Hi serbring. My appologies if I'm not clear. I agree with what you're saying and I think I understand what you're trying to accomplish, I guess we just have a different perspective of the different ways this can be done. Controlling to a pressure and having a regulator take over from there is a valid approach and it may work just fine, but my concern regards the hysteresis which is inherent in the regulator. Perhaps I can explain better.
I believe what you want to do is take a strain gage reading as an input to your controls which will be used to vary pressure on your brake from some minimum to a maximum. For example, if you supply 0 bar, your strain gage will be at one end of the range; let's call this 0. And if you apply the maximum pressure, for example 10 bar, your straing gage will be at the highest end of its range; let's call this 10. For the sake of simplicity, let's just say there is a linear relationship between pressure and strain gage reading, so for a pressure of 0, you get a strain gage reading of 0 and for a pressure of 10, you get a strain gage reading of 10.
My understanding is that you will have a strain gage reading in mind that you want to adjust to. Let's say that number is 5.0, so you want your pressure to be 5.0. Of course, the system won't be that easy and you have to adjust that pressure until you get the value on the strain gage you desire, so you may have a PID loop looking at the strain gage reading and that is trying to adjust the set pressure of the regulator until you have the proper reading on your strain gage. Is that correct?
If that's the case, then what you'll find is that this regulator has a hysteresis. You may try to get the pressure to 5.0 because you want the strain gage to read 5.0. For example, let's say you have a strain gage reading of 4.5 and your controls are attempting to move that up to 5.0, so they increase the value of the set pressure. As they do that, you may find that the strain gage reading overshoots and goes to 5.2, so now you need to reduce the pressure.
If you stop sending signals, the pressure regulator doesn't try to change the set pressure and it maintains this pressure, so your strain gage will settle out to some reading around 5.2. But now your controls (PID loop) tries to reduce this strain gage reading by reducing the set pressure reading. For the sake of this example, let's say the hysteresis in this regulator is 1.0. It might be 0.8 or 1.3, that doesn't really matter. It has some hysteresis which is greater than zero and probably closer to 1 bar but it will be something. It won't be zero.
Now your strain gage is reading 5.2 and you need to reduce that. Your set pressure at this point might be at 5.0 or it might be at 5.5, that doesn't really matter. Let's just say it is 5.0 for this example. What your controls have to do is reduce the strain gage reading to 5.0, so they start reducing the set pressure point that you have sent to your regulator. So it starts decreasing. The set point starts out at 5.0 and drops to 4.9, 4.8, ... 4.1 and still nothing happens because the set point has to pass all the way through the hysteresis before it can actually affect a change to the set pressure. During this time, the regulator remains closed, so the pressure on the brake doesn't change and the strain gage reading continues to say 5.2. When the regulator set point finally reaches 4.0, it begins to vent the pressure off the brake and the strain gage starts to decrease. So now your controls are sending lower and lower signals to the regulator to decrease the strain gage reading. Those controls are sending out 4.0 then 3.9 then 3.8, etc... Now the pressure starts venting and the strain gage reading drops from 5.2 to 5.1 to 5.0, etc...
Your controls may overshoot and the strain gage might go to 4.9, in which case, the controls may be sending a signal of 3.8 and your controls have to go through the process of increasing pressure in exactly the same way as they decreased the pressure. The set point on your regulator will have to pass through this dead band (hysteresis) to get the pressure to increase so your set pressure signal to the regulator has to go from 3.8 to 3.9, 4.0, 4.1, etc... until it gets to 4.8 before it can increase the pressure and affect a change to the strain gage.
This process of trying to increase and decrease a set point on your regulator has the inherent disadvantage of having to deal with this dead range on the regulator called hysteresis.
You can get around that problem by driving the pressure control valve open and closed directly instead of indirectly through a pressure set point. That's what the other valve or similar valve can do for you. It doesn't have a pressure set point. Instead, it pressurizes and vents depending on the signal you send.
Here's my understanding of the Festo MPYE. I could be wrong about this valve so it will be up to you to verify my understanding if you think this is a better way to go. The valve has internal valves just like the regulator. One opens and allows flow to the circuit and the other opens to allow flow out of the circuit. This is called a spool valve because it has a single valving element inside that slides from one side to the other. When it is in the center position, there is no flow. All 5 of the ports are closed at that point and there will be no flow. See the schematic symbol at the top of page 5. In order to get the valve to go to this position, it appears from the graph at the bottom of page 5, that a voltage of 5V will put it in this center position and stop flow. So if you send a signal of 5V, you get no flow. In this case, you are using it to pressurize the brake so your brake pressure won't change if you send it a signal of 5V and the strain gage reading won't change. So whatever the strain gage reading is, the pressure in the brake won't change and therefore the strain gage reading shouldn't change if you send a signal of 5V.
The valve can then be told to pressurize or vent. For the sake of this example, let's say you have the pressurization port (port 1) connected to your source pressure, port 4 connected to your brake piston and port 5 connected to a vent which goes to atmosphere. If you send a signal of 5V, the valve is closed and you don't get any change in pressure and no change in strain gage signal. If you want to increase the strain gage reading, your controls will increase the voltage above 5V (between 5 and 10). Note the graph at the bottom of page 5 that shows how far the valve opens is aproximately linearly related to the signal. So now if you send it a 6V, the valve opens a little bit and pressure gradually increases on the brake. If you send it a signal of 10V, the valve opens all the way and you get a much faster rise in pressure on the brake. When the strain gage reading aproaches the value you want (let's say you want a 5 from your strain gage), your controls will decrease the voltage signal from some value higher than 5V down to 5V and maintain the 5V if your strain gage reading is where it should be.
In the case of having to adjust the strain gage reading now, there is no hysteresis. Sending a signal less than 5V will decrease the pressure and decrease the strain gage reading. Sending a signal greater than 5V will increase the pressure and increase the strain gage reading. That pressure rise or fall rate (ie: the rate of pressure CHANGE) will be proportional to the signal you send it. So if you need a strain gage reading of 5 and it overshoots to 5.2, you send a signal of less than 5V to the valve and it vents pressure immediately and the strain gage reading decreases. When your strain gage reading approaches the value you need it to read, your controls will be sending out a signal that approaches 5V.
Note also that this valve would need to be set up in a way that produces a safe responce in the case of control failure. If controls fail (say from loss of power) and you want the pressure on the brake to go to zero, you would connect the valve as suggested above. If instead you wanted a loss of power signal to apply the brake, you would simply connect the opposite set of ports to this valve (ie: instead of using 1, 4 and 5 you would use ports 1, 2 and 3).
Sorry for the lengthy responce, and I understand that I could be totally mistaken on how your system works.
Best regards.