Question on current draw from an inverter

  • Thread starter Thread starter tommy060289
  • Start date Start date
  • Tags Tags
    Current Inverter
AI Thread Summary
The current draw from an inverter depends on the load's resistance rather than just the wattage. For a 100W pump running at 230V, the current draw is 0.43 Amps, but when using a 12V battery, the inverter would ideally draw around 8.3 Amps, assuming 100% efficiency. However, real-world factors like inverter losses and the motor's power factor complicate this, requiring an inverter rated for at least 200W to handle starting currents. The inverter must convert 12V DC to 230V AC, which involves additional considerations like resistance changes in the load. Ultimately, understanding the resistance of the load is crucial for determining current draw accurately.
tommy060289
Messages
20
Reaction score
0
Hey everyone,

I have a slight question regarding the current draw from an inverter

If you had a 100W pump running on 230V obviously it's current draw is 100/230 which is 0.43 Amps

but what if you were running the water pump from an inverter connected to a 12V battery. Would the current draw still be the same or would the inverter draw from the battery 100 Watts divided by 12V (resulting in 8.3 Amps being drawn - assuming 100% efficiency, i know that's not realistic but I'm simplifying) or would it still just draw 0.43 Amps and alter the voltage?

Cheers,

Tom
 
Engineering news on Phys.org
tommy060289 said:
Hey everyone,

I have a slight question regarding the current draw from an inverter

If you had a 100W pump running on 230V obviously it's current draw is 100/230 which is 0.43 Amps

but what if you were running the water pump from an inverter connected to a 12V battery. Would the current draw still be the same or would the inverter draw from the battery 100 Watts divided by 12V (resulting in 8.3 Amps being drawn - assuming 100% efficiency, i know that's not realistic but I'm simplifying) or would it still just draw 0.43 Amps and alter the voltage?

Cheers,

Tom

I would find the resistance...(v^2)/R=Power
(230^2)/R=100
R=529 ohms

V=IR

12 volts=I*529

New current = .023 amps.
P=IV P=.23*12
New power = 2.76 watts.


The resistance of the load determines the current...not the watts. You can't assume the load will take 100 watts...you have to determine it's resitance first. See what I mean?

If you take a 12 volt battery that does make the 8.33 amps...you will see that the resistance is now different in your load...and that is impossible. And yes, I'm not coverting the DC to inverter...but that isn't really relevant for the problem at hand.

This motor would not even come close to starting.
 
I think Tommy has an Inverter with 12V supply - but still produces 230VAC output for the pump - correct?

In that case Tom - your second case is more accurate - it is a little more complicated - because the Motor will not have perfect power factor and the inverter will have losses as you mentioned. You need 100W to run the motor - 0.43A x 230V ~ 8.3A x 12V - Starting the pump requires higher current - so you would need an inverter of at least 200W - probably more.

If the inverter is only taking 12VDC - and making ~ 8 VAC RMS - that would not run anything.
 
Windadct said:
I think Tommy has an Inverter with 12V supply - but still produces 230VAC output for the pump - correct?
In that case Tom - your second case is more accurate - it is a little more complicated - because the Motor will not have perfect power factor and the inverter will have losses as you mentioned. You need 100W to run the motor - 0.43A x 230V ~ 8.3A x 12V - Starting the pump requires higher current - so you would need an inverter of at least 200W - probably more.

If the inverter is only taking 12VDC - and making ~ 8 VAC RMS - that would not run anything.

If that's the case...then I agree with Windadct. Keep in mind that the inverter would have to change the 12 volts to AC...then it would have to go thru a transformer to up the voltage to 230 volts. But I would guess that the fancy inverters have transformers built in.

But still, the resistance of the load determines most of the factors.
 
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...
Hello dear reader, a brief introduction: Some 4 years ago someone started developing health related issues, apparently due to exposure to RF & ELF related frequencies and/or fields (Magnetic). This is currently becoming known as EHS. (Electromagnetic hypersensitivity is a claimed sensitivity to electromagnetic fields, to which adverse symptoms are attributed.) She experiences a deep burning sensation throughout her entire body, leaving her in pain and exhausted after a pulse has occurred...