Static pressure tubes vs pitot tubes

  • Thread starter Thread starter Chris J
  • Start date Start date
AI Thread Summary
L-shaped tubes with side holes are preferred for measuring static pressure in ducts because they minimize the influence of boundary layer effects and duct surface roughness. This design allows for more accurate readings by positioning the measurement point away from the duct wall, which can distort results if a simple side connection is used. While a direct connection could yield reasonable measurements, it may not be as reliable without additional probes. The L-shaped configuration also facilitates access to deeper areas within the duct for comprehensive pressure assessments. Accurate static pressure measurement is crucial for effective HVAC system performance.
Chris J
Messages
21
Reaction score
3
I've noticed when measuring static pressure in a duct most people use L shaped tubes with small holes in the sides, very similar to a pitot tube except it's missing the hole in the end for dynamic pressure.

What is the reason for using an L tube with holes in the sides for static pressure alone? Wouldn't just a connection into the side of the duct generally provide a fairly accurate measurement?
 
Engineering news on Phys.org
Chris J said:
What is the reason for using an L tube with holes in the sides for static pressure alone? Wouldn't just a connection into the side of the duct generally provide a fairly accurate measurement?
It should, but it would require a second hole and probe. I've also seen L shaped static pressure probes though, and I think they want to be a little away from the side of the duct so there's no weird effects from the boundary layer or roughness.

https://www.contractingbusiness.com/service/article/21212881/secrets-of-the-static-pressure-tip
 
  • Like
Likes jack action and Chris J
How did you find PF?: Via Google search Hi, I have a vessel I 3D printed to investigate single bubble rise. The vessel has a 4 mm gap separated by acrylic panels. This is essentially my viewing chamber where I can record the bubble motion. The vessel is open to atmosphere. The bubble generation mechanism is composed of a syringe pump and glass capillary tube (Internal Diameter of 0.45 mm). I connect a 1/4” air line hose from the syringe to the capillary The bubble is formed at the tip...
Thread 'What type of toilet do I have?'
I was enrolled in an online plumbing course at Stratford University. My plumbing textbook lists four types of residential toilets: 1# upflush toilets 2# pressure assisted toilets 3# gravity-fed, rim jet toilets and 4# gravity-fed, siphon-jet toilets. I know my toilet is not an upflush toilet because my toilet is not below the sewage line, and my toilet does not have a grinder and a pump next to it to propel waste upwards. I am about 99% sure that my toilet is not a pressure assisted...
After over 25 years of engineering, designing and analyzing bolted joints, I just learned this little fact. According to ASME B1.2, Gages and Gaging for Unified Inch Screw Threads: "The no-go gage should not pass over more than three complete turns when inserted into the internal thread of the product. " 3 turns seems like way to much. I have some really critical nuts that are of standard geometry (5/8"-11 UNC 3B) and have about 4.5 threads when you account for the chamfers on either...
Back
Top