Addressing Intermittent Over Current Faults in Dual UPS System

  • Thread starter Thread starter jtweedie@atdesk.com
  • Start date Start date
  • Tags Tags
    Static Switches
AI Thread Summary
The discussion centers on a dual UPS system where an overcurrent fault occurs in UPSB when switching from Source1 to Source2 after a failure in UPSA. The intermittent nature of the fault suggests that UPSB may not be adequately sized to handle the combined load during the transfer. It is emphasized that no switching arrangement can resolve this issue if UPSB cannot support both loads. The conclusion is that each UPS must be rated to supply the total load of both systems to prevent overcurrent faults. Proper sizing of the UPS units is crucial for reliable operation in this configuration.
jtweedie@atdesk.com
Messages
4
Reaction score
0
I have two UPSs, UPSA & UPSB, and two static transfer switches, STSA & STSB. UPSA feeds Source1 on STSA (preferred) and Source1 on STSB. UPSB feeds Source2 on STSA and Source2 on STSB (preferred). Each UPS has approxiamately a balanced 15KW load. Each UPS has 4 downstream transformers.

Question: IF i fail source1 on UPSA, STSA will will transfer from source1 to source2. BUT UPSB's inverter will fault on over current. The same thing will happen if i fail the preferred source of UPSB. This problem is also intermittent on both UPSs

There is more info but i would like to see what questions are generated so i will hold off. This is the core problem.

Any ideas
 
Engineering news on Phys.org
jtweedie@atdesk.com said:
Question: IF i fail source1 on UPSA, STSA will will transfer from source1 to source2. BUT UPSB's inverter will fault on over current.
This seems to make no sense. If B will trip on over current, then B is not adequately sized to carry both loads. No switching arrangement will cure that. You must have two UPS systems, each rated to supply A+B loads.
 
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...