
  11. Feb 21, 2014 #10
    Hi all,

    I'm trying to follow your suggestions: I modelled the flow force to the model in a easy way and the pressure fluctuation is lower than in the previous model.

    Then I tried to identify the pressure regulator parameters to fit a reference pressure - flow rate cuve. I performed the identification with the an optimization solver and using the SSE as cost function.
    The flow rate for all the curves are computed with an inlet pressure of 7 bar and using a ramp and a pressure source I change the outlet pressure during the simulation. The setpoint is constant during the simulation and it is set to the intial outlet pressure, so for the red curve, the setpoint is 6 bar and the outlet pressure changes linearly from 6 to 5 bar. Here you can see a sketch of my model:

    model.jpg

    Here the reference curve for the flow from 1 to 2:
    vppm.jpg

    Here the one of my model:
    curve.jpg

    I can explain the curve of my model: I see the lookup, the drop and the choked flow condition. In my model the flow rate in the choked condition doesn't change with the outlet pressure, instead for the reference curves it looks to change and I can't understand the reason of it. Is the valve Cd (Discharge coefficient) pressure dependent? Does the valve open more at higher pressure than in lower ones? In this case why? Could it be the case the reference curve are created with different inlet pressure? Any suggestion is appreciated

    Thanks

    Cheers


    Serbring
     
    Last edited: Feb 21, 2014
  12. Feb 22, 2014 #11

    Q_Goest

    User Avatar
    Science Advisor
    Homework Helper
    Gold Member

    Hi serbring. I can't tell for sure what you're doing in your model, but the output graphs look reasonable. First, let's talk about "flow force". I'm not sure what you mean by that but I assume you're referring to the force exerted on the poppet due to the change in momentum of the gas as it impinges on the poppet as opposed to the force produced by the difference in pressure across the poppet. The former is small and can generally be neglected. The latter is significant for an unbalanced regulator such as the type you show in the picture. A balanced regulator has a poppet that has the same pressure on both ends so that the forces on the poppet during operation are the same and can be neglected.

    You should have a calculation that shows shows how the forces are balanced in a static condition. That force balance calculation determines the poppet lift. The poppet lift gives you curtain area which is the cylindrical area around the opening of the poppet. That curtain area is the circumference times the height. That area is your flow restriction which, when multiplied by your discharge coefficient, gives you the valve's flow capacity. The flow is then calculated per that link you provided here:
    http://www.mathworks.com/help/physmod/simscape/ref/variableareapneumaticorifice.html

    Note that the link you provided also gives the equation for the critical pressure ratio which tells you if the flow across your poppet is choked or not. If flow is choked AND if the valve poppet has come full open, the line on those graphs goes verticle which you can see on some of the graphs above. On those graphs that don't show a verticle section of line, the valve poppet hasn't gotten to the 'full open' position yet, so a drop in the downstream pressure allows the poppet to open more, increasing CdA and increasing flow. It's only once your poppet has reached it's maximum lift (max open) that you no longer get any increase in flow by decreasing downstream pressure. That statement assumes of course, that flow is choked at the poppet curtain area.

    Regarding discharge coefficient, the discharge coefficient can certainly change as the valve poppet changes position and even as the pressures change. The discharge coefficient in this case is like a 'catch all' for various things that can affect the flow. Note that normally discharge coefficient for an orifice has a more specific meaning regarding the vena contracta. It means the same here but the flow geometry is obviously a bit more complex.
     
  13. Feb 26, 2014 #12
    Hi Q_Goest,

    thanks for your helpful reply, it took a while to meditate about it. Firstly I didn't understand that the poppet could be not fully open with lower outlet pressure. I was firstly mislead by the first valve graph with the straight lines and actually I still don't understand how it happens.

    Regarding the flow force I meant the force produced by the poppet pressure unbalance. I changed the poppet with a balanced one as suggest by Baluncore. In my model the poppet dynamic is affected only by the spring stiffness and the pressure differential between the outlet pressure and the setpoint. So I have modeled somehow that poppet pressure unbalance. Here a sketch of the model:

    valve_sketch_fullpng.jpg

    From the force equilibrium equation I derived the valve area relationship with the outlet pressure P[itex]_{out}[/itex] during the charging. In calculating it I supposed that there is a sharp boundary where the pressure act. So:
    [itex]A_{s0}[/itex]: area where the inlet pressure acts when the poppet is fully closed
    [itex]A_{o0}[/itex]: area where the inlet pressure acts when the poppet is fully closed
    [itex]A_p[/itex]: poppet opening area
    [itex]A_d[/itex]: area of the lower side of the poppet
    [itex]A_s=A_{s0}+A_p cos(\theta)[/itex]: relation between the area where the inlet pressure acts and the poppet opening area
    [itex]A_o=A_{o0}-A_p cos(\theta)[/itex]: relation between the area where the outlet pressure acts and the poppet opening area
    [itex] \theta [/itex]: poppet conical angle
    [itex] A[/itex]: piston area
    [itex] x_{p}, x_{pp} [/itex]: piston and poppet displacement
    [itex] x_{op}, x_{opp} [/itex]: piston and poppet spring free length


    Here the force equilibrium:

    [1] [itex] k_p (x_{op}-x_p)- P_{out}A- k_{pp}(x_{opp}-x_{pp})+P_{out}(A_s cos(\theta) -A_d)+P_{in}*A_s cos(\theta)=0[/itex]

    I rearranged the equation [1] for deriving [itex] A_p [/itex]in function of [itex]P_{out}[/itex] for: [itex] P_{set}=k_p*x_op[/itex], [itex] \Delta P=P_{set}-P_{out}[/itex], [itex]k_{pp}=k_p[/itex] and [itex]x_p=x_{pp}[/itex]:

    [2] A[itex]_{P}=\frac{P_{in}(A_{s0}cos(\theta)-A_{d})-K_{pp}x_{0pp}+\Delta P A+P_{out}A_{o0}*cos(\theta)}{{cos(\theta)}^{2}(P_{in}+P_{out})}[/itex]

    Here the derivative of the equation [2] with respect the outlet pressure (Pout):

    [3] [itex]\frac{d A_{P}}{d P_{out}}=\frac{k_{pp}x_{0pp}+P_{in}(A_d+cos( \theta )(A_{o0}-A_{s0}))-\Delta P A}{{cos(\theta)}^{2}(P_{in}+P_{out})} [/itex]

    it seems the valve area decrease with increasing of Pout, so it should be more open with lower outlet pressure and that it's not like that from the valve flow rate - pressure curve (here the curve again):

    vppm.png

    I tried to change the balanced poppet with unbalanced one, but it doesn't change the story.

    Here a technical drawing of the valve I'm trying to model:

    Valve_drawing.jpg

    I still don't the why the pressure regulator behaves like that. Is there an effect I didn't take into account?

    Thanks

    cheers
     
    Last edited: Feb 27, 2014
  14. Feb 27, 2014 #13

    Q_Goest

    User Avatar
    Science Advisor
    Homework Helper
    Gold Member

    Hi serbring. I went through your post and I’m a bit confused. Equation 1 looks fine. I see you’re using forces downward as being positive and forces up as being negative. I’m not sure if you’re using angles properly, I wouldn’t worry too much about it though. I assume you’ve just rearranged equation 1 to get equation 2 so that’s fine. But I’m not sure about equation 3. Why do you want to take a derivative like that? I see no need to do that and I’m not sure what that even physically represents.

    Let’s look at a simplified model for a second, then you can go back to adjusting it for valve poppet angles and so on. For a balanced poppet, we can neglect pressure forces on the poppet and let’s also neglect the second spring you show that’s under the poppet. You can add those in later. That leaves you with force down from the spring is equal to force up due to pressure on the diaphragm. Now let’s consider a simple example using the following values for our regulator:
    Diaphragm area = 10 square inches
    Spring rate = 1000 pounds per inch
    Set pressure = 100 psig

    For this regulator, the force up due to pressure is just the diaphragm area times the pressure: 10 square inches * 100 psi = 1000 pounds.
    To have the regulator ‘set’ at this point, we need the valve to just come closed at 100 psi, so the spring is almost able to push the poppet off the seat but not quite. So the spring has to push down with a force of 1000 pounds which means that it has to be compressed by x = F/k. So the spring is being compressed 1 inch.

    If we took all the pressure off of the regulator and if the spring could actually move the poppet at that point, the poppet would open 1 inch. However, if pressure dropped to only 90 psig, you have a force upwards of 90 psi times the diaphragm area of 10 square inches or 900 pounds. Looking at the spring again, the spring is only compressed 0.9 inches. So with a discharge pressure of 90 psig this particular regulator has a poppet that’s open exactly 0.1 inches.

    Once you know how far the poppet is open, you can calculate flow. Let’s say our poppet diameter is 1” and at a set pressure of 100 psi, it has a 0.1” opening when outlet pressure drops to 90 psi. The flow restriction through this valve is given by the curtain area which is the circumference times the height. So that’s 1” * .1” * pie = 0.314 square inches. That opening may have a discharge coefficient of 0.7, but that will be a function of the valve’s geometry and is generally only derived experimentally. From my experience, it generally is in the range of 0.6 to 0.8. Now if you have some inlet pressure you can calculate the flow rate by going to that web page you pointed to before. You have upstream pressure, downstream pressure and your CdA (discharge coefficient times area which is your flow restriction).

    The graph you posted has numerous lines. Each line is a set point for that regulator. The lowest line shows a set point of 1.2 bar. Wherever you got this graph from, it should tell you what it assumes for an upstream pressure. The graph doesn’t say, but that is implied somewhere, wherever you got the graph. If you did an analysis on the regulator that you got the graph from, you should be able to sum the forces as shown above, determine how far open the valve poppet is at any given discharge pressure, determine the corresponding flow restriction, and from the pressures on the inlet and outlet of your regulator, you should be able to calculate the flow and come up with the graph.

    Note that as long as your regulator poppet continues to open (and presumably the flow restriction goes down, which is a function of geometry) the flow rate should go up, regardless of whether or not it is choked. Because as the poppet opens, you get a larger flow area (curtain area). Once the poppet is fully opened and the flow restriction stops changing with downstream pressure, and assuming the valve is choked, lowering the downstream pressure isn’t going to change anything.

    Hope that helps.
     
  15. Feb 28, 2014 #14
    Hi Q_Goest,


    Thanks for your helpful reply, maybe there was a misunderstanding about my doubt, I will be clearer. I 'm sorry for it.
    Thanks to you, I found a mistake on the angles of the equation 1 ( :) ): I have to change the [itex] cos(\theta)[/itex] with [itex] sin(\theta) [/itex]. Unfortunately I can't edit anymore the formula of the previous post. I derived the equation 3, because as far as I uderstood the poppet displacement isn't only dependent by the pressure differential between the outlet pressure and the setpoint. Look at the following graph:

    vppm_marked.jpg

    at the point A the outlet pressure is dropped of 0.2 bar as at the point B, but at the point A the poppet displacement is higher than for the point B, otherwise the flow rate should be the same, right?

    Supposing a simple pressure regulator, I can calculate the force balance equation:

    [1] [itex] k_p (x_{op}-x_p)- P_{o} A=0[/itex]

    But [itex]k_p*x_{op}=P_{set}A[/itex]

    Therefore:

    [2] [itex] -k_{p} x_p + (P_{set}-P_{o})A=0 [/itex]

    So the equation of the poppet displacement is [itex]x_p[/itex]:

    [3] [itex] x_è=\frac {(P_{set}-P_{o})A }{k_p}[/itex]

    The equation 3 can't explain why the poppet displacement is higher for the point A than for the point B. So I thought the poppet force unbalance might explain it. For this reason I calculated the derivative of the previous post and I believe it can explain how the poppet area will change with the increasing of [itex] P_{o}[/itex] in a static condtion. Anyway my statement about the derivative was wrong: it isn't always positive with [itex] P_{o}[/itex] but it depends by the other equation parameters.

    My big doubts are: why the poppet displacement at the point A is higher than at the point B? Why the the flow rate for point C is higher than point D?


    Thanks again. :)

    Cheers
     
  16. Feb 28, 2014 #15

    Q_Goest

    User Avatar
    Science Advisor
    Homework Helper
    Gold Member

    Hi serbring,
    I’m trying to determine what your notation is. You posted some earlier:
    [itex]A_{s0}[/itex]: area where the inlet pressure acts when the poppet is fully closed
    [itex]A_{o0}[/itex]: area where the inlet pressure acts when the poppet is fully closed
    [itex]A_p[/itex]: poppet opening area
    [itex]A_d[/itex]: area of the lower side of the poppet
    [itex]A_s=A_{s0}+A_p cos(\theta)[/itex]: relation between the area where the inlet pressure acts and the poppet opening area
    [itex]A_o=A_{o0}-A_p cos(\theta)[/itex]: relation between the area where the outlet pressure acts and the poppet opening area
    [itex] \theta [/itex]: poppet conical angle
    [itex] A[/itex]: piston area
    [itex] x_{p}, x_{pp} [/itex]: piston and poppet displacement
    [itex] x_{op}, x_{opp} [/itex]: piston and poppet spring free length

    Then you have what seems like a problem equation:
    [1] [itex] k_p (x_{op}-x_p)- P_{o} A=0[/itex]
    Which is your force balance for a simple regulator. It says the spring rate times the quantity: free length of the spring minus the piston displacement, minus the pressure Po times the ‘piston area’ (assume that is your diaphragm effective area for a diaphragm type regulator or the piston area for a piston style regulator) and that all equals zero for static balance. You don’t say what Po is but I assume that is your actual outlet pressure which I assume is supposed to be equal to or less than the set pressure.

    But look at the spring force in that equation... Spring force is supposed to be spring rate times how much the spring is compressed. That’s not what you have in the equation. For that spring displacement part of your equation, you need to show how much this spring is compressed. So the amount of compression in your spring (dx) is the free length minus the compressed length, right? The length of the spring after you’ve compressed it has to be subtracted from the free length to give you how much the spring has been compressed which is dx. Then multiply by spring constant to get your force.

    Then you say:

    [itex]k_p*x_{op}=P_{set}A[/itex]

    Which is spring rate of the piston spring times the free length of the spring which has to equal the set pressure times the area. But spring rate times free length gives you a force equal to the force of compressing the spring so that it is absolutely flat and has no height at all.

    Now let’s go back to one of your questions. You asked:
    Let’s talk about a pressure balanced regulator first since that’s a bit easier to understand and you can always modify your equations later to add in additional forces due to pressure and spring loads on the poppet. Equation 1 above should reduce to something like k dx = PA where dx is how much the spring has been compressed (free length minus compressed length). So for some change in pressure (dP) the only thing we have in that equation to make it balance is dx, so dP is linearly proportional to dx. Do you agree? If so, then for any absolute change in pressure, dP, the regulator poppet has to react by changing displacement, dx and those terms are linearly related. Poppet displacement therefore is only dependent on the pressure differential between the outlet pressure and the set point. For the graph in question, point A and point B both show a difference in pressure differential between the outlet pressure and the set point of 0.2 bar, so the valve poppet has opened the same amount in both cases.

    NOTE: The graph doesn’t tell you if the springs used in the regulator are the same or not and it doesn’t tell you what the upstream pressure is. Generally, regulator manufacturers will have numerous different springs for their regulators to handle different outlet pressure ranges because they try to optimize the valve for the pressure range the valve will be operating in. So we can’t say for sure that the amount of poppet opening for those two cases are necessarily the same, but if the same spring was used for each case, then the poppet opening is also the same.
     
  17. Mar 1, 2014 #16
    Hi Q_Goest,

    Thanks for your helpful reply.
    I'm sorry, I changed the subscript for the outlet pressure, let's use [itex] P_o [/itex] for it. There was a mistake in the symbol list, I corrected it as you can see in the bolded text in quote. Here a valve sketch that hopefully will help you to understand my notation:

    Valve_sketch.jpg

    The dotted lines represent the poppet when it's open.

    I say:

    [itex]k_p*x_{op}=P_{set}A[/itex]

    Because when: [itex]P_{set}=P_o [/itex], the valve must be closed, so [itex] x_p=0 [/itex]. Under this assumption my model regulates properly the outlet pressure.

    I completely agree with it.

    Why the valve flow rate is higher for point A then point B? I can't explain it.


    The curves are for a specific valve range (0-2 bar) so I would believe that is the spring rate is the same for all curves. Regarding the downstream pressure, I have few dobts about it, but I talked with the sales man and he said (in not confidently way) that it is the same. Infact in another page of the catalogue I have found the flow rate - pressure chart for the same valve but with a different nominal diameter there is this :

    char_nuovo.jpg

    The choked condition is the same so I would believe the upstream pressure is the same for all curves.


    Thanks again for your preciuos help! :)

    Cheers
     
  18. Mar 1, 2014 #17

    Q_Goest

    User Avatar
    Science Advisor
    Homework Helper
    Gold Member

    Hi serpring,
    So are you saying that [itex]x_{op}[/itex] is equal to the amount the spring is compressed? For example, if a spring has a free length of 2 inches and it’s compressed half an inch then it’s 1.5 inches long at Pset but [itex]x_{op}[/itex] is equal to half an inch. Would you agree?

    I just noticed that the graph you are referring to is for an electronic regulator built by Festo. It is not a conventional, spring loaded regulator such as the ones we’ve been talking about. There are various ways to produce the force needed to open the valve. One way is to use a spring. Another very common way is to use the pressurized gas upstream of the regulator. There are various ways of using this gas. One way is to “dome load” a regulator using a conventional spring loaded regulator. Using this method, you have a simple, spring loaded regulator (preferably a 'self relieving' type) that puts gas pressure above the diaphragm or piston. That pressure pushes down just like a spring but because the volume of gas is generally fairly large compared to the displacement, a regulator loaded this way can more accurately control the outlet pressure. Basically, the equivalent spring rate of the gas is low compared to a spring.

    Another way is to have some electronic valves that adjust the pressure in the dome of the regulator. This should also help to control outlet pressure but the primary reason to do this is to allow for electronic control. So with this type of arrangement, the controls and electric circuits will have some influence on the regulator outlet pressure. It isn't a simple spring arrangement. That's what the Festo regulator is doing. So our discussion around the spring loading of the regulator isn't applicable. This regulator isn't a spring loaded one.
     
  19. Mar 2, 2014 #18
    Hi Q_Goest,

    Thanks again for your helpful reply. I assume [itex]x_{op}= 2[/itex], because the spring is compressed when [itex]P_o > P_{set}[/itex] and it is extended when [itex]P_o < P_{set}[/itex]. It's not probably true because this means to change the spring anytime the setpoint is changed. I was looking for a quick way to model it. Is there any better way of modeling it?

    You're on right. I haven't understood that much the technical drawing you can see in one of my previous posts, but as far as I have understood the diaphrams is pushed down by a solenoid, right? So somehow the pushing force is related to a voltage, right?
    So under this light the valve areas for the points A and B are still the same? Moreover I don't understand why the max flow rate for the line starting from 2bar (point C) is higher than the line starting from 1.2 bar (point D).
    Do you have any suggestion about modeling that kind of valve? Actually I'm completely confused, after 3 months of modeling that valve I still don't have a good model of a pressure regulator and I don't have any how moving forward.

    Cheers
     
  20. Mar 2, 2014 #19

    Q_Goest

    User Avatar
    Science Advisor
    Homework Helper
    Gold Member

    Hi serbring,
    It sounds like you are having some trouble with modeling the spring force. The force exerted by a spring is equal to the spring constant times the amount of compression. F = k dx. So for a spring load of 100 lb/in for example, for every inch the spring is compressed, the force increases by 100 lb. So compress 1 inch, the force is 100 lb. Compress 2 inches, the force is 200 lb. Etcetera.

    This particular regulator uses a diaphragm for its sensing element so if the area is 10 square inches and has a pressure on it equal to 1 bar, then the force is 145 lb. In that case, the spring has to produce a force of 145 lb, so it has to be compressed 1.45 inches. Note that 100 lb/in * 1.45 inches = 145 lb. That equals the force on the diaphragm so that they are in equilibrium.

    I’m sorry but that’s incorrect. The diaphragm is pushed down by the air which is regulated into the chamber (sometimes called a “dome”) above the diaphragm. I would guess that there are solenoid valves to control the air pressure in the dome. The voltage isn’t directly related to the pressure.

    That’s not something you can tell from this analysis because it isn’t a spring loaded regulator. The gas pressure can be highly nonlinear and follow a different curve for each setting.

    Regarding modeling this valve, why do you need to model it? Is this a school project? If you want to model it, you need a lot of details about the valve such as dimensions, spring constants, volumes, how the electronics are used to control the set pressure, etc... You also need to figure out how it works. Perhaps you can explain why you're modeling this and how accurately you need to do so.
     
  21. Mar 2, 2014 #20

    AlephZero

    User Avatar
    Science Advisor
    Homework Helper

    Instead of trying to model the physics (difficult) and electronic control system (impossible unless you know how it is designed), you could attack this from the other direction. You said you have a plot of the step response of the device, as well as the steady-state response curves you have shown. So do a "system identification" exercise to find the transfer function from the step response.

    I don't know what theoretical background you have, but the details should be covered in courses on control systems theory, or experimental vibration measurement.
     