Single-phase Transformer Calculations

  • Thread starter Thread starter Rhirhi
  • Start date Start date
  • Tags Tags
    Transformer
AI Thread Summary
The discussion revolves around calculations for a single-phase transformer connected to a 400 V, 50 Hz supply. The equations used for calculating the induced emf in the secondary winding, the current in the secondary winding, and the number of turns required to produce a specific emf are confirmed to be correct. The frequency of 50 Hz does not affect the calculations for an ideal transformer, and emf is indeed synonymous with voltage. The participant's calculations yield an induced emf of 105.3 V, a secondary current of 76 A, and a requirement of 218.5 turns for a 230 V output. Overall, the participant is reassured about their approach and understanding of the problem.
Rhirhi
Messages
2
Reaction score
0
upload_2016-2-10_21-9-59.png
upload_2016-2-10_21-9-59.png
upload_2016-2-10_21-21-42.png
upload_2016-2-10_21-21-42.png
upload_2016-2-10_21-23-35.png
upload_2016-2-10_21-23-35.png

Homework Statement



I'm a bit thrown at this problem as I am unsure if firstly my equations so far are correct and secondly where/how I need to factor in the 50 Hz part. Or is this a red herring? Also, am I correct in thinking that the emf means voltage?

Any help would be appreciated

A single-phase transformer having a primary winding of 380 turns is connected to a 400 V, 50 Hz single phase supply.
Calculate:
a the emf induced in the secondary winding of 100 turns;
b the current in the secondary winding if the primary winding carries a current of 20 amperes;
c the number of turns required in the secondary winding to produce an emf of 230 V.


Homework Equations


a[/B]
Vs = Ns x Vp / Np

Vs = 100 x 400 / 380

b.
Is = Ip x Vp / Vs

Is = 20 x 400 / 105.3

c.
Ns = Np x Vs / Vp

Ns = 380 x 230 / 400

The Attempt at a Solution


a. = 105.3 V
b. = 76A
c. = 218.5
[/B]
 
Physics news on Phys.org
Hello Rhirhi, :welcome:

What can I say ? To answer your questions:
Equations are correct. You also apply them correctly and do the math correctly.
The 50 Hz doesn't enter in the equations: you can assume the transformer is 'ideal' (no frequency dependence and no power loss).
emf is indeed Voltage.

In PF your part 3 doesn't really count as 'attempt at solution'; you just type the answers.
But all in all: good work :smile: !
 
  • Like
Likes Rhirhi
Thanks very much BvU. you have put my mind at rest :-)
 
Back
Top