Single Phase Voltage from 3-Phase Line: Explained

Click For Summary
SUMMARY

The discussion clarifies that when a 25 kV three-phase line splits into single-phase lines, the line-to-neutral voltage is 14.4 kV, not 25 kV. This is calculated using the formula V_L-N = V_L-L / √3. Single-phase transformers are utilized to convert the 25 kV line-to-line voltage to a usable voltage with a ground reference applied at the secondary neutral. The conversation also highlights that in the U.S., single-phase distribution typically employs a multiple grounded neutral (MGN) system for residential applications.

PREREQUISITES
  • Understanding of three-phase electrical systems
  • Knowledge of transformer operation and ratings
  • Familiarity with line-to-neutral and line-to-line voltage concepts
  • Basic principles of electrical distribution systems
NEXT STEPS
  • Research "Transformer ratings and applications in single-phase systems"
  • Learn about "Multiple Grounded Neutral (MGN) systems in electrical distribution"
  • Study "Three-phase to single-phase conversion techniques"
  • Explore "Voltage calculations in three-phase systems using V_L-N and V_L-L"
USEFUL FOR

Electrical engineers, utility workers, and students studying power distribution systems will benefit from this discussion, particularly those focusing on three-phase and single-phase voltage applications.

louie
Messages
10
Reaction score
0
If I'm considering a 3 phase line (25kV line-to-line voltage) that comes to a point and splits into single phase lines, what is the line voltage of one of the single phase lines ?

Does it remain 25 kV or is it 14.4 kV because you're only dealing with 1 phase and a neutral now ?

Any explanation would be great

Louie
 
Engineering news on Phys.org
Normally, they do not distribute L-N = Vl/sqrt(3)=14.4kV, only L-L =25kV. The phases can split AB, BC, CA. The single phase transformers convert 25K--> user voltage with the ground reference applied at the secondary neutral.
 
A single phase line by definition is a circuit with only one phase. So you need a neutral side to create a loop. The voltage differential between the line and the neutral is, of course, +/- 14.4 kV and not 25 kV.

If you use both line (AB, AC, or BC) ... I don't think that a single phase line. It may be within the category of two phase line :-)

aaNg
 
For distribution purpose only line voltages preferred so neutral is not used. And 25KV will not be splitted into single phase directly it will be step downed and than you will get a sinle phase line. sinle phase line voltage depends on the transformer rating.
rgds
Mahadev
 
Actually, The main method of urban and suburban over head and URD is done single phase with line-neutra *in the usa*, europe is 3-phase secondary distribution 3-phases+ 2*line voltage = 8* the secondary line distance over the US, the neutral designation is MGN, or multiple grounded neutral, It is a lower wire of the four, or sometimes used as a top wire overhead shield in lightning prone areas. the L-N is used as the final distribution to the LNL +120 N -120 final use in typical residential apps.
 

Similar threads

  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 15 ·
Replies
15
Views
6K
  • · Replies 5 ·
Replies
5
Views
12K
Replies
8
Views
4K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 19 ·
Replies
19
Views
4K
Replies
31
Views
5K
Replies
38
Views
6K
  • · Replies 32 ·
2
Replies
32
Views
4K