Query about Power Factor Change in a Power Plant

Click For Summary
SUMMARY

The discussion centers on the power factor (p.f) change observed in a power plant with eight gas engines operating in parallel. When one engine operates at a p.f of 0.8, the output after the transformer (11/132kV, step up Ynd1) remains stable. However, with all generators running at the same p.f, the overall p.f increases to 0.85. This phenomenon is attributed to transformer reactive losses and the cumulative effect of multiple generators operating in parallel. The discussion also highlights the need for precise calculations regarding the consumed reactive power (VAr) of the transformer.

PREREQUISITES
  • Understanding of power factor and its significance in electrical systems
  • Knowledge of transformer operation and reactive power losses
  • Familiarity with measurement tools such as wattmeters, varmeters, and ammeters
  • Basic concepts of impedance and its impact on electrical performance
NEXT STEPS
  • Research transformer reactive power losses and their impact on power factor
  • Learn about the calculations for consumed reactive power (VAr) in transformers
  • Study the effects of parallel generator operation on overall system performance
  • Explore methods for measuring and analyzing power factor in electrical systems
USEFUL FOR

Electrical engineers, power plant operators, and anyone involved in optimizing power factor and transformer efficiency in electrical systems.

rezwan17
Messages
1
Reaction score
0
I have a query about the power factor change in a power plant. There are 8 gas engines in parallel. When 1 engine runs with a set p.f of .8 the output at the delivery after transformer (11/132kv, step up Ynd1) is almost same. But when all generators are running with each having .80 p.f the p.f after transformer changes to .85. (All gensets are in parallel equal capacity and connected to single transformer and distance from gen to trans is comparatively small). Is this only for the transformer reactive loss or other thing is associated with this. Why the p.f increases and any calculation regarding the consumed VAr of the x-former. please specify elaborately.
If you need any further information please specify. I am the engineer of that power plant so can give you enough detail information.
 
Engineering news on Phys.org


what are you using to determine PF? Wattmeters, varmeters, ammeters, Qmeters ?

What is impedance of your transformer?

What would be per unit drop across transformer with one generator, and with 5 ?



old jim
 

Similar threads

Replies
18
Views
2K
Replies
2
Views
2K
Replies
9
Views
2K
  • · Replies 1 ·
Replies
1
Views
2K
Replies
3
Views
3K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 1 ·
Replies
1
Views
3K
  • · Replies 46 ·
2
Replies
46
Views
7K
  • · Replies 52 ·
2
Replies
52
Views
11K
  • · Replies 10 ·
Replies
10
Views
5K