Smoke interface height and temperature

2 replies · 3K views · last reply
Sabra_a
Messages
33
Reaction score
6
Homework Statement
A warehouse has a floor area of 550 m2 and a height of 11 m. An accidental fire starts on the ground. There is one door opening (3 m high and 6 m wide) at the floor level.

(i) The fire is a steady fire with heat release rate (HRR) 2 MW. Determine, using both the dimensionless method and Klote & Milke’s method, the smoke interface position and corresponding smoke layer temperature and plot them as functions of time from 3m below the ceiling to the top of the opening. Make suitable comments on your results.

(ii) Using one suitable method, repeat the calculations and plot the same as in (i) for a fast growing t^2 fire.
Relevant Equations
Dimensionless method
Klote and Milke's method
Heat release rate
smoke layer height
Handwritten-style typed worked solution for a fire smoke layer problem: dimensionless HRR calculation Q* = 2000 / (1.2 x 1.1 x 293 x sqrt(9.81) x 11^(5/2)) = 0.082, and dimensionless height y = 8/11 = 0.72, with a dimensionless-method equation dy/dt + Q* + 0.21(Q*)^(1/3)y^(5/3) = 0.

Graph of dimensionless smoke layer height y against (Q*)^(1/3) t, with curves for ceiling leak and floor leak Q* values 0.002, 0.01 and 0.05, followed by handwritten calculations for time t and dimensionless height y.

Graph of y against (Q*)^(1/3)t with curves for floor leak Q* = 0.002, 0.01 and 0.05 and a ceiling leak all Q*, with a worked reading at y = 0.72 giving (Q*)^(1/3)t of about 3.3, followed by calculations of t = 7.59 and t = 37.95 s.
Line graph titled smoke interface height (z_i), plotting a decreasing curve from about 8 at x near 11 down to about 3 at x near 38; below it, handwritten-style derivation using Klote and Milke's method for 8 m, computing t = 35.48 s and the heat release from convection as 49672 KJ.

Handwritten fire engineering calculations: smoke layer temperature 1 - Ta/Th = -0.0095 leading to Th = 290.2 K, then Klote and Milke method for 3 m giving t = 169.9 s, and convective heat release of 237860 kJ.
Handwritten calculation solving 1 - Ta/Th = 237860 / (1.2 x 1.1 x 293 x 550 x (11 - 169.9)), leading to Th = 36.48 K, above a line graph titled smoke layer temperature.

Table of fire growth rates alpha in kW/s squared against time to reach 1055 kW: Slow 0.00293, 600 s; Medium 0.01172, 300 s; Fast 0.0469, 150 s; Ultrafast 0.1876, 75 s. Below are handwritten calculations for tig and smoke interface height, and a graph titled Fast growing fire.
 
@Sabra_a
Looks to quite an involved calculation with formulas and graphs.
Unfortunately, I do not have much of the familiarity with fires and smoke to help you out.

But some things I would ask about.

Line graph titled "smoke interface height (z_i)" with x-axis from 0 to 40 and y-axis from 0 to 9, showing a blue curve that falls from about 8 near x=11 to about 3 near x=38.

What would be the labels on the axis, and units?
From formula does the graph made?

Line graph titled smoke layer temperature, with T_h = 36.48 K above it. The curve falls from about 290 at x of 12 to about 35 at x of 38, with no axis labels shown.

Same here - labels and units and formula.

Above the graph is the Th = 36.48 K.
( the previous Th was 290.2 K )
What's Th - the temperature of the smoke?
Is Th supposed to be less than ambient?
 
  • Like
Likes   Reactions: berkeman and Sabra_a
Thank you fo the reply. I changed few things in my answer
for the graph smoke interface height on the x-axis its time in seconds any y-axis is the smoke interface height
that's my solution. its a really long solution I sill couldn't fit one more page in and it will be difficult to explain. in the first part we are finding the location of the smoke interface and its temperature. its taken from 3 m below the ceiling and above the door which is 6m. this is solved using 2 different methods. them repeating the same calculation for a fast growing fire.
Handwritten working titled Using Dimensionless method: dy/dτ + Q* + 0.21(Q*)^(1/3)y^(-5/3) = 0, τ = t(H²/S)√(g/H), Q* = 0.082 from 2000 / (1.2 × 1.1 × 293√9.81(11)^(5/2)), y = 8/11 = 0.72, and calculation of time t = 2.27 from τ.
Handwritten calculation steps finding a time t from dimensionless height z/H = 7/11 = 0.63 and a fitted value of 1.4, giving t = 11.35 s and t = 16.1 s, then z/H = 6/11 = 0.54.

Handwritten working showing calculations of dimensionless time from a graph, with values 1.8 and 2.2, time t = 4.14 and 5.06, and t = 20.7 s with dimensionless height y = 5/11 = 0.45.
Handwritten calculation steps: t = 25.3 s from 5.06 = t x 0.2, dimensionless height y = 4/11 = 0.36, then time t = 32 s from 6.4 = t x 0.2, and y = 3/11 = 0.27 at 3 m.

Handwritten working determining (Q*)^(1/3)t from a graph, with calculation of t = 37.95 s, and a graph of ceiling and floor leak curves plotted as (Q*)^(1/3)t against a scale from 0 to 30.

Screenshot of a forum post showing a table of smoke interface height z_i (m) against time (sec), a line graph titled Smoke interface height (zi) vs time, and handwritten-style equations for smoke layer temperature and hot gas density.


Handwritten calculation and line graph of temperature in K against time in seconds, rising to a peak near 1765 K at 32 s, then falling; table of smoke interface heights with times, densities and temperatures beneath.

Handwritten calculation of smoke layer temperature and heat release rate, with an equation solving for time t = 35.48 s and a result of Th = 315 K.


Handwritten-style typed derivation: smoke layer temperature from 1 - Ta/Th = (integral of Q_conv dt)/(rho_a cp Ta S(H - z_i)), then convective heat release 0.7 x 2000 x 169.9 = 237860 kJ, solved to Th = 336.7 K.

Line graph titled Smoke interface height (zi) vs time, showing smoke interface height in metres decreasing from about 8 to about 3 as time in seconds increases from 30 to 170, followed by printed derivation of t_ig and the equation zi/H = 0.91 [...] for a fast growing fire.